2V batteries with 4 bolt connetion between batteries - how to connect the cabel?

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • Roil
    replied
    Originally posted by inetdog
    Yes, it is, and it does suggest that you need to make sure that all of your 24 volt utilization equipment can take that high a voltage or else provide a way to disconnect it when the charging voltage is too high.
    Nominal 12 volt equipment intended for use in a vehicle will be designed for a wider voltage range. Equipment intended for use at 12 volts AC or DC in a fixed location may not have that same tolerance. Especially when, like some lighting equipment, it is designed to be fed by a regulated DC supply rather than directly from a battery.
    I have a 12V system, so the battry is 2 strings of 6V. I will keep my 12V equipment on the old batterybank untill the new one is up and kicking. Anyway it's like you say - they do survive 15V

    Leave a comment:


  • Roil
    replied
    Originally posted by Sunking
    Check your documentation and tell me the recommended FLOAT voltage. Should be around 2.35 vpc. 2.45 would be Equalize, not Float.
    Float 2.25-2.30V
    Cycle use: 2.35-2.45V

    Leave a comment:


  • inetdog
    replied
    Originally posted by Roil
    7 instead of 25 deg C makes 18 x 3mV = 54mV in increased Charging Current - > 2.45V + 0.054V = 2.504V , 15.024 in 12V world and 30.048 in 24W setup - isn't this a very hight voltage?
    Yes, it is, and it does suggest that you need to make sure that all of your 24 volt utilization equipment can take that high a voltage or else provide a way to disconnect it when the charging voltage is too high.
    Nominal 12 volt equipment intended for use in a vehicle will be designed for a wider voltage range. Equipment intended for use at 12 volts AC or DC in a fixed location may not have that same tolerance. Especially when, like some lighting equipment, it is designed to be fed by a regulated DC supply rather than directly from a battery.

    Leave a comment:


  • Sunking
    replied
    Originally posted by Roil
    7 instead of 25 deg C makes 18 x 3mV = 54mV in increased Charging Current - > 2.45V + 0.054V = 2.504V , 15.024 in 12V world and 30.048 in 24W setup - isn't this a very hight voltage?
    Check your documentation and tell me the recommended FLOAT voltage. Should be around 2.35 vpc. 2.45 would be Equalize, not Float.

    Leave a comment:


  • Roil
    replied
    Originally posted by SunEagle
    Were you able to find this 75mm "kobber bar" as a way to make your cable terminations?
    Yes, well I picked up 4 pcs of 40cm copper bar today 25mm x 6mm , so double thickness but thats fine I guess. Giving 150mm2

    Leave a comment:


  • SunEagle
    replied
    Originally posted by Roil
    www.alternativeenergi.no is very much alive. Their connection advice was as follows:


    ....
    More than 2000W? - mount a 75mm2 kobber bar (25mm x 3mm / 1" x 1/8"(ish) ) on top of the 4 post's and then connect the cable on one of them.
    Were you able to find this 75mm "kobber bar" as a way to make your cable terminations?

    Leave a comment:


  • Roil
    replied
    Originally posted by Sunking
    With AGM it is important to use temp comp.
    The documentation state:

    Effect of Temperature on Charging Voltage
    As temperature rises, electrochemical activity in a battery increases. Similarly, as temperature falls, electrochemical activity decreases.
    Therefore, conversely, as temperature rises, charging voltage should be reduced to prevent overcharge and increased as temperature falls to
    avoid undercharge. In general, to assure optimum service life, use of a temperature compensated charger is recommended. The
    recommended compensation factor for SL batteries is -3mV/℃/Cell (standby use) and-5mV/℃/Cell (cyclic use). The standard center point for
    temperature compensation is 25℃. Figure 4 shows the relationshipbetween temperatures and charging voltages in both cyclic and standby
    applications.


    7 instead of 25 deg C makes 18 x 3mV = 54mV in increased Charging Current - > 2.45V + 0.054V = 2.504V , 15.024 in 12V world and 30.048 in 24W setup - isn't this a very hight voltage?

    Leave a comment:


  • Sunking
    replied
    Originally posted by Roil
    How about temp. compensation?

    Currently they hold 7-8 deg Celsius.
    With AGM it is important to use temp comp.

    Leave a comment:


  • Roil
    replied
    Originally posted by Sunking
    Instead apply a EQ charge using your generator which is a constant voltage method running @ 2.45 volts per cell or 29.4 volts. You still need a charger capable of C/10 charge current.
    How about temp. compensation?

    Currently they hold 7-8 deg Celsius.

    Leave a comment:


  • Sunking
    replied
    Originally posted by Roil
    I must admit I am puzzled about the recommendations "Within 12 months after manufacture 8-10 hours at constant current of 0.1C Amps or
    20-24 hours at constant voltage of 2.45Vpc"
    - 0.1C Amps at what voltage?

    Any views on this?
    There are basically two charging algorithms of constant voltage and constant current. Constant voltage is pretty straight forward in that you apply a precision controlled voltage to the battery.

    Constant current is different, there is no voltage associated with it. The charger pushes a set amount of current into the battery regardless of how much voltage is required. However please ignore that method, it is dangerous and can seriously over charge the batteries. They recommend .1C which also is C/10. So for example if those are 2000 AH batteries they are saying push 200 amps of current into them for 20 to 24 hours. Do not do that.

    Instead apply a EQ charge using your generator which is a constant voltage method running @ 2.45 volts per cell or 29.4 volts. You still need a charger capable of C/10 charge current.

    Leave a comment:


  • Roil
    replied
    Kick starting sleeping batteries

    This set of batteries has been sleeping for a while. Fuli users manual says the following on the subject:
    RECHARGING STORED BATTERIES
    In general, to optimize performance and service life, it is recommended that FULI batteries which are to be stored for extended periods of time be given a supplementary charge, commonly
    referred to as a “top charge ", periodically. Since any battery loses capacity through self discharge, it is recommended that, prior to putting the battery into service, a process called “top
    charging “be applied to any battery which has been stored for a long period of time.
    Excluding conditions in which storage temperatures have been abnormally high, top charging is recommended within the following parameters(Table 2):
    Battery Age
    Top Charging Recommendations
    Within 6 months after manufacture 4 to 6 hours at constant current of 0.1C Amps or 15
    to 20 hours at constant voltage of 2.45Vpc
    Within 12 months after manufacture 8-10 hours at constant current of 0.1C Amps or
    20-24 hours at constant voltage of 2.45Vpc

    In order to successfully top charge a battery stored for more than 12 months, the open circuit voltage must be checked to ensure that it is
    higher than 2.0 volts per cell.
    Therefore ALWAYS check the open circuit voltage FIRST. If the open circuit voltage of the battery is 2.0 Vpc or lower, please refer to us
    prior to attempting to “Top Charge ".


    Fuli also write this about charging in general:
    Constant Voltage Charging:
    This is the recommended method of charging for VRLA batteries. It is necessary to closely control the actual voltage to ensure that it is
    within the limits advised.
    Float Service: 2.25-2.30 Vpc at 25℃ .
    Cycle Service: 2.35-2.45 Vpc at 25℃
    FULI suggests that the initial current be set within 0.2C Amps. Figure 1 shows one example of a constant voltage charging.
    Constant Current Charging
    This method of charging is generally not recommended for VRLA batteries, but is an effective method for charging a number of series
    connected batteries at the same time. It is necessary to understand that if the batteries are not removed from the charger after reaching a
    state of full charge, considerable damage will occur to the batteries due to overcharging. Figure 2 shows the characteristics of a FULI
    battery under constant current charging conditions



    I must admit I am puzzled about the recommendations "Within 12 months after manufacture 8-10 hours at constant current of 0.1C Amps or
    20-24 hours at constant voltage of 2.45Vpc"
    - 0.1C Amps at what voltage?

    Any views on this?
    Attached Files

    Leave a comment:


  • Roil
    replied
    The "Answer:"

    Originally posted by _OS_
    The Norwegian company that installed your batteries on the oil rig is still in business: www.getek.no and the dealer selling the identical Fuli batteries is www.alternativenergi.no

    Correction: Getek is out of business!

    www.alternativeenergi.no is very much alive. Their connection advice was as follows:


    If connect to an inverter off less than 2000W it's sufficient to connect to one of the 4 post's.
    (This I assume also answer the question about 4, 2 or one 2V cell)

    More than 2000W? - mount a 75mm2 kobber bar (25mm x 3mm / 1" x 1/8"(ish) ) on top of the 4 post's and then connect the cable on one of them.


    I am planning to use 2 70mm2 cable and was thinking of mounting them on post 2 and 3.

    However...............

    This still leaves me with a 100$ parallel cabling questions since I a do have two of these battery series and have no other options than to put them in parallel.

    In my mind this leaves me with two options:

    1) Connect the 2 70mm2 (+) cables to #1 and the 2 (-) cables to battery pack #2 and connect the 2 battery pack together with 2 70mm2 cables on both sides (+ & -)

    Like this only with two batteries:


    or the more complex

    2) Make a double T-connection on each side making the cable length exactly the same from inverter to battery

    like this (again only with two batteries):



    Nr 2) is probably the best however it is more complex and needs a connect "box" outside the nice protection of the battery "house"

    Leave a comment:


  • Sunking
    replied
    Originally posted by Roil
    Compression and oxide inhibitor only then

    I struggle to find the compound, any product name?
    I do not know if it is available in your area but worth ordering SanChem NO-OX-ID A Special. Absolutely the best compound money can buy. Used by all electric, telephone, water, and structural utilities. If applied correctly will out live you and the system. All you need is a small tube of it.

    Leave a comment:


  • SunEagle
    replied
    I've never seen solder used on battery terminals before.

    Leave a comment:


  • Naptown
    replied
    Originally posted by Roil
    Compression and oxide inhibitor only then

    I struggle to find the compound, any product name?
    Mentioned in this thread look for it

    Leave a comment: