Tesla Power Wall and a generator?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • armourereric
    Junior Member
    • Nov 2014
    • 7

    Tesla Power Wall and a generator?

    I posted this here because IIRC, the Tesla Power Wall runs off of a Lithium Iron system. Please move it if that is incorrect. Anyhow, is there a point that the Power Wall will be made available for installation with the setup being a recharge via generator only. How long would it take to recharge the 10Kwh, frequent cycle Tesla unit using a 7500e generator? I would intuitive guess about 2.5 Hours. Where I live electricity is now 29.9c a Kw, the second highest in the US and annual 15% increases are on the horizon, and SDG&E wants $6000 just to "send a consultant" to see if I can be hooked up.
  • inetdog
    Super Moderator
    • May 2012
    • 9909

    #2
    Originally posted by armourereric
    I posted this here because IIRC, the Tesla Power Wall runs off of a Lithium Iron system. Please move it if that is incorrect. Anyhow, is there a point that the Power Wall will be made available for installation with the setup being a recharge via generator only. How long would it take to recharge the 10Kwh, frequent cycle Tesla unit using a 7500e generator? I would intuitive guess about 2.5 Hours. Where I live electricity is now 29.9c a Kw, the second highest in the US and annual 15% increases are on the horizon, and SDG&E wants $6000 just to "send a consultant" to see if I can be hooked up.
    It is a Lithium Ion not Iron system. And I do not think that it is Lithium Iron Phosphate (LiFePO4).
    Your charging estimate is probably not too far off, although C/2 is a pretty high charging rate for regular use even for Li.
    As far as cost is concerned, the generator is going to cost you even more than SDG&E, so the main use for something like what you describe would be for pure off grid when you want to minimize generator use and maintain quiet hours.
    SunnyBoy 3000 US, 18 BP Solar 175B panels.

    Comment

    • armourereric
      Junior Member
      • Nov 2014
      • 7

      #3
      This would be an off grid situation. Why would the Generator be more than $6000? I frequently see 10000w units with key ignition start and LP/gasoline bi fuel for under $1K It would be just me and I don't use that much electricity. The house is a good 500 feet from any property line, I could likely run the gen at will.

      Comment

      • sensij
        Solar Fanatic
        • Sep 2014
        • 5074

        #4
        No, the generator will cost more per kWh than what you pay (and will pay) for energy from the grid. Whoever convinced you to expect 15% increases in perpetuity is trying to sell you something. The Powerwall might make sense to charge from the grid when energy is cheap (at night), and then discharge during peak times (late afternoon/evening). As an off-grid solution, the case isn't obvious yet.
        CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

        Comment

        • Willaby
          Solar Fanatic
          • Jun 2015
          • 205

          #5
          Originally posted by armourereric
          This would be an off grid situation. Why would the Generator be more than $6000? I frequently see 10000w units with key ignition start and LP/gasoline bi fuel for under $1K It would be just me and I don't use that much electricity. The house is a good 500 feet from any property line, I could likely run the gen at will.
          You'll need an inverter to go with the Powerwall, add at least $1k. After that expense, might as well add some solar if it suits your exposure. Also, the Powerwall is limited to 2kw continuous, 3kw peak, so just a couple of appliances will load it up pretty quickly. You could still time those to work with the gen-set on though.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by armourereric
            This would be an off grid situation. Why would the Generator be more than $6000? I frequently see 10000w units with key ignition start and LP/gasoline bi fuel for under $1K It would be just me and I don't use that much electricity. The house is a good 500 feet from any property line, I could likely run the gen at will.
            Wow ! i'd like to see a source for that

            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • emartin00
              Solar Fanatic
              • Aug 2013
              • 511

              #7
              If you have a generator, a powerwall is just going to add cost and complexity with little to no benefit. Converting electricity from AC to DC, then charging the battery, then discharging, converting back to AC is just going to be a big hit to efficiency. Generators already modulate fuel usage based on electricity demand.

              Comment

              • inetdog
                Super Moderator
                • May 2012
                • 9909

                #8
                Originally posted by emartin00
                Generators already modulate fuel usage based on electricity demand.
                Inverter type generators do a far better job of handling partial loads than conventional generators, even without factoring in any eco-throttle (standby) options.
                Running a large generator at a high constant RPM even for low loads is inefficient.
                SunnyBoy 3000 US, 18 BP Solar 175B panels.

                Comment

                Working...