could anyone tell me how long a GENERAC APS-6.0 DC generator would take to charge ban
Collapse
X
-
And your doorbell uses AC, but that does not mean you can connect 120 Volt AC to it. The voltages have to match and in the case of battery charging the current must be controlled.
The battery bank which the generator was meant to charge and the equipment running off that DC is not 24 or 48 volts!Leave a comment:
-
i dont understand on the genterator their is ahookup that says dc output?Leave a comment:
-
The whole neighborhood would get a "charge" watching that. Sorry, no, you cannot directly connect batteries to a generator. Even cars and trucks have voltage regulators.Leave a comment:
-
would it not charge the batteries hooking up 4 batteries to one output and another lead the other4 batteries in series?Leave a comment:
-
yes i have a sine wave plus 5548 xantrax inverterYou need a genset with 240vac output - you CANNOT get 6kw via a single 120v outlet
Additionally, you NEED a charger, with good PF (power factor). Otherwise, you will not see rated output from genset.
Are you looking for bad weather backup, or to supplement daily charging?
Do you already have 48v inverter? Some inverters have intrgal chargers and transfer switches too.. (XW_6048)Leave a comment:
-
Completely inappropriate equipment for residential use. I tis a custom design specifically for outdoor cabinet Telecom use where battery capacity is measured in the Thousand's of amp hours. not 10's or 100's.its a generac 6.0 dc auxiliary power unit it was used for cell phone tower battery backup idk anything else about it,just figured out there are two leads coming off dc pos and two leads coming off dc neg so i can hook 4 batteries up to one and the other 4 batteries with the other.
For Genera RE applications you want to use the EcoGen series as it is the only generators made for Solar Systems with low power factors and whisper quite operation using LPG or NG.Leave a comment:
-
Do that, without a charge controller and you will fry your batteries in no time at all. Or else pop the circuit breaker on the generator. The voltages do not match.its a generac 6.0 dc auxiliary power unit it was used for cell phone tower battery backup idk anything else about it,just figured out there are two leads coming off dc pos and two leads coming off dc neg so i can hook 4 batteries up to one and the other 4 batteries with the other.Leave a comment:
-
its a generac 6.0 dc auxiliary power unit it was used for cell phone tower battery backup idk anything else about it,just figured out there are two leads coming off dc pos and two leads coming off dc neg so i can hook 4 batteries up to one and the other 4 batteries with the other.Leave a comment:
-
You need a genset with 240vac output - you CANNOT get 6kw via a single 120v outlet
Additionally, you NEED a charger, with good PF (power factor). Otherwise, you will not see rated output from genset.
Are you looking for bad weather backup, or to supplement daily charging?
Do you already have 48v inverter? Some inverters have intrgal chargers and transfer switches too.. (XW_6048)Leave a comment:
-
Very true, and if the DC generator is at a good price since there is not much demand for a used one, then fine. But if you get AC instead, you can always use the same generator to power your AC loads in a crunch!Leave a comment:
-
Note that many switchmode chargers will work with AC or DC; they don't really care which they get. Transformer based chargers will be destroyed instantly, but they are rather rare nowadays. A simple rule of thumb - if you can pick it up it's a switchmode charger.Leave a comment:
-
You would almost certainly be better of with an AC generator and a 120volt or 240 volt battery charger. The DC is not making it easier.That looks like it is rated 6kw at 110 volts DC. You would need some electronics to get it to work into a 48 volt battery string. The output current maximum would be about 54 Amp at 110 volts. If you can get everything to play properly together, you could get through the bulk phase in less than five hours of operation, but that would probably be too high a charge rate for the batteries you have. Figure on at least 8 hours of operation for fully discharged batteries to get up to the point where the charging would have to slow down. You can't always charge a battery faster if you have more power available!
(The 27.2 volts at 4 Amps seems to be a charger for the system control or starting battery or other auxiliary use and is not relevant.)
Manual for a similar 3.5 kW DC unit can be viewed here: http://www.scribd.com/anne_carpenter...-Owners-ManualLeave a comment:
-
That looks like it is rated 6kw at 110 volts DC. You would need some electronics to get it to work into a 48 volt battery string. The output current maximum would be about 54 Amp at 110 volts. If you can get everything to play properly together, you could get through the bulk phase in less than five hours of operation, but that would probably be too high a charge rate for the batteries you have. Figure on at least 8 hours of operation for fully discharged batteries to get up to the point where the charging would have to slow down. You can't always charge a battery faster if you have more power available!could anyone tell me how long a GENERAC APS-6.0 DC generator would have too run to charge up battery bank
48 volts 8 - 6 volt deep cycle 225 AH batteries if the batteries were down to low battery cut out level of 44 volts and i wanted to bring them up too bulk volts of 58.4,the generator is a DC 6000 WATTS 27.2 VOLT MAX DC LEAD 4 AMPS if this is possible to config runs on propane gas.
(The 27.2 volts at 4 Amps seems to be a charger for the system control or starting battery or other auxiliary use and is not relevant.)Leave a comment:
-
Never in your lifetime according to the text in redcould anyone tell me how long a GENERAC APS-6.0 DC generator would have too run to charge up battery bank
48 volts 8 - 6 volt deep cycle 225 AH batteries if the batteries were down to low battery cut out level of 44 volts and i wanted to bring them up too bulk volts of 58.4,the generator is a DC 6000 WATTS 27.2 VOLT MAX DC LEAD 4 AMPS if this is possible to config runs on propane gas.Leave a comment: