    DIY compression terminals on the left as good as high quality crimped on the right??

    which is better?
  • organic farmer
    Solar Fanatic
    • Dec 2013
    • 644

    #2
    I used the 'crimp-on' style and I soldered them on.
    4400w, Midnite Classic 150 charge-controller.

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      Nothing beats a proper hydraulic crimp (15 ton) connection, it is gas tight and the strands and shell are cold welded all together. The "twist to compress" cannot get anywhere near that performance.

      I always warn about soldering connectors that are supposed to be crimped:
      1) solder wicks up the stranded cable to some point, and then stops there. That makes a rapid transition in the flexibility of the cable, and the cable will break internally at that point, over time and with very little flexing needed.
      2) Solder has a higher resistance than copper wire, so under high current conditions, the solder will heat up. Enough current and enough time, the solder will melt and the cable can fall off, letting molten solder and hot cable rattle around
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • Fireside
        Junior Member
        • Dec 2018
        • 20

        #4
        I realise I'm digging up a post from last year here.. But I wanted to know about Crimping + soldering. I'm looking at crimp terminals that have a window in the end. And was planning to crimp the cable into the terminal properly, then backfill the very tip of the cable with solder through the window, with a view to eliminating any oxygen presence in the end of the terminal.
        If done correctly the strands will be effectively cold welded into a solid with the terminal casing where crimped. So with that in mind, it's unlikely/impossible for solder to wick beyond the very tip of the cable where it is still strands.

        Overkill? Introducing a failurepoint? What are your thoughts on end-solder after crimp.

        Comment

        • Ampster
          Solar Fanatic
          • Jun 2017
          • 3649

          #5
          I agree with Mike. Hydraulic crimping is the best.
          9 kW solar, 42kWh LFP storage. EV owner since 2012

          Comment

          • Fireside
            Junior Member
            • Dec 2018
            • 20

            #6
            Originally posted by Ampster
            I agree with Mike. Hydraulic crimping is the best.
            I think we are all in agreement that properly crimped connections are a must. But from an ultimate corrosion prevention point of view, I'm still interested in backfilling the terminal casing from the lug end.

            Comment

            • Ampster
              Solar Fanatic
              • Jun 2017
              • 3649

              #7
              Originally posted by Fireside

              I think we are all in agreement that properly crimped connections are a must. But from an ultimate corrosion prevention point of view, I'm still interested in backfilling the terminal casing from the lug end.
              Yes, I have no disagreement with that since it is your time. I have done that in the past and capillary action wicked the solder further up the wire than I expected but maybe I was too liberal in feeding the solder to the joint. For simplicity. if corrosion is a concern I have used a conductive grease for corrrosion protection. Those cases were in a motive application for an EV and it was 4/0 welding cable that would have taken a torch to heat up. I also used shrink wrap with a glue inside to seal the fitting.
              Last edited by Ampster; 08-21-2019, 11:34 PM.
              9 kW solar, 42kWh LFP storage. EV owner since 2012

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                Like Ampster states, I've seen solder wick into places it should not have. Even aircraft wire harnesses are crimp only. They see daily thermal excursions and condensation and the 22ga wire does just fine - when properly crimped.
                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • emartin00
                  Solar Fanatic
                  • Aug 2013
                  • 511

                  #9
                  Originally posted by Fireside
                  I realise I'm digging up a post from last year here.. But I wanted to know about Crimping + soldering. I'm looking at crimp terminals that have a window in the end. And was planning to crimp the cable into the terminal properly, then backfill the very tip of the cable with solder through the window, with a view to eliminating any oxygen presence in the end of the terminal.
                  If done correctly the strands will be effectively cold welded into a solid with the terminal casing where crimped. So with that in mind, it's unlikely/impossible for solder to wick beyond the very tip of the cable where it is still strands.

                  Overkill? Introducing a failurepoint? What are your thoughts on end-solder after crimp.
                  I would suggest either getting lugs without the inspection window, or simply putting a drop of No-ox in the window and covering it with a bit of electrical tape.

                  Comment

                  • bcroe
                    Solar Fanatic
                    • Jan 2012
                    • 5198

                    #10
                    I have used liquid tape, often covering that with heat shrink which may bring
                    some of it out both ends. Bruce Roe