    Is Li-ion now viable for off-grid?

    I have an off grid system built around the FP1 (FX3048 & FM80) which has been running nicely for about three years. I let the water get low on my Trojan L16s and damaged some of them. So Im shopping for a new battery bank.
    Ive become quit disillusioned by Lead Acid technology and Im very keen to give Li-ion a go. I know in the past it was poo-poo'd for complexity. But it seems it may be a more viable option these days.

    While I would love to get some Simpli-phi batteries https://www.altestore.com/blog/2017/02/ ... batteries/ the price is too high for my budget. But searching on ebay, there are several options from the auto industry which are sold with BMS systems which seem to be a plug-n-play solution for my off-grid needs.


    I just got an email back from the "EV Battery Center" company (attached below).

    So, I'm trying to get some feedback on this idea...is it a viable solution? Or should I be looking at something else? I was starting to get excited about Aquion, but with them filing bankruptcy, it drops them out of contention.
    li-ion.JPG

    3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15190

    #2
    IMO any type of Li-ion battery system is a gamble. They may work or they may not. If you are worried about wasting your money then stay with an FLA chemistry. At least if you do not follow the required maintenance procedure the worst is that they just run out of water and fail. If you fail to follow the maintenance procedure with Lithium the result may be a little more exciting.

    If money is no issue then try out the Li-ion chemistry. Good luck.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      I'd let Li batteries mature a couple more years. And realize that they may only slightly outlive lead acid by a couple years unless you grossly oversize them.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • Sunking
        Solar Fanatic
        • Feb 2010
        • 23301

        #4
        If you had LFP for 3 years you would be looking at replacing them soon. There is no better option than FLA batteries. FLA's are tough as nails and can take a lot of abuse. One mistake with LFP and they are done.

        For one you need to get a handle on your daily Kwh usage. For FLA you need 5-day reserve capacity and for LFP you need 3-day reserve to be equal. Example if you use say 1.67 Kwh per day on a 48 volt system you need a 8.4 Kwh FLA of 185 AH, and for LFP you need 100 AH.

        A good solid 5 to 7 year 8 x Trojan T-105RE 48 volt 200 AH FLA will cost you $1100 with a 3/6 warranty. Or you can buy a Chi-Com Calb 16 x CA-100 for $2200 and just a 1-year warranty. If you go with Calb you wil be on your second set before the Trojan needs replaced.

        Today to go LFP you are looking at a long range cost increase of 400% higher than FLA.

        MSEE, PE

        Comment

        • adoublee
          Solar Fanatic
          • Aug 2009
          • 251

          #5
          Simpliphi might be the best of the best with price to prove it. Check out some of the other options shown on Schneidersolar li-ion webinar replayed on YouTube. Some of these options still depend on a future bridge component.

          Comment

          • miahallen
            Solar Fanatic
            • Apr 2014
            • 108

            #6
            Thanks guys...there has always seemed to be a FLA bias here, so I'm not too surprised by your responses. But I listened to this advice 3 years ago, and I have been quite disappointed. I have good Trojan batteries...and even before the low-water damage that was admittedly my own fault...I had other problems, like posts melting down, and poor charging efficiency. I'm not very impressed with the technology, and I'm ready to move on. Maybe I'll pick up some clearance Aquion stacks while I still can.
            3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

            Comment

            • jflorey2
              Solar Fanatic
              • Aug 2015
              • 2333

              #7
              Originally posted by miahallen
              Thanks guys...there has always seemed to be a FLA bias here, so I'm not too surprised by your responses. But I listened to this advice 3 years ago, and I have been quite disappointed. I have good Trojan batteries...and even before the low-water damage that was admittedly my own fault...I had other problems, like posts melting down, and poor charging efficiency. I'm not very impressed with the technology, and I'm ready to move on.
              Well, if you are willing to spend the money, Iron Edison has some pretty good packs. The Fortelion line has been getting very good reviews but are again pricey. The cheap LiFePO4's like the CALB's work OK (we've used them here a bit) but you have to get somewhat home-brewy with the protection circuitry.

              Comment

              • Bala
                Solar Fanatic
                • Dec 2010
                • 734

                #8
                Originally posted by miahallen
                Thanks guys...there has always seemed to be a FLA bias here, so I'm not too surprised by your responses. But I listened to this advice 3 years ago, and I have been quite disappointed. I have good Trojan batteries...and even before the low-water damage that was admittedly my own fault...I had other problems, like posts melting down, and poor charging efficiency. I'm not very impressed with the technology, and I'm ready to move on. Maybe I'll pick up some clearance Aquion stacks while I still can.

                Why do you think posts melted? Generally the cause of melting is poor termination, which would also explain poor charge efficiency.

                Comment

                • miahallen
                  Solar Fanatic
                  • Apr 2014
                  • 108

                  #9
                  Bala, yes...that's what I have been lead to believe, but then I went and bought properly terminated 4/0 battery cables and torqued them to the rated specifications, and have still had issues...which again has simply turned me off of the technology. I'm living off-grid, and I respect the fact that many of you are die-hard lead acid believers...no problem. But I have always been tech savvy, and an early adopter...and if I'm going to have issues, I'd rather have them with new technology, than with "tried-and-true" tech. Hence this thread.
                  3680W - FLEXmax 80 - FX3048T - 8x L16P-AC 435Ah

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Lead Acid battery post technology has been around many years, and is well proven. Problems arise from poor connections that heat up and melt the posts.
                    The first solution is clean and torque the connections.
                    Second is to re-wire to a higher voltage bank that requires less amps flowing through the connections. Lead terminals should handle 200Amps without issue If you are at 48V already, a 3Kw inverter should only be capable of pulling 80A long term. LFP batteries will not solve the melting post problem, except that the terminals may be made from plated copper or steel and have higher melting temps than lead. Then you get into melting the cases of the cells. I use a copper loaded low resistance electrical grease.

                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • Bala
                      Solar Fanatic
                      • Dec 2010
                      • 734

                      #11
                      It seems more like set up and maintenance issues that caused problems rather than the battery technology. I would like a better battery tech than fla but I don't want another hobby at the moment so if I had to replace my bank today it would be new fla. My current set is over 10 years old.

                      Comment

                      • solar pete
                        Administrator
                        • May 2014
                        • 1860

                        #12
                        We have recently installed 10 LG Chem batterys, 8 out of the 10 were dead on arrival, we thought it must be our guys stuffing it up but we got in the most respected solar guy in the state to hook up a few of the replacements and we did everything exactly as he did, turns out they were knackered. Dealing with LG to get the replacement batteries has been a very painful experience. We are thinking of a LG ban they suck.

                        Comment

                        • Sunking
                          Solar Fanatic
                          • Feb 2010
                          • 23301

                          #13
                          Originally posted by miahallen
                          Thanks guys...there has always seemed to be a FLA bias here, so I'm not too surprised by your responses. But I listened to this advice 3 years ago, and I have been quite disappointed. I have good Trojan batteries...and even before the low-water damage that was admittedly my own fault...I had other problems, like posts melting down, and poor charging efficiency. I'm not very impressed with the technology, and I'm ready to move on. Maybe I'll pick up some clearance Aquion stacks while I still can.
                          No you did not listen, your own words incriminated you. You flat out abused and neglected your batteries. Melted term post is 110% proof positive your fault from neglect. As is over charging your batteries letting them run dry. LFP batteries would have been dead on your first mistake and can just as easily burn the term post off. LFP and any Lithium battery is very fragile and do not tolerate neglect or mistakes. If you cannot keep a set of Pb batteries healthy, you stand no chance with Lithium. One thing with Pb batteries when you abuse them like you did, they still worked. Do that with Lithium and 1 of 2 bad things happen, or both. You kill them immediately and/or they explode into fire you cannot extinguish. Over discharge them and they are dead. Over charge them and they burn.
                          Last edited by Sunking; 03-30-2017, 08:44 PM.
                          MSEE, PE

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15190

                            #14
                            Someone once told me that everything requires maintenance. Except a brick as long as it stays a brick. Once it becomes part of a wall someone has to make sure to take care of it or it will fall apart and become a brick again or worse.

                            Battery technology is no different. The more complex the more it takes to keep it happy and working. There is no such thing as "plug, play and forget".

                            Comment

                            • adoublee
                              Solar Fanatic
                              • Aug 2009
                              • 251

                              #15
                              To many parameters to get exactly right during operation and hassles to deal with using lead-acid. Lithium gets rid of most of the hassles. Once reasonable protection is built in (pre-integrated for most), cost is reasonable, and interface equipment is readily available lead acid will pass. Commercialization of EVs guarantees it. There are multiple pre-integrated protection systems now and better interface equipment should be coming out this year. The value might be there very shortly for integrally protected systems (where off-grid is required), but cost for a non-DIY protected system is still hard for most to handle. It is becoming much easier to design a lithium system that automates protection from self-destruction and still works properly versus lead-acid, but protection is the key and risky if building yourself.

                              Comment