I am planning to route the AC cable of the APSystems microinverters through my attic. For the rooftop connection, I am using an Ironride JayBox. What is the proper and Florida code-compliant way to connect the AC cable into the JayBox? Ironridge just recommends to drill a hole into the side of the JayBox, and to use watertight fittings to route the cable to the inside. Does anyone have examples of such watertight fittings? I am not finding any for outdoor cables. Only for conduits. But then the question would be how to get the cable into the conduit with a water-tight entry point?
Try our solar cost and savings calculator
Connecting cables to junction box
Collapse
X
-
-
IronRidge is describing the normal approach, and the fitting you are looking for is a listed watertight cord grip, also sold as a cable gland or strain-relief connector. It is different from an ordinary NM or EMT connector. Look for one rated for outdoor / wet locations, with a sealing ring and a dome nut that compresses around the cable jacket. Match it to the actual outside diameter of your microinverter AC cable, not just to the trade size of the hole, and check that the gland is rated for the cable type you are using.
Drill the hole to the size the gland needs, deburr the edge inside and out, and fit the gland through the side of the JayBox with its sealing washer against the outside of the box. Tighten the dome nut until the seal grips the jacket without crushing or deforming it. The cable should enter from below or from the side with a small drip loop, so water runs away from the entry instead of tracking along the jacket into the box. Do not rely on silicone alone to seal a plain drilled hole, and do not use a standard indoor connector outdoors in Florida.
If you would rather run conduit, that is also a clean option. Terminate the cable inside a listed junction box at the roof, transition to individual conductors in liquidtight flexible conduit or EMT as your local inspector allows, and use a listed liquidtight connector into the JayBox. Keep the cable supported so it does not rest on the roof or pull on the gland, protect any exposed run from UV and abrasion, and keep the splice / connection area accessible. Confirm the final arrangement with your local inspector, because Florida jurisdictions vary on conduit, disconnect, and labeling requirements.
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 10:33 PM.
Comment