    increasing battery storage

    I am looking to replace my current single string of 8 - 6v batteries with two strings of 8.
    my full system is
    ​​​​​​9-suntech 175 watt modules and 9 up solar 185watt panels in strings of 3,
    8- Deka 6V for 48v. system
    outback VFX 3648 inverter,
    outback FM-60 charge controller.
    Propane 15KW Genset
    System Installed August 2009...Hence the need for new batteries


    I am looking to go to 16 Trojan L16H's

    two questions
    1. my understranding is they should be wired as two strings of 8 in series connect the positives of the two strings and the negative of the two strings then pull the + and the negative off to the charge controller.... correct??

    2. given my system is there anything else I need to consider or change??
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    is this new battery bank larger than your old one ? If so, does your solar have the capability to recharge it at 10% of the ah rating of the bank
    ( 800ah bank needs 80a of charge current)
    if not, you will need to add more charging, either more solar or generator

    9x 175w
    9x 185w
    I come up with less than 60A which gives you only marginal recharging.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • galaxieflier
      Junior Member
      • Aug 2019
      • 2

      #3
      Thank you Mike.
      Yes currently only one string of 370ah batteries looking to move to two 430ah.
      There is a Generator inplace but the point was to lessen the usage of it not set us up for more.