    Suppose I install 200Wp panel, chargecontroller and before I connect all to the batterybank 12v i charge the bank full with an ac-charger. Then i intend to draw daily only approx 700-800Wh.

    Is the 200Wp panel able to charge a 450Ah batterybank full each day or is the capacity of the panel to small that it wont be able to charge the 800Wh.
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15125

    #2
    Short answer on panel wattage being 200 is no.

    A 450Ah battery requires at least 38 amps or more of charging. With an MPPT CC you would need about 500 watts to generate that much charging amps.

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #3
      No next question.

      It will require a 500 to 600 watt panel.
      MSEE, PE

      Comment

      • fivewin
        Junior Member
        • Aug 2016
        • 203

        #4
        So this guy with his 400+ Ah and 185Wp panel can not charge what he uses daily


        panel PV 185Wp (y) Video 2009: https://www.youtube.com/watch?v=Nn2DWB_LF_k

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15125

          #5
          Originally posted by fivewin
          So this guy with his 400+ Ah and 185Wp panel can not charge what he uses daily


          panel PV 185Wp (y) Video 2009:
          Sure he can but don't expect those batteries to last long with only 12amps max available to charge them.

          Also 4 paralleled wired batteries are doomed for an early grave so that is two strikes against the poster of that video.

          Since that video was listed in 2009 I expect he has gone through multiple sets of batteries by now.
          Last edited by SunEagle; 05-04-2018, 01:28 PM.

          Comment

          • Mike90250
            Moderator
            • May 2009
            • 16020

            #6
            Originally posted by fivewin
            So this guy with his 400+ Ah and 185Wp panel can not charge what he uses daily
            If the battery does not receive an adequate amount of amps to bubble/stir the electrolyte, it will not have a full life.
            AGM will not have that restriction, but the cells cost 2x as much, and have shorter lifetime anyway.

            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

            solar: http://tinyurl.com/LMR-Solar
            gen: http://tinyurl.com/LMR-Lister

            Comment

            • jflorey2
              Solar Fanatic
              • Aug 2015
              • 2331

              #7
              Originally posted by fivewin
              So this guy with his 400+ Ah and 185Wp panel can not charge what he uses daily
              You posted a video of a guy who is using 15 watt amorphous panels to charge his "deep cycle" marine batteries - which are standing without protection on his carpet. His AC distribution system is apparently "run extension cords all over the house."

              It is very safe to say that this guy hasn't been doing this for very long, and it would not surprise me to discover that his batteries had gone dead in a week. (Indeed that's probably a pretty good outcome for him compared to the alternatives.)

              Comment

              • fivewin
                Junior Member
                • Aug 2016
                • 203

                #8
                Im convinced ...hehe
                Thanks for all replies

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by fivewin
                  So this guy with his 400+ Ah and 185Wp panel can not charge what he uses daily


                  panel PV 185Wp (y) Video 2009: https://www.youtube.com/watch?v=Nn2DWB_LF_k
                  Cheese and rice, quit watching youtube idiots. If you watch them and take their advice, then you are as stupid as the guy making the video. The internet is the most dangerous technology man has invented.

                  MSEE, PE

                  Comment

                  • DanS26
                    Solar Fanatic
                    • Dec 2011
                    • 972

                    #10
                    YouTube videos are like real life.....some are idiots....some are mediocre....some are genius......you just have to know the difference.

                    If you have been raised to know the difference, then good for you.

                    Comment

                    • J.P.M.
                      Solar Fanatic
                      • Aug 2013
                      • 14926

                      #11
                      Originally posted by DanS26
                      YouTube videos are like real life.....some are idiots....some are mediocre....some are genius......you just have to know the difference.

                      If you have been raised to know the difference, then good for you.
                      And what about those who have not been raised to think and so know the difference ? I think I've met a few of them. Screw them ? Or what ?

                      In real life, at least until fairly recently, information of a technical nature was vetted/peer reviewed. That the utube stuff of a technical nature or dealing with stuff that can do damage is not vetted/peer reviewed as far as I can tell, and IMO only, is a problem. It's the wild west of information dissemination. The medium allows anyone to say or claim or do just about anything they want without consequence with the result that, using your caveat about knowing (or not knowing) the difference, those who don't know squat will happily, innocently and ignorantly wander into trouble.

                      Look, I'm a libertarian at heart and don't like regulation much and probably less than most, but nothing is all or nothing. If I have any common sense, and any compassion for the rest of humanity or even enlightened self interest, it tells me that today's morons need some protection, if only from their own slothful stupidity, not better and faster descriptions of unfettered lunacy.

                      Redneck engineering used to be the stuff of jokes. Now, folks see about the same on utube and take it seriously. WTF ?

                      Or, I suppose I could look on the bright side and consider utube a tool to improve the gene pool.

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        Originally posted by J.P.M.
                        Or, I suppose I could look on the bright side and consider utube a tool to improve the gene pool.
                        Problem is today that pool only has a shallow end.

                        Reminds me a swimming pool signs I have seen in Lost Wages at the casino/resorts where they divide the adult and kid side of the pools with a rope. Adult side of the pool has a sign: "No Pee Allowed This Side of Rope"
                        MSEE, PE

                        Comment

                        • J.P.M.
                          Solar Fanatic
                          • Aug 2013
                          • 14926

                          #13
                          Originally posted by Sunking
                          Problem is today that pool only has a shallow end.

                          Reminds me a swimming pool signs I have seen in Lost Wages at the casino/resorts where they divide the adult and kid side of the pools with a rope. Adult side of the pool has a sign: "No Pee Allowed This Side of Rope"
                          To the degree that anyone takes the sign seriously is some confirmation of the appropriateness of your pool depth comment.

                          Comment

                          • Mike90250
                            Moderator
                            • May 2009
                            • 16020

                            #14
                            Chlorinate the gene pool.
                            Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                            || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                            || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                            solar: http://tinyurl.com/LMR-Solar
                            gen: http://tinyurl.com/LMR-Lister

                            Comment

                            Working...