    Originally posted by Mike90250
    The waiting time is at least 3 hours.
    The temperature correction is for when you measure the battery acid in the hydrometer, warm electrolyte is less dense than cold electrolyte. You use the chart to adjust the temp reading from what the floating element indicates.
    Will do. Thanks Mike.

    Bala, I think you asked me 2 times if I did temp correction and each time I answered you 'yes', but here you are asking again. "If temp correction is done correctly you can read SOC using SG at any time" is not correct based on this experience of mine.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #17
      There is temp comPensation the Charger settings , this adjusts the charging voltage, lower when hot, higher when cold
      To read battery SoC, you need several idle hours for the battery to "settle"

      When measuring SG, you use a temp Correction table to adjust the SG the float reads. done correctly, you can read SG at any time, as long as your sample fluid has no bubbles in it.

      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||