Normally checking SOC on batteries requires the batteries to be in open circuit status for no less than 4 hrs to disapate plate charges. My installation does not lean favorably to that criteria due to the fact I have a Xantrex Sw 4048 inverter that doesn't take kindly to removing the 48v bank from the inverter as it will loose all of it's internal programming. So I wanted to exercise the batteries that have been in service about 9 months. I have had 4 or 5 incedents of the grid going down for a couple of hrs each during that time. I separated from the grid starting out at 50.0 volts full charge and in 12 hrs of discharge, I ended up at 48.8 volts. Now what is the remaining capacity of the bank? As close as I can determine, I have 80% remaining.
Now heres the rub, the batt voltage was recorded under about a 9 amp load. There is only one website on the net that I could find, the Rolls Royce site, that has a chart, Fig #2, that shows SOC under load values. But these are for FLA not AGM. I have 4 Deka 8g's in series for a 48v bank. The are rated at 210 ah.
What do you off griders do to measure the remaining capacity of your batteries that you obviously cannot take out of srvice to read the voltages? Comments anyone?
Now heres the rub, the batt voltage was recorded under about a 9 amp load. There is only one website on the net that I could find, the Rolls Royce site, that has a chart, Fig #2, that shows SOC under load values. But these are for FLA not AGM. I have 4 Deka 8g's in series for a 48v bank. The are rated at 210 ah.
What do you off griders do to measure the remaining capacity of your batteries that you obviously cannot take out of srvice to read the voltages? Comments anyone?