Question about Fusing

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Willowmore
    Junior Member
    • Feb 2021
    • 2

    Question about Fusing

    Hi there! I have a Renogy Rover Elite 40 for my portable setup. The manual says never to connect the panels with the battery not installed. It makes a very strong point of it. If I were to fuse the battery as suggested on the website, and the battery fuse blows, what happens to the controller with the panels still connected?
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Without the battery as a load for the Controller, the controller is likely to blow.

    However, properly wired and fused, the battery-controller fuse would only blow if the controller fries and presents a dead short to the battery.
    Solution - never place loads on the controller, and then the only thing that would cause the battery-controller fuse to blow, is a bad controller.
    If it's a 20A controller, wire it with 40A wire and fuse at 25A.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Willowmore
      Junior Member
      • Feb 2021
      • 2

      #3
      Thank you!

      Originally posted by Mike90250
      Without the battery as a load for the Controller, the controller is likely to blow.

      However, properly wired and fused, the battery-controller fuse would only blow if the controller fries and presents a dead short to the battery.
      Solution - never place loads on the controller, and then the only thing that would cause the battery-controller fuse to blow, is a bad controller.
      If it's a 20A controller, wire it with 40A wire and fuse at 25A.

      Comment

      • chrisski
        Solar Fanatic
        • May 2020
        • 547

        #4
        I had my panels briefly connected to the SCC prior to installing the batteries. This caused 20 volts to go through my 12 volt system. Did not ruin anything in the RV. It was the initial power on of my system and The SCC had not been set up yet, so perhaps that's why it pushed out so much.

        On a different forum, there's a great debate about if this is safe. I'm of the camp that if it says it in the manual don't do it!!! The other camp has experimented by setting up SCC both PWM and MPPT and of the dozens that have claimed to do it, only one guy said he fried a charge controller that way. I'm more worried about spikes going into my 12 volt system and ruining something.

        Comment

        • bob-n
          Solar Fanatic
          • Aug 2019
          • 569

          #5
          I can't comment on any RVs or your particular use, but automotive electronics is engineered to withstand double-battery operation for jump-starting. In other words, devices in cars must survive undamaged when powered for many seconds with +24VDC. This has been an automotive electronics requirement for >30 years.

          There is another automotive electronics requirement called "load dump" that means that car electronics must survive brief excursions up to +35V or higher.

          But I also agree with the Chrisski's comment: If the manual says don't do it, don't do it.
          7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV