Designing of off grid solar system
Collapse
X
-
Leave a comment:
-
Leave a comment:
-
@ wedgeantilles If you have not run this sort of high power system, please refrain from advising neophytes un-tested theory.
There is no practical way to run a 5 hp 3 ph pump from a small or moderate solar system. You are better off getting a generator to run it. It WILL NEVER run directly off solar panels, without a VERY expensive system, and then, only in full, bright sunlight for a couple hours only.
engineering (best case) 750watts = 1 hp. That's 3750 watts, in a perfect, loss free system, and much more in real life.Leave a comment:
-
There is no practical way to run a 5 hp 3 ph pump from a small or moderate solar system. You are better off getting a generator to run it. It WILL NEVER run directly off solar panels, without a VERY expensive system, and then, only in full, bright sunlight for a couple hours only.
engineering (best case) 750watts = 1 hp. That's 3750 watts, in a perfect, loss free system, and much more in real life.Leave a comment:
-
For the 5 HP pump, you can use amorphous panels, just connect series of them to have the grid voltage ( if it is 230 V 50 Hz, I don't know) you will need 230*SQRT(2)=330 Volts aprox. Then connect others series in parallel to reach the amps needed.
Then connect the output from the solar pannels to the DC input of the VFD and you have it, connect the electrical motor in a star configuration if it is rated to 230 V star. The VFD will do the rest.
Wedge.
Kindly also guide is it possible that VFD itself control the speed of the motor as the radiation varies.
Many thanks for your battery less solution suggestion.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
What a joke. I get it though.Leave a comment:
-
Solar Pumps
For the 5 HP pump, you can use amorphous panels, just connect series of them to have the grid voltage ( if it is 230 V 50 Hz, I don't know) you will need 230*SQRT(2)=330 Volts aprox. Then connect others series in parallel to reach the amps needed.
Then connect the output from the solar pannels to the DC input of the VFD and you have it, connect the electrical motor in a star configuration if it is rated to 230 V star. The VFD will do the rest.
For providing a better control use a LDR (Light dependant resistor, in a voltage divider) connect the voltage divider to the DC source included with most of the inverters, and the output to the potentiometer input of the VFD. The VFD will control the frequency depending on the solar light falling into the LDR (the LDR must be at the same place as the amorphous panels, same orientation and inclination). Thus you will have more pumping hours, but don't be confused, less frequency lower water flow. And this has a limit, when there is not enough power the VFD will stop the motor. You will have to change some parameters in the VFD, in order to automatically restart the motor, in case there are some passing clouds. Only if there is no life threatening due to motor automatic restart.
I will be delighted to hear from this if you try.
Good luck!!!
Wedge.Leave a comment:
-
Leave a comment:
-
Real thought here.
What are wind conditions like?Leave a comment:
-
Leave a comment:
-
generic Grid-Tie (batteryless)
or
Off-Grid with batteries, PV and inverter that Sunking listed
Panel wattage = 9600 watts divided into 3 systems of 3200 watts each with its own separate Charge Controller
Battery capacity configured @ 48 volts = 3000 AH, approx weight = 9000 lbs or 4100 Kg
Charge Controllers = 3 units 80 Amp MPPT
Inverter = Industrial Grade 10 Kva