  • Copper Buss Bars

    I made some copper buss bars for my battery bank today. They are made from 1 1/4" x 1/4" solid copper and right now I have stainless steel 8mm "studs" installed to attach 6 batteries and I machined some insulating standoffs from Delrin for mounting . The center stud is longer as I plan on the inverter, MPPT charge controller, and IOTA battery charger connected to be connected to that point. Batteries will be wired to the bars with equal length cable.



    Buss bars 1.jpgBuss bars 2.jpg


  • #2
    Looks Nice! What's the amperage you're planning to run through the system? Any reason you didn't just order a pre-made busbar? (just curious - I make stuff I can buy sometimes just for fun)

    Comment


    • #3
      You made two mistakes.

      1. Should have made the bar two-hole connectors minimum.
      2. The big mistake you can fix. Drill those threads outs and use regular 3/8-inch or 1/2-inch Bolts, Nuts, Washers, and Locking Hardware. You cannot get enough torque to hold a connector tight enough, especially using one-hole connectors. I would not need any tools to break off any connection you can make with your setup.

      Never mind, just gofer it. You will learn later the hard way latter when connections fail.

      Last edited by Sunking; 10-08-2018, 10:44 AM.
      MSEE, PE

      Comment


      • #4
        A pair of holes assures the lug, bracket, or whatever cannot twist loose. The friction under
        a single bolt, maybe not. Probably more of a problem with bigger conductors. Bruce Roe
        Last edited by bcroe; 10-08-2018, 11:51 AM.

        Comment


        • #5
          If you strap the cables as they leave the bus bar and then tighten the bolts, that should help hold the tension.

          Comment


          • #6
            Originally posted by bcroe View Post
            A pair of holes assures the lug, bracket, or whatever cannot twist loose. The friction under
            a single bolt, maybe not. Probably more of a problem with bigger conductors. Bruce Roe
            That's a small part of it, but not the biggie. Surface Contact Area, and Pressure is what is lacking to obtain 25 micro-ohm or less contact resistance. Additionally threading the holes in the copper buss compounds the problem because you cannot tighten a bolt tight enough to keep a terminal from slipping and making good electrical contact.



            MSEE, PE

            Comment


            • #7
              Threads in copper cannot hold enough torque to be useful. You need thru-bolts as stated before, and should use anti-ox on the fittings, otherwise, the copper bar will oxidize and become useless.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment


              • #8
                Not sure why everyone is making a big fuss about threading the bus bar. OP referred to the bolts as "studs" which eludes to the fact that he will be containing the lugs under a nut. That will allow him to get the torque he needs, as the threads are essentially just holding the stud in place.

                Comment


                • #9
                  Originally posted by emartin00 View Post
                  Not sure why everyone is making a big fuss about threading the bus bar. OP referred to the bolts as "studs" which eludes to the fact that he will be containing the lugs under a nut. That will allow him to get the torque he needs, as the threads are essentially just holding the stud in place.
                  Maybe or maybe not.

                  Copper tends to flex and those threads are small and can easily move with can loosen up the connection when they experience hot and cold cycles.

                  It is better to use a stronger metal (then copper) bolt that has threads that allow you to torque the nut tight.

                  Comment


                  • #10
                    Originally posted by Sunking View Post

                    1. Should have made the bar two-hole connectors minimum.
                    Are you saying I should have cables with a lug that has two holes in it? I'm somewhat confused as no matter how many holes are in the bus bar the lug only has one...

                    The "bolts" are being used as studs and are 8mm stainless. The cables are torqued down tight with wave lock washers on top of flat washers. The threading in the bars doesn't do anything other than hold the bolts in place so I didn't loose them.

                    Connections 1.jpg

                    I have made Lexan "shields" to attach over the top of each bar but don't have them installed yet. Next trip I will wire-brush the bars and apply silicone grease where the lug mates with the bar.

                    Comment


                    • #11
                      He is referring to lugs that actually have 2 holes. They're common in big power applications in the electrical industry.

                      like these
                      https://atielectrical.com/wp-content...le_Long-18.jpg

                      I would find a way to secure the cables so they can't vibrate/swivel around and work loose.

                      How much amperage are you running through the lugs/bars?

                      Comment


                      • #12
                        Originally posted by Justin B. View Post
                        Are you saying I should have cables with a lug that has two holes in it? I'm somewhat confused
                        Confused how? Here is a #6 AWG two-hole compression terminal There is no possible way a single hole lug can match two-hole. There is over 300% more surface area and twice the pressure applied to surfaces that cannot be torqued off.




                        Last edited by Sunking; 10-09-2018, 12:20 PM.
                        MSEE, PE

                        Comment


                        • #13
                          So if it were me with what you have now I would make 3 corrections.

                          1. Drill the threads out just enough to allow your bolt to pass through with a snug fit.
                          2. Remove every thing from the Bus Bar, then take Green Scotch Brite and buff both the Buss Bar and Terminals to a nice shinny finish. Clean off with acetone. Be careful with the terminals not to buff down too far and remove the tin/lead plating. If you see red copper, you went to far.
                          3. Apply a very light coat of No-Ox-Id "A" Special made by Samchem to mating surfaces, hardware, and wire skinners.


                          I assume you know what is going to happen with a steal bolt threaded into copper right? If not you failed chemistry class. Well in about 6-months time or later will come a time when you need to remove a bolt and lug for maintenance. Good luck taking it apart. Your bolt will likely break apart as you apply torque because it has fused with the copper via electrolysis because you used dissimilar metal which made an Anode and Cathode. If you had used Straight Though Bolts with Antioxidant, you would have eliminated that failure point.

                          A tube of No-Ox will last well beyond your grand children life time long after you have turned to dust. I have battery plants that are 40 years old with absolutely no corrosion issues. It is the only product allowed to be used by utilities, CATV, Cellular, Telephone, Water Plants, Generation Plants, and Bridges.

                          No Ox is so good, they employed Cyclone Fence Company in NOLA to run a 50 year test. Back in the 70's they had Cyclone Fence put of a Chain Link Fence up at the factory. Heated up the No-Ox so it would liquidfy, diluted with acetone, and sprayed the fence. That fence has been submerged 3 times in sea water and blasted with God only knows how many hurricanes and to this day, no corrosion. Ever seen a 10 year old chain link near a coast?? Nope you have not unless it was protected somehow.



                          Last edited by Sunking; 10-09-2018, 12:53 PM.
                          MSEE, PE

                          Comment


                          • #14
                            Originally posted by Xplode View Post

                            I would find a way to secure the cables so they can't vibrate/swivel around and work loose.

                            How much amperage are you running through the lugs/bars?
                            I will add something to secure the cables to as I hadn't given any thought about them getting jarred and loosened.

                            As far as juice is concerned, not much as I am only supplying a 24V 1500W inverter so I guess around 60 - 65 amps max. I didn't make the bar with intentions of running tons of current through them but to hopefully help the parallel strings charge more evenly.

                            I have ordered a small jar of the compound referenced by sunking and will clean and reattach the cables as he described. I had always used silicone grease in the past and in the Army we used just wheel bearing grease on battery terminals!

                            As far as the double-holed terminals I had no idea such a thing existed so I have fulfilled today's requirement toward my lifelong philosophy of "learning at least one new thing per day."

                            Comment


                            • #15
                              Originally posted by Sunking View Post

                              A tube of No-Ox will last well beyond your grand children life time long after you have turned to dust. I have battery plants that are 40 years old with absolutely no corrosion issues. It is the only product allowed to be used by utilities, CATV, Cellular, Telephone, Water Plants, Generation Plants, and Bridges.





                              I just pulled my tube of No-Ox out the other day only to find the threaded nozzle had cracked off at the base. Probably the Baja summer heat degrading the plastic like every other plastic item that goes through a couple summers in Gods Furnace of Northeastern Baja.

                              Note to self.... Next time buy it in the tin can.