    Battery protection automatic cut-off

    I'm planning to install a battery guard, something like the Morningstar driver relay but that solution is a little pricy for the objective.

    Does someone know of a simple, cheap way to shut down the inverter at a PERSONALIZED voltage?

    I was reading of an automotive gadget at about 50 USD but it's fixed to 12V.

    The inverter does it also but at about 10.5V what is far to much in my opinion, I don't wanna open that thing and try out all potenciometers till finding the right one, maybe I never get the right and blow the whole thing, lol.

    All that happens if you are a cheap bastard , some Xantrex inverters can adjust the shut off position.

    Thanks for any hint

    Joe
  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    Well a lot of inverters have auto shutdown.
    MSEE, PE

    Comment

    • ecusolar
      Solar Fanatic
      • Dec 2009
      • 125

      #3
      Yeah, but they shut down when they want, not when I want.

      I would like to cut-off at 11.6V about.

      There must be some cirquits that can drive a relay to personalize the voltage.

      Comment

      • ecusolar
        Solar Fanatic
        • Dec 2009
        • 125

        #4
        If we can find a cheap but reliable gadget could be very useful for DIY projects.

        For example you could use one to switch to a grid inverter when your batteries are fully charged for not to waste the solar production.

        A generator battery could give an alarm when discharged cause of few use etc.

        It hurts having a diesel generator and when you need it, the bloody starter battery is dead.

        There are simple battery monitors that show a different LED depending on the charge, those could drive a relay instead of the LED

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          This becomes a mind set problem. You start with a set of training batteries and you have to learn not to kill them. You need to monitor your power usage, and delay high power stuff till an afternoon after your batteries are out of the BULK mode. Things that you want to not run at night or early AM, put a timer on them.
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Originally posted by ecusolar
            I would like to cut-off at 11.6V about.
            You need to rethink this a bit because it is flawed. You never want to go below 50% DOD which for Flooded Lead Acid batteries is 2.033 volts per cell, so for a 12 volt battery is 12.2 volts.

            At 100% DOD or 0% charge is 1.966 vpc or 11.8 volts for a 12 volt battery. At 11.6 is well beyond completely discharged at rest.
            MSEE, PE

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              It's also very hard to set a cut-off point, because the cell voltage is lower, depending on the drain at the time. You need to let the battery bank idle for about 2-3 hours before the voltage is a good indicator of State Of Charge.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • ecusolar
                Solar Fanatic
                • Dec 2009
                • 125

                #8
                I'm sure it can be done

                Thanks friends.

                Your posts gave me more reasons to worry about a good gadget as most cheap inverters cut at 10.5V.

                Temporally I solved the problem with a Morningstar PS30 charge/load controller which cut-off at 11.4V.

                I have a conversation with a company in UK which offers a personalized LVD gadget with time delay for about 20 USD.

                I really would love to have a simple circuit to drive a voltage driven relay, other use would be the folks that have a DJ in car, it would not be the first time I see them at Saturday night asking for a jump start.

                Comment

                • ecusolar
                  Solar Fanatic
                  • Dec 2009
                  • 125

                  #9
                  Originally posted by Sunking
                  You need to rethink this a bit because it is flawed. You never want to go below 50% DOD which for Flooded Lead Acid batteries is 2.033 volts per cell, so for a 12 volt battery is 12.2 volts.

                  At 100% DOD or 0% charge is 1.966 vpc or 11.8 volts for a 12 volt battery. At 11.6 is well beyond completely discharged at rest.
                  That's exactly the reason for a unit I'm thinking of, the controllers and inverters cut-off to late, Mike and Dereck.

                  I want a unit that is personalizeable like the Morningstar relay driver but in a more economic way.

                  Sorry if I'm thinking out of the box.

                  Joe

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #10
                    Originally posted by ecusolar
                    Sorry if I'm thinking out of the box.
                    Joe you are actually asking very good questions. You are starting to gain experience and asking the right questions.

                    As you hav e noticed many charge controllers have LVD outputs, some are programmable. Problem is if you use the LVD output severely limits output current, so serving large loads like an inverter is just not possible.

                    As Mike stated using SOC (state of charge) voltages is practically useless for live operating systems, and only useful for rested batteries of several hours which is not practical.

                    I do not know of any add on devices on the market made to do what you want. For an example a black box that is installed say between the batteries and inverter. I know some inverters have built in LVD and some of the higher end models can be programmed.

                    Now with that said if you have time to do homework, have mechanical and fabrication skills, they are pretty easy to make. It involves a few electronic discreet components to kake a voltage comparator to operate a relay to open the circuit when a low voltage is detected, and reconnect when the voltage is higher.

                    Do a little research on Google for voltage comparator circuit or even Low Voltage Disconnect circuits. Heck if i was not so busy and had time I could find or design one quickly, but it would be up to you to build at your own risk.

                    Maybe a guy by the name of John p might see this and probable already has a few as they are a common circuit as most just use a single Integrated Op-Amp, a few passive components like resistors and zener diodes, and a driver transistor to operate a relay. The trouble you could yourself into is not knowing what size wire to use to handle high currents safely and end up burning up you work or worse. Nothing is more frustrating working for hours, than letting out the magic smoke.

                    One last mote, there might even be such a product on the market. It is just something I have not ever looked for or had a need for it as most of my work is with telephone companies which hate LVD devices.

                    As for economics, you are going to have to bite the bullet and ask yourself which is more important. Sacrificing your battery or buying insurance to maximize battery life. IMHO a good LVD is a wise investment. So my recommendation is to purchase a quality inverter with built in programmable LVD.
                    MSEE, PE

                    Comment

                    • ecusolar
                      Solar Fanatic
                      • Dec 2009
                      • 125

                      #11
                      Thanks Dereck and Mike

                      Thanks for the complete reply Dereck.

                      What Mike said makes sense, I can have 11V under load, cut the load and the battery is coming back to let

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #12
                        [QUOTE=ecusolar;20396] What Mike said makes sense, I can have 11V under load, cut the load and the battery is coming back to let
                        MSEE, PE

                        Comment

                        • ecusolar
                          Solar Fanatic
                          • Dec 2009
                          • 125

                          #13
                          Yup, I'll wait for what this guys can offer, hope it's OK to link there: http://www.reuk.co.uk/Low-Voltage-Ba...t-Circuits.htm

                          I'm waiting for a reply to my request, will let you know what they say.

                          Comment

                          • Naptown
                            Solar Fanatic
                            • Feb 2011
                            • 6880

                            #14
                            Originally posted by Sunking
                            You need to rethink this a bit because it is flawed. You never want to go below 50% DOD which for Flooded Lead Acid batteries is 2.033 volts per cell, so for a 12 volt battery is 12.2 volts.

                            At 100% DOD or 0% charge is 1.966 vpc or 11.8 volts for a 12 volt battery. At 11.6 is well beyond completely discharged at rest.
                            Grid tie guy here
                            But when the inverter is under load wouldn't the voltage be lower than the voltage at rest and setting the cut out point lower under load would be the same as a higher at rest voltage?
                            NABCEP certified Technical Sales Professional

                            [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                            [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                            [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by Naptown
                              Grid tie guy here
                              But when the inverter is under load wouldn't the voltage be lower than the voltage at rest and setting the cut out point lower under load would be the same as a higher at rest voltage?
                              Yes sir, it is called SAG. Batteries have internal resistance, thus voltage drop proportional to the amount of current and resistance of the battery.
                              MSEE, PE