  • #31
    Originally posted by eric@psmnv View Post

    If I'm going to build a whole new bank, I'll explore a different chemistry than FLA. I need something that can put up with the temperature swings and my overall ignorance.
    FLA is the most forgiving of temps and ignorance. Sealed lead batteries are expensive and shorter lived than their flooded brothers. Li will reward you in cold temps, by shutting down, unless you keep them heated. Ignorance with them is rewarded with smoke. NiFe is awfully forgiving - but expensive.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment


    • #32
      Originally posted by Mike90250 View Post

      FLA is the most forgiving of temps and ignorance. Sealed lead batteries are expensive and shorter lived than their flooded brothers. Li will reward you in cold temps, by shutting down, unless you keep them heated. Ignorance with them is rewarded with smoke. NiFe is awfully forgiving - but expensive.
      I like NiFe and could see myself shelling out the money, except it has a really poor charge/discharge rate. From what I can see, it's hard to run high-amp stuff for short bursts, and even harder to charge the things on the 4 hours of sunlight I get. Currently, I'm thinking maybe LiFePo4.

      Comment


      • #33
        Eric, On your test diagram, you show the input in Amps from the 2 chargers. Note that the two together (46 and 14) add up to about 60A of charge. You are using a 6500 watt genny. 6500W / 110V = 59Amps. it is not possible to get 110 amps out of two 55 amp chargers when the max the genny can produce is 59A. It appears to me that you are getting the max out of the two chargers. I know I'm a little late with the comment here, but I hope you got your problem solved.
        It would be great to hear how you solved the issue.
        JD