    GEL with no limit chargecurrent voltage???

    Ive never seen specs like the attached GEL specs. Unfortunately I dont have lifecycle chart. Marketed as KiJo Battery.

    questions:
    Is it not unusual for "standbyUse" to have a NO limit on chargecurrent Voltage" for a GEL??

    Also for a gel rather unusual CycleUse charge algorithm. It is about the same as for a non-gel or not ????
    ​​​​
    Specs or advertisement can write anything under "applications", do you think this battery is suitable for pv offgrid application as I always read here "forget gel for pv offgrid"
    Attached Files
    Last edited by GeorgeF; 07-17-2019, 11:53 PM.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    I read 30A charge limit. for my peace of mind, I'd stick with a major mfg of AGM.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • GeorgeF
      Solar Fanatic
      • Nov 2018
      • 277

      #3
      A guy asked if it wise to buy this gel battery as he intend to setup a small sistem.

      Perhaps wise that he also evaluates true deep cycle FLA batteries which for sure will give him more cycles @ 50% DoD

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        AGM has shorter life and higher cost than flooded. I like to see new users start with flooded, and after they get flooded working reliably for 3 years and debugged, then switch to AGM

        but throwing out system specs piecemeal, and getting pieces evaluated without the whole, is not going to work.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • GeorgeF
          Solar Fanatic
          • Nov 2018
          • 277

          #5
          Switch to AGM while AGM is more expensive and less cycles? Sorry Mike, i can't follow you.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Sometimes folks get a bug in their pants and just have to have AGM batteries. I'm suggesting instead of starting with AGM and ruining then in a month, start with forgiving flooded batteries and then - if needed, switch to AGM and you have a fair chance of them lasting 4 years.
            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15125

              #7
              Besides being able to mount the AGM batteries on their side they also allow you to charge them faster then an FLA type.

              The problem is that they cost much more then a similar system of FLA batteries and may not even last as long. So AGM is not something you start out with or IMO go to.

              Comment

              • GeorgeF
                Solar Fanatic
                • Nov 2018
                • 277

                #8
                Mike, if I understood well you advise starters to start with (cheaper) FLA and if they already have some experience and want for some reasons more expensive AGM's they will treat their batterybank more gentle. 👍

                Suneagle, if i see the specs of for example Rolls AGM 1250 cycles @ 50% DoD comparing to CS 11P 3200 cycles @ 50% DoD 😇 it is abvious that FLA is the PV winner 😊

                Thanks for all above replies.

                Comment

                • PNjunction
                  Solar Fanatic
                  • Jul 2012
                  • 2179

                  #9
                  Bogus specs.

                  First indication: "Motorcycle Fit". Yeah, you don't use "deep cycle gel" for that application in the first place. Not only that, but the internal resistance of a "conventional agm", which this appears to be is way higher than it should be for a starting application. This is why REAL motorcycle starter batteries are more costly than these little generic bricks.

                  Too many red flags. Tell your friend not to be so cheap, or he'll end up paying for things TWICE or more with replacements for the real stuff.