    NiFe Electrolyte Refurbishment/Replacement 8-20128 (& DIY battery inverter )

    After 7 nearly trouble free years, I had a shoulder replacement, and while it's doing good, I decided to do the electrolyte and be good for 10+ years.

    Remembering the weight (about 80# each) and the 40 batteries, I decided to build a jig to hold and invert them for draining. It worked out really well, I made a cradle and drilled 2 holes for the axle in a cider press (which is now really clean !) The cradle has a rope handle to start the lift and rotation, and at the top is a rope to prevent over-rotation. the bad juice goes into a bucket, then emptied into a couple of olive barrels.
    But taking it all apart, mixing up 90 gallons of lye, dumping the old, cleaning the batteries, and the next step - putting it all back together. Going to take about 3 or 4 more days, between the fires and smoke here, and the 90+ heat, I can only do a couple of hours with help. Started at 6am, while it was still cold and had to knock off at 11am. For the last 4 days !
    So, I've got a sacrificial bank of 4, G27 marine batteries basically on float daylight hours and i fire up a honda eu2000 to put-put all night to keep the batteries up. 90ah is not going to last long if the gas runs out.
    more pics later & at https://www.facebook.com/media/set/?...1&l=1988b7f97a

    20180801_080750.png
    Attached Files
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Mike I really admire your creativeness and abilities. You would make an excellent redneck like myself where you depend on anyone., or take any crap from anyone.
    MSEE, PE

    Comment

    • J.P.M.
      Solar Fanatic
      • Aug 2013
      • 14920

      #3
      [QUOTE=Sunking;n381760]Mike I really admire your creativeness and abilities. You would make an excellent redneck like myself where you depend on anyone., or take any crap from anyone./QUOTE]

      But even with the glove, a lousy Michael Jackson celebrity look alike.

      Comment

      • sdold
        Moderator
        • Jun 2014
        • 1424

        #4
        I don't think that's Mike. Mike, I followed your link and was really impressed, that system you came up with is pure genius
        .

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          PS - the fellow in the photo is Fred B, an ultra reliable hard worker, and smart too. He came up with the idea for the safety rope at the top, to let the battery rest and drain, all hands off.
          This AM, I got all the cells refilled with magic battery juice (Koh & Lithium ) and am now starting in on cleaning up the terminals and re-coating with them with vaseline.20180803_094848.png
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Question is would you do it again with hind site? I mean use NiFe.

            Reason I ask is because if I were to go that route I would have used wet NiCd to get around some of the pitfalls of NiFe like low C rates, efficiency, and availability of chemicals and factory support.
            Last edited by Sunking; 08-04-2018, 10:29 PM.
            MSEE, PE

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              Would i do it again ?
              yes
              NiCad is too much of a toxic mess
              FLA is a constant worry, over charge, under charge. NiFe, I pretty much ignore except for adding water. Bank is large enough to not worry about damage, as long as plates are covered

              In 10 years, when change out needs to be done again. I don't know. That's a younger mans job. I'm still not done with it yet, cleaning up the hardware, new vaseline on all the metal, bolting up 170 connections (dual terminals on the batteries). In 8 years, I may start looking for a Li "powerwall" to use, instead of the electrolyte change out.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • SunEagle
                Super Moderator
                • Oct 2012
                • 15123

                #8
                Originally posted by Mike90250
                Would i do it again ?
                yes
                NiCad is too much of a toxic mess
                FLA is a constant worry, over charge, under charge. NiFe, I pretty much ignore except for adding water. Bank is large enough to not worry about damage, as long as plates are covered

                In 10 years, when change out needs to be done again. I don't know. That's a younger mans job. I'm still not done with it yet, cleaning up the hardware, new vaseline on all the metal, bolting up 170 connections (dual terminals on the batteries). In 8 years, I may start looking for a Li "powerwall" to use, instead of the electrolyte change out.
                How about a used EV battery?

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Originally posted by SunEagle
                  How about a used EV battery?
                  We'll see what's there in 10 years

                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • J.P.M.
                    Solar Fanatic
                    • Aug 2013
                    • 14920

                    #10
                    Please pass along to Fred B. : My wife thinks he's hot.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      Originally posted by J.P.M.
                      Please pass along to Fred B. : My wife thinks he's hot.
                      Are you trying to get rid of her ? Fred will get a kick out of this.

                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • littleharbor
                        Solar Fanatic
                        • Jan 2016
                        • 1998

                        #12
                        Take my wife, please.jpg
                        2.2kw Suntech mono, Classic 200, NEW Trace SW4024

                        Comment

                        • J.P.M.
                          Solar Fanatic
                          • Aug 2013
                          • 14920

                          #13
                          Originally posted by Mike90250

                          Are you trying to get rid of her ? Fred will get a kick out of this.
                          No, but thinking about it, it might be the other way around.

                          Reality: SWMBO & I have a deal. Doesn't matter where you get your appetite as long as you're home for dinner. Or, you don't have to eat at the restaurant, but you can always peruse the menu. We're married, not dead.

                          But that's not to say Fred's reduced to the equivalent of a roast beef sandwich either. No disrespect intended.

                          Best to Fred.

                          Comment

                          • Garrett
                            Junior Member
                            • Feb 2018
                            • 12

                            #14

                            Comment

                            • littleharbor
                              Solar Fanatic
                              • Jan 2016
                              • 1998

                              #15
                              Originally posted by Garrett


                              Some threads around here run their course, then lose focus, others outright Crash and Burn.
                              2.2kw Suntech mono, Classic 200, NEW Trace SW4024