Adding more batteries to an existing off-grid system?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • JohnnyR
    Junior Member
    • Aug 2016
    • 2

    Adding more batteries to an existing off-grid system?

    Can someone explain why it is not recommended to add more batteries to an existing off grid system? I have 24 Werbat 8 SPzS 720 batteries which on a sunny day are fully charged by mid afternoon so a lot of solar production is going to waste. Why can i not just increase the battery bank to give me a greater reserve for the evenings?
  • organic farmer
    Solar Fanatic
    • Dec 2013
    • 644

    #2
    There is a thought that you current old batteries will cause the new batteries to age prematurely.
    4400w, Midnite Classic 150 charge-controller.

    Comment

    • solarix
      Super Moderator
      • Apr 2015
      • 1415

      #3
      The charging characteristics of the new batteries will be different than the old ones (even if the same make and model) leading to non-optimum charging. The old ones will be overcharging while the new ones will be undercharged. You won't get a full charge capacity out of either one and their lifetime will be reduced. Its the perennial battery problem and what else you gonna do?
      BSEE, R11, NABCEP, Chevy BoltEV, >3000kW installed

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15125

        #4
        While most used FLA type batteries will shorten the life of new FLA batteries (due to build up resistances) those SPzS seem to be built a little different and may not have the same affect on new ones when you add them to old ones if they have not been discharged very deeply.

        They are very impressive but I would imagine also very expensive compared to something like the Trojan 2V 720Ah battery.

        But then again I am not a battery expert by any means.

        Comment

        • JohnnyR
          Junior Member
          • Aug 2016
          • 2

          #5
          Thanks for responses, but how much shorter will it make the new batteries lives?

          Comment


          • Wy_White_Wolf
            Wy_White_Wolf commented
            Editing a comment
            To less than the remaining life of the old batteries. It also shortens the life of the old batteries. How much depends on the resistance differences of the strings.

            So if you had a 2 year old bank that you expected to last 5 years it would have 3 years left. Adding another string could easily cut it's life down to 2 years and the life of the new string would only be 2 years.

            WWW
        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #6
          Originally posted by JohnnyR
          Can someone explain why it is not recommended to add more batteries to an existing off grid system? I have 24 Werbat 8 SPzS 720 batteries which on a sunny day are fully charged by mid afternoon so a lot of solar production is going to waste. Why can i not just increase the battery bank to give me a greater reserve for the evenings?
          Adding batteries does NOT eliminate waste silly, it compounds the issue and makes it worse.

          All Off grid systems have to be over sized with a lot of waste especially during the longer days of summer. It is one of the reasons you should never go off grid. Doing so makes you a heavy polluter, waste resources your kids cannot use, and cost you a fortune. That is what you chose to do, waste energy, waste resources and throw money away. when you went off-grid.

          The solution is getting rid of some of your panels, or use more electricity. Adding batteries does nothing. You could double the capacity of the batteries, and by noon they too will be recharged. Your panels only replace what you use each day.

          If you use say 2 Kwh each day, but your panels can generate up to 4 Kwh each day. So if you have a 10 Kwh battery, use 2 Kwh takes you down to 8 Kwh, then the panels generate 2 Kwh to bring the battery back up to 10 Kwh.

          So you get the bright idea to increase the size of your battery to 15 Kwh. So you use 2 Kwh which takes the batteries down to 13 Kwh, then the panels replace the 2 Kwh to bring it back up to 15 Kwh.

          Nothing changed except you lost a lot of money buying batteries you have no use for. What will make you even happier is when you added the new batteries wil only last as long as th eold ones so you get to spend a lot of money replacing even more batteries. That will make you real happy loosingg g alot more money faster. It should make you happy because you went off-grid to waste money and resources.
          Last edited by Sunking; 08-25-2016, 11:27 AM.
          MSEE, PE

          Comment


          • JohnnyR
            JohnnyR commented
            Editing a comment
            I didn't have a choice to go off-grid. The electricity company do not supply to our area. Thank you for your semi-constructive comment but if I wanted replies like this I would have gone elsewhere
        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #7
          Don't let the door hit you in the butt on the way out. If you went elsewhere, you would not have got the correct answer in a short time. All other sites are ran by companies who will tell you what you want to hear, then sell the solution to you sucker. I just saved you a ton of cash. You should be saying Thank You not FU.

          You have a Non Problem or Make Believe problem. All off grid systems have to be over sized by design. .
          Last edited by Sunking; 08-25-2016, 11:41 AM.
          MSEE, PE

          Comment


          • JohnnyR
            JohnnyR commented
            Editing a comment
            You've said me jack sh*t bud. Just been rude so I'm saying FU

          • dapago
            dapago commented
            Editing a comment
            Is there a way to ban this "Suking" member from this site? Too many insults to too many members....
        • J.P.M.
          Solar Fanatic
          • Aug 2013
          • 14925

          #8
          Originally posted by JohnnyR
          You've said me jack sh*t bud. Just been rude so I'm saying FU
          Guess you can't please everyone.

          Was it something SK wrote (that does happen once in a while), or did you miss your meds or Wheaties today ?

          Comment

          • organic farmer
            Solar Fanatic
            • Dec 2013
            • 644

            #9
            The ideal sweet spot for battery capacity is how many days you need to go on battery charge without recharging.

            PoCo normally goes dark every year for four to five days in my town, once maybe twice a year. Since I have lived here, I have never experienced any PoCo outage to last 6 days here. There are always news reports of towns losing power for longer. But my town is not very remote, so we always get our grid back up in less than 6 days.

            Therefore the ideal battery size in our town is determined by daily need X 5 days.

            With such a battery capacity the usual monthly PoCo outages once or twice a month of 6 hours to 2 days duration are normal hiccups that do not become a crisis.

            That is how you determine battery size.

            An unusual power outage crisis is inherently difficult to plan for. By the nature of being unusual events. you can not easily predict how long the PoCo will take to get their heads out of their arses. It is easiest to look at normal Poco outages, what normally happens every month 6 hour to 2 days outages, and what normally happens every year in this case 4 to 5 day outages, and you plan from there.






            4400w, Midnite Classic 150 charge-controller.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #10
              At some point, instead of buying more and more batteries, getting a generator & charger to keep a smaller bank, becomes more efficient, As outages get longer, and fuel costs go up, solar becomes a better way to recharge
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • organic farmer
                Solar Fanatic
                • Dec 2013
                • 644

                #11
                During our first 8 years living here. We did not have a generator. Most homes here do. But we just tried to live on grid with the outages. We were tempted a few times to get a generator, but talking to neighbors, the amount of fuel generators consume is a lot. You may commonly go through $1000 / year [of more] in fuel for the darn thing.

                That was what eventually convinced us to go with solar.
                4400w, Midnite Classic 150 charge-controller.

                Comment

                • ddrbnn
                  Junior Member
                  • Oct 2021
                  • 2

                  #12
                  Originally posted by Sunking
                  Adding batteries does NOT eliminate waste silly, it compounds the issue and makes it worse.

                  All Off grid systems have to be over sized with a lot of waste especially during the longer days of summer. It is one of the reasons you should never go off grid. Doing so makes you a heavy polluter, waste resources your kids cannot use, and cost you a fortune. That is what you chose to do, waste energy, waste resources and throw money away. when you went off-grid.

                  The solution is getting rid of some of your panels, or use more electricity. Adding batteries does nothing. You could double the capacity of the batteries, and by noon they too will be recharged. Your panels only replace what you use each day.

                  If you use say 2 Kwh each day, but your panels can generate up to 4 Kwh each day. So if you have a 10 Kwh battery, use 2 Kwh takes you down to 8 Kwh, then the panels generate 2 Kwh to bring the battery back up to 10 Kwh.

                  So you get the bright idea to increase the size of your battery to 15 Kwh. So you use 2 Kwh which takes the batteries down to 13 Kwh, then the panels replace the 2 Kwh to bring it back up to 15 Kwh.

                  Nothing changed except you lost a lot of money buying batteries you have no use for. What will make you even happier is when you added the new batteries wil only last as long as th eold ones so you get to spend a lot of money replacing even more batteries. That will make you real happy loosingg g alot more money faster. It should make you happy because you went off-grid to waste money and resources.
                  Sunking I share a very similar question as the OP's, but i'm pretty sure i have a good reason for wanting another battery. I'm living in a van with a few solar panels up top. My problem is that my batteries are filled up to 100% during the day and I'm running out of juice in the night, so in my case I think it makes sense to add another battery. I have a friend that has the same batt's as me and just dumped them for some newer ones -- would I be able to add one of my friend's used batteries to my existing system and have that benefit me? Is there something I don't know about how that will degrade my other batteries even more?

                  Comment

                  • SunEagle
                    Super Moderator
                    • Oct 2012
                    • 15125

                    #13
                    Originally posted by ddrbnn

                    Sunking I share a very similar question as the OP's, but i'm pretty sure i have a good reason for wanting another battery. I'm living in a van with a few solar panels up top. My problem is that my batteries are filled up to 100% during the day and I'm running out of juice in the night, so in my case I think it makes sense to add another battery. I have a friend that has the same batt's as me and just dumped them for some newer ones -- would I be able to add one of my friend's used batteries to my existing system and have that benefit me? Is there something I don't know about how that will degrade my other batteries even more?
                    Anytime you add an old battery to a new system the entire system drops down the the health of the oldest battery. Then you end up with an early death.

                    On top of adding a battery you also have to make sure you have enough charging amps from your existing solar panels. If not then you need to add additional panel wattage to increase your charging amps going into the battery system.

                    But another solution is to find a way to reduce your nightly load and not kill off your batteries.

                    Comment

                    • ddrbnn
                      Junior Member
                      • Oct 2021
                      • 2

                      #14
                      So the reason my batteries are getting too drained at night is because they’re also getting old. The question i’ve been having a hard time finding the answer to is: Does it make sense for me to add an old battery to an existing battery bank (that is already composed of old batteries)?

                      Comment

                      • Mike90250
                        Moderator
                        • May 2009
                        • 16020

                        #15
                        how many batteries in your existing battery bank ?
                        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                        solar: http://tinyurl.com/LMR-Solar
                        gen: http://tinyurl.com/LMR-Lister

                        Comment

                        Working...