3 parallel Lead Acid strings
Collapse
X
-
Is cadmium-plated solid copper OK ?
example: Something like this ...
https://www.ebay.com/itm/Solid-Coppe...0AAOSwDNdV3eqGLeave a comment:
-
Leave a comment:
-
My mistake sorry.
Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.
FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.
will try to find 200 amps busbar or may have to order them in the US. Was thinking of using earth bar but apparently (true?) I have been told that they are only brass coated (?)Last edited by dapago; 10-24-2017, 12:44 PM.Leave a comment:
-
Will do it as you suggest. My problem is to find the busbar here. Have been calling many electrical supplier AND the very few solar provider, nobody has busbar
F169EE73-3AC7-4477-8FB7-7A9159E2481F.jpegLast edited by dapago; 10-24-2017, 12:54 PM.Leave a comment:
-
Can the OP add a DC Rated Fuse in series with each string ?
Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.
FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.Leave a comment:
-
Then, why not opposite ends of the bus bar,
Inverter (+) @ top of bus bar, near string #1's connection
Inverter (-) @ bottom of bus bar, near string #3's connection
Same with CC'sLeave a comment:
-
Leave a comment:
-
Does not compute. Busbars are not rated in AH, the are rated in AMPS. The busbar current ratings (Amps) must be equal to or greater than the load imposed on it. If you have at least 1/8 inch thick copper 1 inch wide busbars will exceed anything you can throw at it as it will be rated at least at 200 amps.
FWIW the bus bars are the least of your concerns, or perhaps mine. What I want to know is just how you plan to integrate Over Current Devices using bus bars.Last edited by Sunking; 10-23-2017, 11:40 PM.Leave a comment:
-
Leave a comment:
-
An other question. What Ah is needed for the busbar for my bank?Leave a comment:
-
017B5036-FA62-453B-868C-237A7D24FD8C.jpeg
i have made a little diagram. Just need to know if that is correct and if each batts will be well balanced.
cant afford to damage my batts or have unbalanced batts.Last edited by dapago; 10-23-2017, 09:39 PM.Leave a comment:
-
Thanks a lot for your inputs!!! Really appreciate it.
For lead-acid batteries you do NOT want to add the cross connections (dotted lines). The batteries and strings will be better equalized if you do not use them.
For lithium chemistry batteries, which do not tolerate overcharging some batteries in a string to get full charge on others, you would want to use the cross connections.
Leave a comment:
-
Leave a comment:
-
For lead-acid batteries you do NOT want to add the cross connections (dotted lines). The batteries and strings will be better equalized if you do not use them.
For lithium chemistry batteries, which do not tolerate overcharging some batteries in a string to get full charge on others, you would want to use the cross connections.Leave a comment: