I am in the process of upgrading our system from 24 to 48 Volts and I came across a post from a year or so ago where someone was discussing the same type of thing. One post that caught my eye was a post about the amount of panels needed to properly charge a system and I need some clarification on this.
This was posted by SUNKING if configured at 24 volts the current out from the charge controller is 1410 watts / 24 volts = 58.75 amps. With 6 strings of batteries means the current is divided by 6 right. So we have 58.75 amps / 6 strings = 9.79 amps /string.
I currently have a 24Volt system using 6 panels @ 235V, a 60Amp MPPT solar controller and 16 - 6Volt batteries hooked up in four rows of 24Volts each for a total of 1600AH.
Now SUNKING suggest that the current solar panels are not enough to properly charge, maintain the batteries
He posts; The minimum charge current to prevent sulfation is C/12 where C = the battery amp hour capacity. Your batteries are 225 AH batteries correct? So C/12 for your batteries is 225 AH / 12 hours = 18.75 amps minimum charge current required.
In my case the batteries are 400AH but it would mean that my batteries would require 400/12 = 33.33Amps and I am only getting 1410/24 = 58.75 / 4 = 14.69Amps so also not enough to prevent sulfation?
If I go to 48 Volts I have the batteries hooked up in two strings of 8 and double the panels to 12 I still only going to get 2820 / 48 = 58.75 / 2 = 29.38Amps. Still not enough. Somehow this doesn't sound right to me and I am missing something.
Any thoughts?
This was posted by SUNKING if configured at 24 volts the current out from the charge controller is 1410 watts / 24 volts = 58.75 amps. With 6 strings of batteries means the current is divided by 6 right. So we have 58.75 amps / 6 strings = 9.79 amps /string.
I currently have a 24Volt system using 6 panels @ 235V, a 60Amp MPPT solar controller and 16 - 6Volt batteries hooked up in four rows of 24Volts each for a total of 1600AH.
Now SUNKING suggest that the current solar panels are not enough to properly charge, maintain the batteries
He posts; The minimum charge current to prevent sulfation is C/12 where C = the battery amp hour capacity. Your batteries are 225 AH batteries correct? So C/12 for your batteries is 225 AH / 12 hours = 18.75 amps minimum charge current required.
In my case the batteries are 400AH but it would mean that my batteries would require 400/12 = 33.33Amps and I am only getting 1410/24 = 58.75 / 4 = 14.69Amps so also not enough to prevent sulfation?
If I go to 48 Volts I have the batteries hooked up in two strings of 8 and double the panels to 12 I still only going to get 2820 / 48 = 58.75 / 2 = 29.38Amps. Still not enough. Somehow this doesn't sound right to me and I am missing something.
Any thoughts?