Wire gauge requirement for 24V 420AH battery bank and 1,500 Watt inverter?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Silver_Is_Money
    Solar Fanatic
    • Aug 2014
    • 148

    #1

    Wire gauge requirement for 24V 420AH battery bank and 1,500 Watt inverter?

    Can I use #3 AWG THHN wire to series connect 4 x 6V and 420 AH batteries to achieve 24V and then connect the bank to my 24V x 1,500 Watt (3,000 Watt surge) inverter by also using #3 AWG THHN? Or will I need to use #2 AWG for this application? Asking because I already have #3 AWG, but I would need to purchase #2 AWG.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    AWG Wire size chart and ampacity table for design engineers including skin depth frequencies and tensile strength data; electrical cable size


    3AWG is good for 75A, how far are the wire runs ?

    3Kw @ 24V is going to end up being 150A. That's closer to O gauge for low losses. Maybe 2 ga if your batteries are fresh and it's only a surge AND just a short run, but the voltage loss in the wire and battery bank will both get you.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • inetdog
      Super Moderator
      • May 2012
      • 9909

      #3
      If the area where the wire is installed is a wet or damp location, or the wire run is outside (even in conduit) wire which is ONLY labelled/listed as THHN will not be allowed. That wire type is for dry locations only.

      However, most of the THHN that you see in supply houses or stores is also rated as THWN or THWN-2, giving it approval for wet areas as well.
      SunnyBoy 3000 US, 18 BP Solar 175B panels.

      Comment

      • Silver_Is_Money
        Solar Fanatic
        • Aug 2014
        • 148

        #4
        I'm hoping to keep the wire runs down to 10 feet or less overall.

        Comment

        • Silver_Is_Money
          Solar Fanatic
          • Aug 2014
          • 148

          #5
          My inverter instructions recommend the use of #4 AWG, so by that measure wouldn't #3 AWG be offering a margin of safety and also a reduction in line loss?

          Comment

          • thastinger
            Solar Fanatic
            • Oct 2012
            • 804

            #6
            1008 watts is all you should pull from those batteries discharging them at a C10 rate so 3ga would be fine for a 10ft run of that.
            1150W, Midnite Classic 200, Cotek PSW, 8 T-605s

            Comment

            • Silver_Is_Money
              Solar Fanatic
              • Aug 2014
              • 148

              #7
              Originally posted by thastinger
              1008 watts is all you should pull from those batteries discharging them at a C10 rate so 3ga would be fine for a 10ft run of that.
              Thanks! Even C/8 is only 52.5 Amps (1,260 Watts).

              Since it is only a budget 1,500 Watt inverter I figured that any pull of greater than 1,500 watts for more than a very brief "surge" time will shut down the inverter with an overload. And 1,500 Watts / 24 Volts = 62.5 Amps, which is below the maximum 75 Amps rating of the #3 AWG. Now I'm doubting this and wondering if I actually need #2 AWG.

              Comment

              • sensij
                Solar Fanatic
                • Sep 2014
                • 5074

                #8
                Originally posted by Silver_Is_Money
                Thanks! Even C/8 is only 52.5 Amps (1,260 Watts).

                Since it is only a budget 1,500 Watt inverter I figured that any pull of greater than 1,500 watts for more than a very brief "surge" time will shut down the inverter with an overload. And 1,500 Watts / 24 Volts = 62.5 Amps, which is below the maximum 75 Amps rating of the #3 AWG. Now I'm doubting this and wondering if I actually need #2 AWG.
                Is your wire aluminum? Copper #3 has an allowable ampacity of 100 A.
                CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                Comment

                • Silver_Is_Money
                  Solar Fanatic
                  • Aug 2014
                  • 148

                  #9
                  Originally posted by sensij
                  Is your wire aluminum? Copper #3 has an allowable ampacity of 100 A.
                  It is copper. It will be fused at 100 amps (per the inverter instructions). But what if I do get a momentary surge to 3,000 Watts, which is 125 Amps, and the inverter does as it claims and takes this brief surge without tripping? And if the surge lasts more than a brief moment, will the ANL type 100 amp fuse blow before the #3 wire burns? This is why I'm having second thoughts about the #3 wire vs. #2.

                  Comment

                  • Naptown
                    Solar Fanatic
                    • Feb 2011
                    • 6880

                    #10
                    Originally posted by sensij
                    Is your wire aluminum? Copper #3 has an allowable ampacity of 100 A.
                    with not more than three current carrying conductors in a cable or raceway Free air is much higher and depends on the insulation on the wire.
                    NABCEP certified Technical Sales Professional

                    [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                    [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                    [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                    Comment

                    • sensij
                      Solar Fanatic
                      • Sep 2014
                      • 5074

                      #11
                      Originally posted by Naptown
                      with not more than three current carrying conductors in a cable or raceway Free air is much higher and depends on the insulation on the wire.
                      Although the conductor rating may be higher in free air, the termination rating will always be limited to 100 A (if marked), or 85 A (if not marked). 3 AWG copper is never compliant for a circuit over 100 A.
                      CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                      Comment

                      • sensij
                        Solar Fanatic
                        • Sep 2014
                        • 5074

                        #12
                        Originally posted by Silver_Is_Money
                        It is copper. It will be fused at 100 amps (per the inverter instructions). But what if I do get a momentary surge to 3,000 Watts, which is 125 Amps, and the inverter does as it claims and takes this brief surge without tripping? And if the surge lasts more than a brief moment, will the ANL type 100 amp fuse blow before the #3 wire burns? This is why I'm having second thoughts about the #3 wire vs. #2.
                        The fuse will protect the conductor. That is what it is there for. With a 100 A fuse, as long as your 3 AWG is in free air and has insulation rated at 90 deg, you should be fine.
                        CS6P-260P/SE3000 - http://tiny.cc/ed5ozx

                        Comment

                        • Silver_Is_Money
                          Solar Fanatic
                          • Aug 2014
                          • 148

                          #13
                          Originally posted by sensij
                          The fuse will protect the conductor. That is what it is there for. With a 100 A fuse, as long as your 3 AWG is in free air and has insulation rated at 90 deg, you should be fine.
                          It is THHN wire and it will be in free air. That is, if a battery box is considered to be free air. ???