Vince what size UPS systems are you talking about?
What I am driving at is size matters. Smaller KVA UPS can and do operate at lower battery voltages. For example let's say a rather small 5 KVA UPS operating on 48 volt batteries will draw up to 120 Amps from the batteries. For a 15 minute reserve capacity you can use small 50 AH AGM batteries. 120 amps is not a lot of current.
But now turn the table for something like a 1 or 2 MVA UPS. If you tried that at 48 volts we would be dealing with 21,000 amps. There is no conductor or battery that could handle that much current. So for those systems you have to use much higher voltages to get the current down to something manageable.
What I am driving at is size matters. Smaller KVA UPS can and do operate at lower battery voltages. For example let's say a rather small 5 KVA UPS operating on 48 volt batteries will draw up to 120 Amps from the batteries. For a 15 minute reserve capacity you can use small 50 AH AGM batteries. 120 amps is not a lot of current.
But now turn the table for something like a 1 or 2 MVA UPS. If you tried that at 48 volts we would be dealing with 21,000 amps. There is no conductor or battery that could handle that much current. So for those systems you have to use much higher voltages to get the current down to something manageable.