What the Heck are We Doing Wrong?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • eric@psmnv
    Member
    • Sep 2015
    • 93

    #16
    Originally posted by SunEagle
    I am still a little confused. Why do you have 2 chargers on the bank and why are they connected differently?

    Chargers are pretty stupid and will react to the battery voltage so one could be confused by the output of the second
    We inherited the solar from the previous cabin owner. That's the way it was wired when we got here. I always assumed there were two Iota DLS-55 chargers because the generator is putting out more amps than one charger could handle. I guess they are wired differently because the positive terminal of the upper left battery already has a bunch of stuff connected to it (as does the negative terminal of the lower right battery) so one of the chargers was connected to an adjacent positive terminal.

    Comment

    • SunEagle
      Super Moderator
      • Oct 2012
      • 15186

      #17
      Originally posted by eric@psmnv

      We inherited the solar from the previous cabin owner. That's the way it was wired when we got here. I always assumed there were two Iota DLS-55 chargers because the generator is putting out more amps than one charger could handle. I guess they are wired differently because the positive terminal of the upper left battery already has a bunch of stuff connected to it (as does the negative terminal of the lower right battery) so one of the chargers was connected to an adjacent positive terminal.
      I still think that 2 chargers may be causing your issue. It may be smart to get an electrician to check the wiring and batteries because it sounds like they are not working well for you and one or more may be close to the end of it's life.

      Comment

      • eric@psmnv
        Member
        • Sep 2015
        • 93

        #18
        Originally posted by SunEagle

        I still think that 2 chargers may be causing your issue. It may be smart to get an electrician to check the wiring and batteries because it sounds like they are not working well for you and one or more may be close to the end of it's life.
        Based on the findings shown in my drawing above, I'd say the upper right battery is definitely bad. It's voltage is low and it is not accepting amps. Can I replace just that battery or would we have to replace the whole bank?

        You may be right about the chargers. As someone pointed out above, the bulk charge voltage for these batteries should be around 14.7 V, but they never go above 14.0 even when the generator is pumping amps into them through both chargers, so it seems likely that the bank is never being fully charged. I'm not sure what to do. We live off grid way up in the mountains and electricians don't come up here. Do you know any that do consulting by video?

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15186

          #19
          Originally posted by eric@psmnv

          Based on the findings shown in my drawing above, I'd say the upper right battery is definitely bad. It's voltage is low and it is not accepting amps. Can I replace just that battery or would we have to replace the whole bank?

          You may be right about the chargers. As someone pointed out above, the bulk charge voltage for these batteries should be around 14.7 V, but they never go above 14.0 even when the generator is pumping amps into them through both chargers, so it seems likely that the bank is never being fully charged. I'm not sure what to do. We live off grid way up in the mountains and electricians don't come up here. Do you know any that do consulting by video?
          It is best to replace the entire bank because a new one will drop quickly to the life of the older ones. But if you got the money then you can try that or just take 2 of the worst batteries out of the bank and go with just 6 for now. Based on what you stated for load usage 6 of those batteries should be enough.

          Based on my calculations 6 225Ah batteries wired in a 2 x 3 system will give you (3 x 225Ah x 12V x 25% = 2025wh) where 2kWh should get you through the day with only a 25% discharge.
          Last edited by SunEagle; 08-16-2021, 12:08 PM.

          Comment

          • eric@psmnv
            Member
            • Sep 2015
            • 93

            #20
            Originally posted by SunEagle

            Based on my calculations 6 225Ah batteries wired in a 2 x 3 system will give you (3 x 225Ah x 12V x 25% = 2025wh) where 2kWh should get you through the day with only a 25% discharge.

            The cabin is drawing 179 watts on average (more during the day, less at night), which works out to 4.3 kWh per day. If my math is right, with 8 good batteries we would theoretically be able to meet our needs with a 40% DoD. We've never seen that happen, so we must not be getting the banks charged right (or the temperatures around here are playing hell with the efficiency, or both). With only 6 batteries in the bank, we'd need a 54% DoD.

            Assuming we can get the bank fully charged, we should be able to make do for a while with 6 batteries, but I can never tell when the batteries are fully charged. The Trojan T-105 spec sheet does not list a C-Rate. I do know that the generator can pump in at least 50 amps through the chargers. Any idea how long I should run the genny to get a full charge?

            Everybody is always warning about how under or over charging your batteries will damage them. I feel like I'm flying mostly in the dark. I've probably damaged my batteries without even know how I'm doing it.

            Comment

            • sdold
              Moderator
              • Jun 2014
              • 1479

              #21
              I think two or more of these in parallel should be OK as long as your wiring is sufficient, the chargers are more current-sources during the bulk phase anyway. By the way there is something screwy with the bottom charger's Positive cable in your diagram, it should go the the same terminal as the top charger.

              It does sound like you are under-charging. What version of the iota charger do you have, is it the straight DLS55 or the one with IQ4? If it's the non-IQ4 version there is an option board for $25 or so that will give it the ability to do Bulk, Absorb and float at the higher voltages needed for cycle service. If you don't have that option then it's stuck at 13.6V (normally used when connected to a constant source of AC power).

              Comment

              • sdold
                Moderator
                • Jun 2014
                • 1479

                #22
                By the way in case you don't have Autocad, here's iota's Autocad file with their suggested 4-battery parallel scheme, click the thumbnail to view:

                iota charger parallel config.jpg :

                Comment

                • eric@psmnv
                  Member
                  • Sep 2015
                  • 93

                  #23
                  Originally posted by sdold
                  I think two or more of these in parallel should be OK as long as your wiring is sufficient, the chargers are more current-sources during the bulk phase anyway. By the way there is something screwy with the bottom charger's Positive cable in your diagram, it should go the the same terminal as the top charger.
                  I talked with Iota. They said connecting 2 of them is fine. They won't fight or get confused. Their total output is added together and becomes the input to the bank. The upper left battery's positive terminal is crowded with other connections and there isn't room for more, so the bottom charger is connected to an adjacent positive terminal.

                  Originally posted by sdold
                  It does sound like you are under-charging. What version of the iota charger do you have, is it the straight DLS55 or the one with IQ4? If it's the non-IQ4 version there is an option board for $25 or so that will give it the ability to do Bulk, Absorb and float at the higher voltages needed for cycle service. If you don't have that option then it's stuck at 13.6V (normally used when connected to a constant source of AC power).
                  I don't have the IQ4 version, but I do have an RJ-11 "two-step voltage jack" in the unit that raises the voltage to 14.2. I leave it in there all the time. Iota says that's fine as long as the battery is okay with that voltage, The T-105 spec sheet says the batteries are okay with 14.82 volts for bulk charge on a 12V bank.

                  Comment

                  • sdold
                    Moderator
                    • Jun 2014
                    • 1479

                    #24
                    Sounds good, I think with that setup the bulk and absorb should take at least 6 hours, are you running the generator that long?

                    Originally posted by eric@psmnv
                    The upper left battery's positive terminal is crowded with other connections and there isn't room for more, so the bottom charger is connected to an adjacent positive terminal.
                    I'd use busses or their suggested wiring then, it's important to keep all of the parallel paths equal so that the batteries have a chance of sharing the current equally. The battery internal resistances are very low, so small resistances in the cables are significant.

                    Edit: It just occurred to me that your method might not ever allow an Equalization cycle, that might be one problem.
                    Last edited by sdold; 08-16-2021, 02:25 PM.

                    Comment

                    • eric@psmnv
                      Member
                      • Sep 2015
                      • 93

                      #25
                      Originally posted by sdold
                      Sounds good, I think with that setup the bulk and absorb should take at least 6 hours, are you running the generator that long?

                      I'd use busses or their suggested wiring then, it's important to keep all of the parallel paths equal so that the batteries have a chance of sharing the current equally. The battery internal resistances are very low, so small resistances in the cables are significant.

                      Edit: It just occurred to me that your method might not ever allow an Equalization cycle, that might be one problem.
                      The suggested wiring is for a 4-battery bank. Did you happen to see a wiring diagram for an 8-battery bank?

                      Comment

                      • sdold
                        Moderator
                        • Jun 2014
                        • 1479

                        #26
                        Yes, but it's for eight 12V batteries, not 6V batteries. In your case when you connect two 6-volt batteries in series, you pretend that's one 12V battery. So for the purposes of parallel wiring, you're using four batteries

                        Except that I wouldn't do that in your case if I could help it. Parallel is OK in float service with full-time AC power and occasional battery backup, but has trouble in cycle service as you've found out. So ditching the parallel batteries and going to one string or at most two in parallel, will probably give you much better service life.

                        Comment

                        • eric@psmnv
                          Member
                          • Sep 2015
                          • 93

                          #27
                          Originally posted by sdold
                          Yes, but it's for eight 12V batteries, not 6V batteries. In your case when you connect two 6-volt batteries in series, you pretend that's one 12V battery. So for the purposes of parallel wiring, you're using four batteries

                          Except that I wouldn't do that in your case if I could help it. Parallel is OK in float service with full-time AC power and occasional battery backup, but has trouble in cycle service as you've found out. So ditching the parallel batteries and going to one string or at most two in parallel, will probably give you much better service life.
                          But not much in terms of amp hours.Not enough to hold us for a full 24-hour period.

                          Comment

                          • SunEagle
                            Super Moderator
                            • Oct 2012
                            • 15186

                            #28
                            Originally posted by eric@psmnv

                            But not much in terms of amp hours.Not enough to hold us for a full 24-hour period.
                            Based on your load I think going to a bigger Ah battery system would make sense. Start looking at higher Ah Trojan batteries. You can find them using lower voltages like a 2V and then put 6 of them wired in series instead of 4 parallel banks of 12V.

                            Comment

                            • eric@psmnv
                              Member
                              • Sep 2015
                              • 93

                              #29
                              Originally posted by SunEagle

                              Based on your load I think going to a bigger Ah battery system would make sense. Start looking at higher Ah Trojan batteries. You can find them using lower voltages like a 2V and then put 6 of them wired in series instead of 4 parallel banks of 12V.
                              If I'm going to build a whole new bank, I'll explore a different chemistry than FLA. I need something that can put up with the temperature swings and my overall ignorance.

                              Comment

                              • Mike90250
                                Moderator
                                • May 2009
                                • 16020

                                #30
                                But not much in terms of amp hours.Not enough to hold us for a full 24-hour period.

                                then you get larger batteries, like L-16 floor sweeper batteries. Another alternative is to move to a 24V bank. When you run out of amp hours and
                                need more, go to a higher voltage system. It will require the same amount of lead, but configured in a more efficient manner.
                                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                                solar: http://tinyurl.com/LMR-Solar
                                gen: http://tinyurl.com/LMR-Lister

                                Comment