It might be just me, but after learning my lesson with that old bus box we had I don't believe in leaving DC bus bars exposed where people can get at them. And I don't believe in using metal boxes to put them in in the event something would go bad and come into contact with the metal box where you would have virtually unlimited current from the battery able to go to ground and not stop until it was all burned up.
That grey plastic (or PVC) box I put our bus bars in won't burn. It has some sort of retardant in it. It will melt with direct flame or high heat to it, but as soon as you take the flame away it won't continue burning. The box itself is UL Listed. And the bars that are in it were from a UL Listed generator switchgear. But combining the two does not make a UL Listed or even approved bus box. But I feel a lot safer with it than a metal one.
Even so, I never open it up or even hook up a little fused wire in it without shutting everything off. We have a battery combiner with 90A breakers on each string. When I have to work in that bus to hook something up, I start our little generator and flip the manual transfer switch to switch the loads to gen power. Then I shut the entire DC system down and turn off all the breakers on the battery strings so that box is dead and it's safe to work on.
Try our solar cost and savings calculator
Good wire gone bad
Collapse
X
-
I have been on plant start ups where buss connections in the HT switchgear were not properly tightened - torqued - we vaporized meters of heavy copper buss bar - after a somewhat violent indication that something was not right.It may just be a shaggy dog story, but an acquaintance who had worked for Ma Bell back in the day told of a pair of HVAC guys who were putting a new air duct in the battery room of a large Central Office.
The bus bars (@ 48V nominal) were so large that you could easily walk on them. And they did. That was not a problem.
What was a problem was that they dropped the 6' section of duct they were trying to put in place.
Two ends of the duct hit the floor and the middle section vanished in a flash.Leave a comment:
-
It may just be a shaggy dog story, but an acquaintance who had worked for Ma Bell back in the day told of a pair of HVAC guys who were putting a new air duct in the battery room of a large Central Office.I was working on it one day and had one of those Craftsman hammers with a steel handle with a rubber grip on it. I hung the hammer on the wall by the claw on a nail. Somehow that hammer fell off, hit the top of the box and flipped in mid-air and went inside the box and came into contact with the positive bar. It was not just sparks - it was an instant explosion and the top half of that hammer was instantly turned to molten metal that sprayed me (I still got some burn scars from it) with a brilliant flash of light.
The bus bars (@ 48V nominal) were so large that you could easily walk on them. And they did. That was not a problem.
What was a problem was that they dropped the 6' section of duct they were trying to put in place.
Two ends of the duct hit the floor and the middle section vanished in a flash.Leave a comment:
-
Chris it i snot the wire heating up. It is the resistance in a poor connection that is heating up. If you use mechanical clamp connectors, you will have a failure period. It is just a matter of time. Get rid of the buses that use Mechanical Clamp connections and replace it with a copper bus bar wide enough to terminate 2-hole connectors using proper bolts, washers, and lock washers. Terminate wire with compression connectors using th eproper size and tooling to make a UL tested connection. When done properly will last a life time.
See ya down the road, gotta go.Leave a comment:
-
Hello from paradise. On Tablet so my response is short as well as time.I was working on it one day and had one of those Craftsman hammers with a steel handle with a rubber grip on it. I hung the hammer on the wall by the claw on a nail. Somehow that hammer fell off, hit the top of the box and flipped in mid-air and went inside the box and came into contact with the positive bar. It was not just sparks - it was an instant explosion and the top half of that hammer was instantly turned to molten metal that sprayed me (I still got some burn scars from it) with a brilliant flash of light.
It never blew a single fuse on any of the strings. Every since, I been scared crapless of DC bus boxes hooked to batteries.
Well if it hit the battery terminal buss there was no fuse. That is what is so dangerous about battery systems. Voltage is not high, but available fault current is extremely high.Leave a comment:
-
Mike, I sort of wonder about this. AWG 4 does not heat up here with 45 amps in it. I got 6 AWG from my MPPT60's to the bus. Those controllers run that 6 AWG THHN (90C rated wire) at 60 amps continuous for hours and the wire does not get warm. I think you still got a high resistance connection there someplace if 4 AWG is warming noticeably at 45 amps. Maybe fire up your mV meter and check the circuit to see how much drop you're getting across those connections? Something has to be not right there.
Edit:
Like maybe a defective bus bar? Maybe that bus bar is plated aluminum instead of tin plated copper or something? I've seen where you order stuff like that from a vendor and a cheaply made or substandard component gets mixed with the rest in a shipment and gets installed during assembly because it's hard to tell the difference. If something like happened and you got a bus bar that's made of the wrong aluminum alloy or something, guess what you got? A built-in resistor in your panel.
I'd be highly suspect of it when you're heating 4 AWG wire with 45 amps.Leave a comment:
-
John Wiles on flexible cables:
--mapmakerLeave a comment:
-
I'm sort of wondering about what happened with Mike's box what would happen if it had a cascade failure. If the bar can get hot enough to melt the standoffs on the bar in a metal box and short out - how big is the fire going to be? You can think you got it fused but DC power is pretty mean compared to AC when that happens.
Years ago when we first started out here we had an old DR-series inverter (I don't think they make those anymore) and a bus in a metal box. We just had marine deep cycles then - 12V batteries hooked in series and parallel. We'd just go to Farm and Fleet and buy a couple more batteries and add them in when we had the money for it and eventually we ended up with 9 strings hooked into that bus box. I had 200A inline fuses on them.
I was working on it one day and had one of those Craftsman hammers with a steel handle with a rubber grip on it. I hung the hammer on the wall by the claw on a nail. Somehow that hammer fell off, hit the top of the box and flipped in mid-air and went inside the box and came into contact with the positive bar. It was not just sparks - it was an instant explosion and the top half of that hammer was instantly turned to molten metal that sprayed me (I still got some burn scars from it) with a brilliant flash of light.
It never blew a single fuse on any of the strings. Every since, I been scared crapless of DC bus boxes hooked to batteries.Leave a comment:
-
You need to try finding them here! Everyone just looks at me funny.Leave a comment:
-
That doesn't surprise me. The only place that handles ferrules around here is Viking Electric and they only sell to contractors. The contractors usually got 'em in the truck in their tackle box. But no other stores around here carry them either.Leave a comment:
-
the hot buss bar crisped the plastic standoffs. Both of them. Got a new wire in today, to a new setscrew in the buss bar, and that's working fine. But #4 wire does heat up with just 45 amps continuous through it, so I may move to #2. Maybe NE code only assumes 30% duty cycle, but with solar PV, when the sun shines, the batteries charge for hours - 100% duty cycle.
And I'll have to recheck the set screws now.
And the large electrical house in the area, does not stock ferrules
Leave a comment:
-
Mike, was the bus bar and the standoff damaged too?
When we put in our new system I debated and debated over whether or not I should get one of them MidNite boxes. But then decided to build my own. I stole a couple bus bars out of an old Cummins generator switchgear box and mounted them in a grey plastic electrical utility box that I got at Menards. It ain't UL Listed or none of that, but she'll handle 400 amps across the bus bars with no problem and it has bolted connections on the bars with stainless steel bolts. Although I did add a few of them bolt-on screw lugs to connect THHN wire to. I just tinned the wire where it goes in them screw lugs:
Leave a comment:
-
So, I'm going to go looking for a crimp on ferrule at any of the stores around here. got to get a pair of them, I'll be adding another controller and another 25 amps to that buss bar.Leave a comment:
-
Leave a comment:
-
Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 06:05 PM.
Leave a comment: