2 serious batteries one charges more than the other

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • gendil
    replied
    Originally posted by Mike90250
    Either charge the bad (lower voltage) battery separately, or - IF you have flooded, extend the absorb portion of the cycle.
    they are still withing spec just few diffrence and once i install that balancer it will be goood again

    Leave a comment:


  • Mike90250
    replied
    Either charge the bad (lower voltage) battery separately, or - IF you have flooded, extend the absorb portion of the cycle.

    Leave a comment:


  • gendil
    replied
    Originally posted by gendil
    hi people

    great news


    after i lost all hope in getting them in balance again i decided to make my system 12vdc by make them parallel but my mppt wont go beyond 400 watt due to

    high diffrenece between panel voltage which are at 100 (3 panels 24vdc nominal in serious) the controller kept on turning the fan on

    and it was impossible to go to 400 w attt because when ever the fan turn on the controller enters some sort of standby by lowering the power produced

    so i decided to back to 24 vdc i said may be it will get in balance again after the were about one month in paraller they charge and dicharge together


    and yes today i let them 24vdc in serous and they were amazingly blamaced at 13.77vdc both of them were exactely at 13.77 at the float so the mission is done


    now all left is to cure my system which have one panels that have snail trail and mini crack ....one panel seems to drag 3 in serious 250 solar to just 420 peak of watt

    as i use mppt they supose to bring at least 500 watt at peak so that is left to be done with this small yet great system

    my system is 2 100 amps 12vdc maxima battery one piece mppt 60 amps emsart3 controller and 3 solar panels 2 of them called amira solar they 270 and one chinse 250

    the chinse one is the defected one that drag my system down

    the 3 panles are hooked in seroious to minimize current loses and voltage loses



    after 2 days the batteires go out of balance slightly one at 13.65 one at 13.8 so balacncer is a must here ....they do so because of diffrence in auto dicharge rate

    Leave a comment:


  • gendil
    replied
    hi people

    great news


    after i lost all hope in getting them in balance again i decided to make my system 12vdc by make them parallel but my mppt wont go beyond 400 watt due to

    high diffrenece between panel voltage which are at 100 (3 panels 24vdc nominal in serious) the controller kept on turning the fan on

    and it was impossible to go to 400 w attt because when ever the fan turn on the controller enters some sort of standby by lowering the power produced

    so i decided to back to 24 vdc i said may be it will get in balance again after the were about one month in paraller they charge and dicharge together


    and yes today i let them 24vdc in serous and they were amazingly blamaced at 13.77vdc both of them were exactely at 13.77 at the float so the mission is done


    now all left is to cure my system which have one panels that have snail trail and mini crack ....one panel seems to drag 3 in serious 250 solar to just 420 peak of watt

    as i use mppt they supose to bring at least 500 watt at peak so that is left to be done with this small yet great system

    my system is 2 100 amps 12vdc maxima battery one piece mppt 60 amps emsart3 controller and 3 solar panels 2 of them called amira solar they 270 and one chinse 250

    the chinse one is the defected one that drag my system down

    the 3 panles are hooked in seroious to minimize current loses and voltage loses

    Leave a comment:


  • gendil
    replied
    Originally posted by Sunking

    Be careful putting a fully charged battery in parallel with a discharged battery, you can get a nasty surprise if the voltage is more than 1/4 volt difference. You could melt the battery term post or wire. A difference of 1 volt can generate 500 to 2000 amps of equalizing current on a golf cart size battery or more with AGM. Neither battery, wire, or you will like the result.
    i wont do that actually i even wont dicharge one battery more than the other some one did this and yet too many poeple here call me stupid do i have to say all details? about who did that nasty thing?

    any way i solved all this problem by buying new mppt solar 60 amps and wiring my battery in paraller for 12vdc system it works nice just one thing 500 watt susytem only peaked 290 watt maximum

    Leave a comment:


  • Sunking
    replied
    Originally posted by gendil
    i start to charge them in parallel using pwm solar charger i know i lose power but i will try to save my batteries
    Be careful putting a fully charged battery in parallel with a discharged battery, you can get a nasty surprise if the voltage is more than 1/4 volt difference. You could melt the battery term post or wire. A difference of 1 volt can generate 500 to 2000 amps of equalizing current on a golf cart size battery or more with AGM. Neither battery, wire, or you will like the result.
    Last edited by Sunking; 08-10-2018, 09:19 PM.

    Leave a comment:


  • gendil
    replied
    Originally posted by SunEagle
    Try splitting up the 2 batteries and charge each independent of each other using a 12v charger. Maybe you can save the bad battery.


    thanks they are agm so they must endure the bad operation note that i left them for 2 full days only


    one gone in overcharge and other easily be saved because it low in charge they both work fine only when in parallel they seems note to share voltage evenly.


    the one that accustomed to eat more voltage is try to deprive the other from its natural charge!!!



    they need abit of taming ! i start to charge them in parallel using pwm solar charger i know i lose power but i will try to save my batteries



    i will reply you within 2 days after both 2 batteires be sujbjected to equal amounts of charge and equlazation voltage as well as float they will start act normally i think

    Leave a comment:


  • SunEagle
    replied
    Try splitting up the 2 batteries and charge each independent of each other using a 12v charger. Maybe you can save the bad battery.

    Leave a comment:


  • gendil
    started a topic 2 serious batteries one charges more than the other

    2 serious batteries one charges more than the other

    one day i desiced to use my 12 volt lamp and put it in one battery


    the system is 24vdc one and seems that i discharged one battery very badly now the system will full charge one battery at 12.9vdc other at 14 i dont know how to restore balance

    i tried to load the other battery but still same as soon as left the load on it the charge controller seems to direct all charge to it and re put it on the 14vdc level i am really stuck
Working...