Charge controller settings

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #46
    For my oddball voltage bank, I have re-bulk set so that if heavy loads cause the batteries to sag below the setting, the charger will re-start a bulk cycle if the loads abate and there is sufficient sun. Otherwise, could start the evening with 15% out of my bank. When I'm running heat tape on water lines and low sunlight in winter, I want as much juice in the bank as I can get.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Sunking
      Solar Fanatic
      • Feb 2010
      • 23301

      #47
      Originally posted by Mike90250
      When I'm running heat tape on water lines and low sunlight in winter, I want as much juice in the bank as I can get.
      Mike you must be at altitude up Northern in CA. Heat Tape in CA caught my attention. I kind of know where you live, but never gave high altitude any thought. Funny because one of the worse blizzards I have ever been caught in is Truckee enroute to Tahoe from Sacramento.

      Well I take that back. Memorial Day weekend, first day of Summer vacation season on I-40 AZ/NM border Gallup NM of 2008 I think. We were in route to Lost Wages IN 2008 I think.. Got to Gallup in a White Out storm and they closed I-40. Quite a site seeing Wifey and I in shorts and tank tops looking for a motel to ride the storm out over night. Got to Lost Wages two days later and they were at record cold and flood waters had just cleared out. Denver had a record snow storm that weekend. If I remember correct that same storm went through to Washington DC, buried the cherry blossoms, and they had to cancel the Global Warming Conference due to record snow and cold.
      Last edited by Sunking; 12-30-2016, 05:12 PM.
      MSEE, PE

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #48
        Originally posted by Mike90250
        ...... When I'm running heat tape on water lines and low sunlight in winter, I want as much juice in the bank as I can get.
        Only at 1400 feet, 20 miles from the ocean, but it's cold enough to bust up the windshield washer water tank in the winter, Stupid nanny state only allows window washer antifreeze to be sold in the "alpine counties".

        Remember the Donner Party 1846 !

        I think Calif must set the record for the longest state, measured north to south, it's longer (800 mi) than half the eastern seaboard (Florida to Maine is 1,342 miles)

        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #49
          Originally posted by Mike90250
          Remember the Donner Party 1846 !
          You mean the Donner Dinner Party for 87 people? I think Hannibal Lector brought the Chianti right?
          Last edited by Sunking; 12-30-2016, 09:00 PM.
          MSEE, PE

          Comment

          • Diesel Pro
            Junior Member
            • Sep 2016
            • 26

            #50
            Making progress here with charge status. Back to John Galt's comments the Crown batteries seem to want 1-1.5v higher setting after a while. I think we'll be in really good shape soon

            Bat 1
            1.255
            1.255
            1.2475

            Bat 2
            1.2475
            1.240
            1.250

            Bat 3
            1.250
            1.2475
            1.245

            Bat 4
            1.2375
            1.250
            1.250


            Changed charge controller settings to 32 EQ, 28.5 abs and 28.4 float. The sun came out nicely so I ran a couple hrs of EQ on it. They took decent amperage, but not excessive. Quickly tapered to 10-15 amps. I was preoccupied with other tasks, but I did check the previously low cell right before running out the door. It was 1.375 and it was now at 1.255 with the controller on float.


            So how balanced/equalized do I want to be?

            Comment

            • Sunking
              Solar Fanatic
              • Feb 2010
              • 23301

              #51
              First things first. You are trying to EQ the batteries to save them. Crank the voltage up to 31 volts until EQ'd then go back to float. Better yet get them on a generator and get it done. Like I said you cannot do EQ and maintenance with Solar. Takes to dang long, and impossible if you use the batteries. Now if you cannot be there, Float will eventually work, at least by spring. Or you can set it for a week with Absorb = 29 and Float = 27 to speed things up a bit. .

              As for what the max High to Low spread on SG should be has already been answered a couple of times. It is right in your Owners Manual, last page under Trouble Shooting. Also take note the approx recommended charging voltages on top of page 3 under RE USERS. You are not going to see to see what you expect. Crown has already updated and done away with archaic 3-Stage charging. Like Trojan and some others only specify:

              Daily Charge sometimes called Absorption is for Daily Cycle users. 29 volts
              Float for batteries using Float Charge method. 27 volts
              Equalization for equalization. 31 volts

              All you have to remember is 2 and 27 as a starting point

              Bare in mind those are Ball Park voltages and only your hydrometer knows the specific voltages you should use. It is going to rane +/- 1 volt assuming your panels and batteries a properly sized and matched. If you are going to error you want more panel wattage than necessary like gas in your car. For daily cycle users, many find there is no voltage high enough except for maybe a month in summer or if they leave for a few days and turn everything off. That is when they learn they should have more panel wattage, generator and hydrometer. What you will likely find, the job never ends. Lowering voltages in summer months and raising them in winter months. It is your new part time job, with no vacations, no time off, and you have to pay for the privilege and not get paid.
              Last edited by Sunking; 01-01-2017, 08:49 PM.
              MSEE, PE

              Comment

              • Diesel Pro
                Junior Member
                • Sep 2016
                • 26

                #52
                I guess next check should tell the story. I now recognize that I have plenty of horsepower and just need to creep my settings up. I guess 17 points spread on SG is not too bad and realistically should be tighter next test.

                During Sunday's EQ session I leaned on them hard with my 32v EQ setting and the wattage used from the panels was only in the 500 range most of the time. I turned on loads in the cabin just for grins and managed to get the wattage up to the 8-900 range but ran out of loads. I guess I could have run the microwave, but I know that if the batteries demand it will pass 1200w with ease.


                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #53
                  Originally posted by Diesel Pro
                  I guess next check should tell the story. I now recognize that I have plenty of horsepower and just need to creep my settings up. I guess 17 points spread on SG is not too bad and realistically should be tighter next test.nge but ran out of loads. I guess I could have run the microwave, but I know that if the batteries demand it will pass 1200w with ease.
                  17 points is real good and why I made you look it up yourself , do the drill and never have to ask again.

                  Crown is pretty darn liberal stating 50 point spread. Rolls, Trojan, C&D and other manufactures state state a much tighter 30 points which you are inside of. I sugest 30 points as you default. Crown will not take issue with it. As you have discovered set point voltage suggestions are just that, a starting point. With solar applications the voltage set points will most always be higher. For most there is no voltage high enough and a down hill ride from day 1 to dead batteries.

                  Good Luck to you and Happy New Year
                  MSEE, PE

                  Comment

                  • Diesel Pro
                    Junior Member
                    • Sep 2016
                    • 26

                    #54
                    Well if I do as well with these as I did in my boat I should be OK. My boat is used 3-5 times a year, maybe more. I have no meter on the trolling batteries, but I have taken them down to where the power is noticeably reduced. After each outing I just plug in and the trollers charge at 5amps each off a dual bank Guest charger and the starting battery is on a Battery Tender waterproof 800. Run it overnight and park until next outing. I typically repeat before next outing. Boat sits all winter with batteries installed and disconnected. I got 8 yrs of service and the trollers were still going if only a little weak. Never a hydrometer, water, or anything... Starting battery finished this season and will be replaced just for good measure.

                    Comment

                    • Diesel Pro
                      Junior Member
                      • Sep 2016
                      • 26

                      #55
                      Looks like 28.4 is right where I need to be. I arrived and the charge was in float at .7 amps so it was more or less done.

                      I now have 2 hydrometers: 1) Hydrovolt and 2) EZ Red

                      The EZ red is more optimistic by about 10 points, but basically I'm at 1.265 +/- 10 points with 1.275 readings on some cells with the EZ red. I did not have a lot of time to play around. What I did for this coming week's test was I restarted the inverter and left it idle with the same controller settings. This should give the system just a very modest bit of load to exercise it. At some point I'd like to consider a small resistance based heater to help reduce my propane use. I'm at a point that I come up just a bit short of the season with the thermostat set at antifreeze.
                      Last edited by Diesel Pro; 01-09-2017, 05:13 PM.

                      Comment

                      • Sunking
                        Solar Fanatic
                        • Feb 2010
                        • 23301

                        #56
                        Originally posted by Diesel Pro
                        it. At some point I'd like to consider a small resistance based heater to help reduce my propane use.
                        Sorry but forget that idea. You do not have the battery capacity, and if you did would bankrupt you. Propane is a whole lot less expensive.

                        MSEE, PE

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #57
                          Originally posted by Sunking
                          Sorry but forget that idea. You do not have the battery capacity, and if you did would bankrupt you. Propane is a whole lot less expensive.
                          Where I am (No. Cal) propane costs about the same as electric resistance heating (at $.20+ per kWh).
                          Electric heat pump is cheaper than propane. Natural gas is the best, but not available everywhere outside urban areas.
                          PV stored in a battery rather than just surplus from the panels, on the other hand, is the most expensive of all.
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • Diesel Pro
                            Junior Member
                            • Sep 2016
                            • 26

                            #58
                            I'm not talking about heating it completely, just thinking that I could determine a manageable resistive load to add a little bit of supplemental heat from a system that already exists. It could be on a timer even and/or a thermal switch. Could be as simple as a light bulb like we used to use in the pump house years back to prevent freezing. My thought is that a little exercise of the system would not be a bad thing. For right now the minimal heat from the inverter idle process will be helping.
                            Last edited by Diesel Pro; 01-10-2017, 11:42 AM.

                            Comment

                            • Diesel Pro
                              Junior Member
                              • Sep 2016
                              • 26

                              #59
                              So after a week with the inverter on and idling and poor sun I found the batteries down to the 1.225 range. I switched off the inverter and after a week of reasonably decent sun with zero demand the batteries were still hanging a bit low. in the 1.24 range. The production number on the Classic 150 said it made a mere .3kwh after what was a day with plenty of sun. I know there was enough sun off and on during the week and it has enough capability to do more.

                              I would think that 28.4v should be plenty of a float charge. Unsure about creeping the float charge up any further so I increased the absorb from 28.5 to 29.5v for this week's test and the inverter is back on and idling.
                              Last edited by Diesel Pro; 02-08-2017, 04:35 PM.

                              Comment

                              Working...