OK...
And I guess the end of the line means DOD=100%
Correct ??
It is interesting to see that the line of 0.1CA ends little before 10Hours. --> 0.1CA[Amp] x 10[Hours] = 1CA[A-H]
but the line of 1CA ends at 40minutes --> 1CA[Amp] x (40/60)[Hours] = 0.66CA [A-H]
And it is getting worse as the CA goes higher.
Also the voltage is lower at higher currents because of the internal resistance.
OK I got it....
Thanks Sunking.... the battery magician..
SolarWattComment
-
Correct
That is Peukert Law at work. When a battery is specified it is typically specified at the 20 hour discharge rate. So for example if you have a 100 AH battery means you can draw 100 AH / 20 H = 5 amps for 20 hours. However take that same battery and out a 2 (50 amps) hour discharge on it, and the battery is now a 45 AH battery. On the flip side take the same battery and take a 100 hour (1 amp) discharge on it and it is now a 150 AH battery.MSEE, PEComment
-
Comment
-
Comment
-
found the 3rd ed
Linden's Handbook of Batteries, Fourth Edition
the desired 4th can't be too far away - still looking
could be here, or it could be a wumpus http://ge.tt/4cyAIYe/v/4D1
is there a wumpus here ? https://docs.com/13K8ULast edited by Mike90250; 05-30-2014, 09:35 AM.Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||