    I only have 24V Meanwell 350W 14amp supply , The PWM change controller LS2024B which I have provide automatic 3 stage charging (and voltage can be set by user) that is why i want to use it
    Not going to work and you will destroy your Meanwell power supply. Your PWM controller is made to operate from a current source. You Power Supply is a Voltage Source. You are going to let the Magic Smoke Out of the Meanwell, and quite likely the PWM controller.

    So my advice is go for it. You will learn a lesson, and you will not like it one bit.

    If you have a AC power source, there is no reason to use 3-Stage Charging. All you need is a Float Charge of 13.6 to 13.8 volts. All 3-stage doe sis make the job quicker. Catch is for Solar it does not work because there still are not enough hours in a day to complete.. If you want as fast as possible you still use a Float Charger set to 14.4 to 15 volts and terminate when current tapers to .03C.

    What you can do if you have electronic design experience is make a Shunt Regulator using something like a TI LM7812 and a 15-amp MOSFET to step down the Meanwall to a usable voltage. Replace D1 with a 2.4 volt Zener diode to raise the voltage from 12 to 13.8 volts.

    Last edited by Sunking; 05-03-2016, 02:43 PM.
    MSEE, PE

    Comment

    • jflorey2
      Solar Fanatic
      • Aug 2015
      • 2331

      #17
      Originally posted by Logan005
      Is the mean well power supply, also a charger? if it is why not just charge two 12 volt batteries in series? If it's just a power supply, not sure what to do with that.
      It's just a power supply. You can use them as cheap chargers. For example, a 600 watt 48 volt supply can be dialed back to 42 volts and used to charge 36 volt electric bicycle batteries, and a 15 volt supply can easily be set to 13.8 volts and make a very cheap lead acid battery charger/maintainer. It will NOT do multi step charging, so is not suitable for lead acid applications that are cycled often. But to maintain the various lead-acid batteries I have for my job it works OK.

      One of the reasons that Meanwell supplies seem to work well is that the small/medium supplies will run in current limit - in other words, they don't just shut down on overcurrent, they limit the current and continue operating. This isn't how they are designed to run, which is why it's critical to ensure that they have plenty of cooling and also why it's critical to drop the voltage on the output. If a 600 watt supply is run at 48 volts 12.5 amps it will generally work OK; that is what it is designed to do. If the same supply is run into current limit at 14 amps it is now running at 672 watts, which is outside its thermal rating. By dropping the voltage to 42 volts the supply is now running at 588 watts at a current limit of 14 amps.

      (Needless to say a dedicated lead-acid charger would be far better.)

      Comment

      • burraak
        Junior Member
        • May 2016
        • 13

        #18
        Originally posted by Sunking
        Not going to work and you will destroy your Meanwell power supply. Your PWM controller is made to operate from a current source. You Power Supply is a Voltage Source. You are going to let the Magic Smoke Out of the Meanwell, and quite likely the PWM controller.

        So my advice is go for it. You will learn a lesson, and you will not like it one bit.

        If you have a AC power source, there is no reason to use 3-Stage Charging. All you need is a Float Charge of 13.6 to 13.8 volts. All 3-stage doe sis make the job quicker. Catch is for Solar it does not work because there still are not enough hours in a day to complete.. If you want as fast as possible you still use a Float Charger set to 14.4 to 15 volts and terminate when current tapers to .03C.

        What you can do if you have electronic design experience is make a Shunt Regulator using something like a TI LM7812 and a 15-amp MOSFET to step down the Meanwall to a usable voltage. Replace D1 with a 2.4 volt Zener diode to raise the voltage from 12 to 13.8 volts.


        So how do I know which power supply is made as current source and which one as voltage source? How do I recognize it ? because this info is something new to me I'm not an electronics expert Can you please explain this thing a little bit more ?
        A power supply with 14 amp current output is suppose to be a good power supply to charge a 135AHr battery, Voltage in Meanwell 25V can be reduced to 19V and PWM will further decrease it around 14.4V therefore theoretically I was thinking of it as a perfect match
        Last edited by burraak; 05-04-2016, 01:50 PM.

        Comment

        • jflorey2
          Solar Fanatic
          • Aug 2015
          • 2331

          #19
          Originally posted by Logan005
          Is the mean well power supply, also a charger?
          Let me reiterate that it is MUCH better to buy a dedicated charger than to use a power supply, or even a power supply + charge controller.
          if it is why not just charge two 12 volt batteries in series?
          You need ~28 volts to charge two 12 volt batteries in series, not 24. That's why you need a 15 volt capable supply to charge a 12 volt battery.

          Comment

          • burraak
            Junior Member
            • May 2016
            • 13

            #20
            Originally posted by jflorey2
            It's just a power supply. You can use them as cheap chargers. For example, a 600 watt 48 volt supply can be dialed back to 42 volts and used to charge 36 volt electric bicycle batteries, and a 15 volt supply can easily be set to 13.8 volts and make a very cheap lead acid battery charger/maintainer. It will NOT do multi step charging, so is not suitable for lead acid applications that are cycled often. But to maintain the various lead-acid batteries I have for my job it works OK.

            One of the reasons that Meanwell supplies seem to work well is that the small/medium supplies will run in current limit - in other words, they don't just shut down on overcurrent, they limit the current and continue operating. This isn't how they are designed to run, which is why it's critical to ensure that they have plenty of cooling and also why it's critical to drop the voltage on the output. If a 600 watt supply is run at 48 volts 12.5 amps it will generally work OK; that is what it is designed to do. If the same supply is run into current limit at 14 amps it is now running at 672 watts, which is outside its thermal rating. By dropping the voltage to 42 volts the supply is now running at 588 watts at a current limit of 14 amps.

            (Needless to say a dedicated lead-acid charger would be far better.)
            Just got this question after reading your comment i.e Meanwell 24V 350W 14amp can also be adjusted around 19V (and current limit can also be reduced by changing R33) And in combination with PWM solar charge controller those voltages would be further reduced around 15V so Why it is OK to directly attach Meanwell to battery but not through PWM controller?

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #21
              most power supplies are voltage sources. You can get a current limiting PS but not many are made, and they will cost $$
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • jflorey2
                Solar Fanatic
                • Aug 2015
                • 2331

                #22
                Originally posted by burraak
                Just got this question after reading your comment i.e Meanwell 24V 350W 14amp can also be adjusted around 19V (and current limit can also be reduced by changing R33) And in combination with PWM solar charge controller those voltages would be further reduced around 15V so Why it is OK to directly attach Meanwell to battery but not through PWM controller?
                A good question. The big issues with doing it as you describe (24V supply into PWM charge controller) are 1) the nature of the load (slamming on-off) and 2) the inaccuracy of the current limit.

                PWM controllers are either on or off - full load or none. That is a worst-case application for switchmode power supplies, since it forces rapid excursions from zero to full power at the point that the PWM controller starts to limit. Better power supply manufacturers test for this condition, but Meanwell is about as cheap as they come - so I wouldn't be surprised if they omit it,

                Current limits on these supplies are not that accurate. I think they actually spec 105 to 135% (check your data sheet) but I've found that they can be anywhere from 100% to 140%, in one case over 150%. (Usually not an issue - the current limit is not intended to regulate current, just to protect the supply in the event of an overload or short circuit.) Thus you might see more than 20 amps from your system in current limit, and your charge controller will have to switch this.

                As I mentioned, it might work. If you are going to try this, the first thing I would try is getting a good active load and setting the output to constant voltage, 13 volts. Connect the supply. If the output stays up at 13 volts and the current is reasonable (i.e. 17 amps or something) then the second issue has been addressed. Then connect the charge controller between the two devices and slowly ramp the voltage up. At some point the PWM will start opening to limit the charge. Watch the output of the supply - if it's varying between ~14 and 19 volts, and the current is ramping up and down without big glitches or overshoots - and the supply is obviously not in distress* - then the first issue has been addressed.

                Or just get a charger.

                (* - distress defined as blown fuses, overheating, arcing, whining or clicking, or error indications.)

                Comment

                • inetdog
                  Super Moderator
                  • May 2012
                  • 9909

                  #23
                  Originally posted by burraak


                  So how do I know which power supply is made as current source and which one as voltage source? How do I recognize it ? because this info is something new to me I'm not an electronics expert Can you please explain this thing a little bit more ?
                  A power supply with 14 amp current output is suppose to be a good power supply to charge a 135AHr battery, Voltage in Meanwell 25V can be reduced to 19V and PWM will further decrease it around 14.4V therefore theoretically I was thinking of it as a perfect match
                  Very simple: Look for a power supply that has both a current limit adjustment AND a voltage adjustment. The current limit will protect the supply and the CC and will let the voltage go down when the current setting is reached. When the battery stops drawing high current (later stages of charging) the voltage limit will protect the battery from overcharging.

                  Some power supplies have a fixed (non-adustable) current limit which is there to protect the supply. If you hit that limit the voltage may drop to zero and require a manual reset.
                  SunnyBoy 3000 US, 18 BP Solar 175B panels.

                  Comment

                  • burraak
                    Junior Member
                    • May 2016
                    • 13

                    #24
                    Thank you everyone for taking your time in explaining the details and saving me from doing a blind shot ... really appreciate that ........