If you charge at less than C/12 for FLA batteries, you end up stratifying the electrolyte in a stationary battery. Kind of like never shaking a bottle of oil and vinegar dressing. Your salad will eventually sulfate. 
Although you plan to hit the bank up with the genny when it reaches 75% SOC, there may not be enough charge time for it to fully destratify what you've done with the low current charging in the previous days. A one-off situation might not be so bad, but for day in day out, I think the effects will be cumulative. What you save in proper panel wattage is cancelled out by having to buy batteries a bit sooner.
Also consider that low-current charging means that the charge never goes deep into the plates, but is mostly is a surface charge, and you may not be able to sustain a large load, and when you try, the surface charge depletes and your voltage crashes fast.
Although you plan to hit the bank up with the genny when it reaches 75% SOC, there may not be enough charge time for it to fully destratify what you've done with the low current charging in the previous days. A one-off situation might not be so bad, but for day in day out, I think the effects will be cumulative. What you save in proper panel wattage is cancelled out by having to buy batteries a bit sooner.
Also consider that low-current charging means that the charge never goes deep into the plates, but is mostly is a surface charge, and you may not be able to sustain a large load, and when you try, the surface charge depletes and your voltage crashes fast.
Comment