I have a 4 year old, 24V bank of 20 Roll S-530's, charged by 2 stacked Xantrax and one Outback PV charge controller. There are five strings of 4 batts. Fo the last two year I have been charging them as Rolls recommends: charging at 15% of c6 rate which is 296 AH per battery, using their voltage settings. I usually charge the bank at 225ADC split between the two Xantrax, or about 112ADC each. The setting computation in AAC according to Xantrax is 25% for my 24V system, or 27AAC on the panel.
Problem: The generator runs too much. And for some time, batteries seem to be quite hot when charging, but I only have a thermostat in the middle string (and THAT seems to be the culprit!). I can barely get the bank up to 1.200 SG. The charging system was not originally set up for the aggressive charging that Rolls recommends. I suspect they were badly sulfated from undercharging for the first two years, and probably not watered well. I used the recommendation that Rolls has for corrective charging for heavy sulfation: equalize at 5% of c6 (1/3 normal rate) for as long as it takes to reach the charging system's max Volts of 32, then 4 more hours.
It looked good for a while. After 8 hours, the slow charge rate was keeping the batteries at 94F. I thought I could continue the process without the overheating I experience during normal equalization, and clean up the bank. Unfortunately, over the next 8 hrs, the middle string (ONLY the middle string) overheated, badly!
After 8 hours, V=27.2, T=94F, SG=1.146 (avg of 4 test cells)
After 8 more, V=25.1, T=150, SG=1.178.
SG went up in all but the overheated middle string, and overall volts was down.
What's going on?? The water in the other strings has some occasional bubbles, like you might see in a glass of resting soda water and was quite clear, and the strings were a balmy 95F. The middle string was gassing profusely: the color was muddy like when I do a normal equalization.
Why just the middle string? Any explainations?
I can't recondition the bank with the overheating. I'm thinking of removing the middle 4, and trying to recondition the rest.
Am I ever going to get this bank back into shape, or is it junk? Any suggestions?
BTW, I am using an expensive electronic SG gauge, so the reading are accurate.
Problem: The generator runs too much. And for some time, batteries seem to be quite hot when charging, but I only have a thermostat in the middle string (and THAT seems to be the culprit!). I can barely get the bank up to 1.200 SG. The charging system was not originally set up for the aggressive charging that Rolls recommends. I suspect they were badly sulfated from undercharging for the first two years, and probably not watered well. I used the recommendation that Rolls has for corrective charging for heavy sulfation: equalize at 5% of c6 (1/3 normal rate) for as long as it takes to reach the charging system's max Volts of 32, then 4 more hours.
It looked good for a while. After 8 hours, the slow charge rate was keeping the batteries at 94F. I thought I could continue the process without the overheating I experience during normal equalization, and clean up the bank. Unfortunately, over the next 8 hrs, the middle string (ONLY the middle string) overheated, badly!
After 8 hours, V=27.2, T=94F, SG=1.146 (avg of 4 test cells)
After 8 more, V=25.1, T=150, SG=1.178.
SG went up in all but the overheated middle string, and overall volts was down.
What's going on?? The water in the other strings has some occasional bubbles, like you might see in a glass of resting soda water and was quite clear, and the strings were a balmy 95F. The middle string was gassing profusely: the color was muddy like when I do a normal equalization.
Why just the middle string? Any explainations?
I can't recondition the bank with the overheating. I'm thinking of removing the middle 4, and trying to recondition the rest.
Am I ever going to get this bank back into shape, or is it junk? Any suggestions?
BTW, I am using an expensive electronic SG gauge, so the reading are accurate.
Comment