The primary value of my original post is the Sandia report's conclusion that lead acid charging efficiency drops to 55% at a little more than 80% SOC. That means the last bit of charging really does take "forever".
Try our solar cost and savings calculator
What is wrong with wiring batteries in parallel?
Collapse
X
-
Right. But that's not a string. A string is a series connected set of batteries.
-
The term string refers to series wired, batteries, in this case. A group of paralleled batteries, no matte how long, is not a string.Leave a comment:
-
DIY systems are often 12 volts (all the available 12 volt appliances and accessories) with multiple batteries in parallel. That is where you find the parallel "string the length of the shelf". Some of the 12 volt systems using 6 volt golf cart equivalent batteries are also "the length of the shelf". Nothing to do with detailed design or engineering in these small systems, just wherever the space and the $$$ cross.
My comments are an aside. The primary value of my original post is the Sandia report's conclusion that lead acid charging efficiency drops to 55% at a little more than 80% SOC. That means the last bit of charging really does take "forever".
Leave a comment:
-
Leave a comment:
-
In amongst the angst, there was a mention of the time it takes to *fully* charge a lead acid battery. Have you read this paper from Sandia National Laboratories?
http://www.otherpower.com/images/sci...Efficiency.pdf
The "Conclusions" section tells us much.
I've seen "Not more than two strings in parallel" many times, but then you're faced with the question "How long is a string?" DIY systems are likely to have a string length that fits on the available shelf.
My solar power is currently a "Wait until daylight" solar charged generator with 504AH of 12HX330FR AGM (six 84AH batteries cost me a total of $235 used in year 5 of a 10 year projected service life and I've had the use of and the opportunity to learn about those batteries while planning their future replacement - relatively cheap education and it appears that at least 3 of those batteries might make 10 years). The 2000 watt pure sine wave inverter powers the fridge, a few LED lights and internet access plus the furnace in winter, giving 10 to 24 hours of silent power depending on the season. In a longer outage, all 1600 watts of solar would be in place on 6 MPPT controllers (I like redundancy) to provide some level of power in the long term.
No impressive initials (BS Information Systems, but consider the connotations of "information"). Now retired for the fourth or fifth time and writing fiction:
MOD NOTE. Please do not attach advertisement links for your products to your post.Leave a comment:
-
For someone who claims to be a battery expert ask some really ignorant questions. Equalization is a controlled over charge and is only performed when specific gravity spread is greater than .030 among all cells. Only a daily cycled Pb battery gets EQ every couple of months. Pb batteries in Float Service never requires EQ. Corrosion of the grids are created by voltages above 2.45 volt @ 77 degree F for extended periods of time. That does not happen with a Solar system. Pb batteries charge at 2.4 vpc ... Grid corrosion is a problem with automobiles. Autos do not lower the voltage to 2.25 volts aka FLOAT.
I was not talking about Equilising LA batteries, I was talking about limiting the absorb phase to limit the grid corrosion and water loss.
This is what Battery University has to say on the subject
"The correct setting of the charge voltage limit is critical and ranges from 2.30V to 2.45V per cell. Setting the voltage threshold is a compromise and battery experts refer to this as 'dancing on the head of a needle'. On one hand, the battery wants to be fully charged to get maximum capacity and avoid sulfation on the negative plate; on the other hand, over-saturation by not switching to float charge causes grid corrosion on the positive plate. This also leads to gassing and water-loss
You, yourself say the same thing regarding LA batteries being charged in cars.
I was stupidly hoping that by starting this tread that there could be a rational discussion about the different issues involved with paralleling batteries and how to circumvent them but it appears not to be the case.
No. Nor can it be done with a lithium battery. You would never know when the cell is fully charged. Both charge the exact same way, there is no difference. On a 4S lithium or 12 volt PB you apply 14.4 volts and charge until charge current tapers to C/33 to C/20. Just for you that means 3 to 5% of C. At C/50 to C/100 you would never be able to detect full charge.
Difference would be a lithium battery would be destroyed leaving a 4S at 14.1 volts after it charged up. Quite possible catch fire from thermal runaway. A lead acid battery would be just fine with it and need a drink now and then.
Leaving both 12V LA and LFP batteries at 14.1 volts for extended periods would I think be bad for them.
FWIW C/50 to C/100 is not a charger. It is a Trickle Charger. Any battery expert would know that. In any solar application minimum charge rate is going to be C/10 or higher.
Minimum charge rate for solar applications is nearly zero at sunrise and sunset.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controllerLast edited by karrak; 01-20-2018, 06:17 PM.Leave a comment:
-
So the answer to your question is: irrelevant and insignificant. EQ is only done when needed infrequently. Just like lithium batteries, fully charging and equalization stresses the batteries. The difference is Pb batteries are brutes and extends battery cycle life by dissolving lead sulfate crystals. Lithium on the other hand shortens battery life.
FWIW C/50 to C/100 is not a charger. It is a Trickle Charger. Any battery expert would know that. In any solar application minimum charge rate is going to be C/10 or higher.
Last edited by Sunking; 01-18-2018, 04:33 PM.Leave a comment:
-
I was under the impression that overcharging LA batteries was bad for them due to grid corrosion, is this only a fairy minor issue?
By using external active balancing I would have thought you would be helping to avoid both overcharging and undercharging. Of course whether this is practicable or not has to be considered.
A question, is charging to say 2.35V/cell with a low termination current of say less than ~C/50-C/100 a reliable way to fully charge a LA battery?
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controllerLeave a comment:
-
I wonder if the same issues occur with cells in series as in parallel. With cells in series as you say the same amount of charge has to go through all the cells. Unless all the cells in series have the same capacity and same charge efficiency some will end up being overcharged and some undercharged.
I wasn't thinking about keeping the voltage the same but more about actively shifting charge from cells that have reached the absorb voltage early and during absorb actively pushing extra charge into the cells which are staying at a lower voltage rather than letting the voltage rise in some cells to the point where they outgas. That is why I specified active balancing.
However, again, you can't say "oh, that cell is at 2.35V so it's fully charged, any more charging and it will outgas." You can measure with a hydrometer (most accurate) or you can charge until you know it's at 100%. So traditional voltage balancing won't be as effective as it is for (say) lithium ion.
Leave a comment:
-
Series string lead acid batteries have a mechanism where you can guarantee 100% charge on all batteries by effectively overcharging some cells. Since all cells see the same current, you can guarantee this by providing X coulombs to the battery. Of course, overcharging 'uses up' water, so equalizing charges - or even long absorption charges - can reduce life as well. So that's a tradeoff.
That assumes that keeping lead acid batteries at the same voltage is the same as keeping them at the same state of charge. That is less true of lead-acid than it is of other chemistries (like lithium ion.) It will prevent damage by preventing cell voltages below (for example) 1.75 volts, but will not guarantee full charge.
These sort of issues don't arise with lithium ion batteries. With lithium ion batteries you still want to make sure that the cell interconnections don't result in current imbalance.
I am yet to be convinced that you can't mix lithium ion cells of different ages and impedances in parallel as they will automatically share the current dependant on their individual SOC and impedance. With LA batteries you would not want to mix cells with different characteristics for the reasons we have been discussing.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controllerLeave a comment:
-
Series string lead acid batteries have a mechanism where you can guarantee 100% charge on all batteries by effectively overcharging some cells. Since all cells see the same current, you can guarantee this by providing X coulombs to the battery. Of course, overcharging 'uses up' water, so equalizing charges - or even long absorption charges - can reduce life as well. So that's a tradeoff.
Parallel strings do not have this mechanism, and indeed the weak cells see less charge current due to Kirchoff. So they tend to not see 100% charges.
Again, in applications where you can float forever, eventually all cells will reach 100%. But that's not how RE systems are used.
I would have thought that having a BMS with active balancing where charge is electronically shunted between cells could improve the life of LA batteries over just relying on passive balancing as used at the moment.Last edited by jflorey2; 01-17-2018, 01:45 PM.Leave a comment:
-
As Mike, Jflorey, and I have said many times to you there is absolutely no reason or excuse to parallel Pb batteries in a solar system. They come in every size from 10 AH to 6000 AH.
200 AH and less Pb batteries come in in 12 and 6 volt blocks. 200 to 800 AH come in 6 volt blocks, 600 to 1000 AH come in 4 volt blocks. 800 to 6000 AH come in 2 volt cells with a back breaking 900 pounds for a 2 volt 6000 AH cell.
Having said all that based on the largest controller you can buy, 80 to 100 amps, and a 48 volt maximum battery voltage limit to remain under the 50 volt NEC limit for exposed electrical parts, the largest battery you can have is 800 AH. That would take a 4000 to 5000 watt panel system. You would have to be a fool to use 4-strings of 12 volt 200 AH batteries. Do you have any clue what the Wiring and OCPD would cost would be? Not too mention the frequent battery replacement cost would be going parallel? Nope you do not have a clue. Smart money would use something like Rolls 6CS25P 5000 series and comes with a real Battery Manufacture 10 year Warranty that will actually be honored and last longer than any lithium. The Chi-Com Winston Lithium Batteries you sell and use DO NOT HAVE A WARRANTY. Go to Winston's website and search for Warranty. It does not exist.Last edited by Sunking; 01-17-2018, 01:53 PM.Leave a comment:
-
Active Balancers (and shunting) add a lot of complexity and parts, with each part added, adding to the failure rate of the Balancer system. As noted before, poorly engineered balancer failures ruin many cells.
Leave a comment:
-
If you were a real engineer like you claim, and had any real experience with batteries, you would understand Ohm' Law and know parallel blocks of batteries resistance cannot be equalized and that it is impossible to do so. You have proven time and time again you do not understand battery Internal resistance, and cable/connection resistances. Ohm's Law is first week electrical 101 every student gets drilled with by doing thousands of equations until they completely understand. If not, they drop out and go to cooking school.
As I have told you hundreds of times and now Jflorey is telling you, both of us are real engineers telling you the exact same thing. In a Standby Emergency Standby Battery plant used in UPS and Telecom, you can certainly use parallel battery blocks (more than one cel in series like a 4,6, 8, or 12 volt Pb batteries. Those type of plants are called FLOAT plants that rarely ever get used and the batteries will equalize of a period of DAYS.
In a cycle application where the battery is cycled every day you DO NOT HAVE THE LUXURY OF TIME. Solar is even MORE TIME LIMITED to a few brief hours each day, you cannot get away with Parallel Battery Blocks.
We all understand it is not always possible, well those of us with experience, to obtain a specific AH capacity with a single cell. However there is a right way and wrong way to parallel batteries and that is on a CELL LEVEL not BLOCK LEVEL. Every commercial EV made does that. Example a Tesla Roadster uses 99S69P or 6,831 18650 cells and uses a 99 channel BMS. All 69 cells are in parallel @ 3.6 volts, not 7.2 or 14.4, or 28.8 volt blocks. The exact same thing can be done with any battery type, even PB but would be done with 2 volt batteries, not 4, 6, 8, or 12 volts.
Perhaps your brain can only understand pictures.
The long absorb time necessary to properly charge LA batteries can be a real problem with solar systems, another good reason not to use LA batteries in off-grid systems.
You still haven't answered the question why it is wrong to parallel at a block level and left one very important thing out of your diagram, the balancing circuitry that balances the individual cells within the block.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controller
Leave a comment:
-
The problem is that all batteries have slight differences in their internal impedance. A slightly higher than normal internal impedance will, over time, result in less charge current to that battery, thus resulting in a lower average SoC. This in turn will tend to age the battery faster, increasing its internal impedance.
You can get around this by charging batteries long enough that all the batteries really _do_ reach the same SoC - but that can take a long time (days.) That's why UPS systems generally don't have this problem. But RE systems, that are cycled every day and often don't sit at 100% SOC for any length of time, can get out of balance quickly.
In the situation where there is enough absorb time to fully charge the weak cells which of course will be overcharging the other cells I would have thought that this plus the decreased stress on the weaker cells due to the lower charge/discharge current will tend to degrade the better cells at a faster rate so that the cells impedance and SOC will tend to balance out over time.
I agree that keeping LA batteries equalised/balanced and for that matter lithium ion batteries is important for longer lifespan. In the case of lithium ion batteries, making sure that all the cells are charged to the same voltage is an important factor to maintain equal stress on all the cells.
I would have thought that having a BMS with active balancing where charge is electronically shunted between cells could improve the life of LA batteries over just relying on passive balancing as used at the moment.
Simon
Off grid 24V system, 6x190W Solar Panels, 32x90ah Winston LiFeYPO4 batteries installed April 2013
BMS - Homemade Battery logger github.com/simat/BatteryMonitor/wiki
Latronics 4kW Inverter, homemade MPPT controllerLeave a comment: