New Se 7600H inverter Drops out 1 to 5 times a day

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • cdtruckn
    replied
    Originally posted by ButchDeal

    bring it up to code. You also mentioned it was on a 20amp breaker which is not right either. It should be on a 40a breaker and disconnect and the wires should be rated for 40a as well.
    That was the capacitor. Sorry for the confusion 1st time on a forum. Still learning
    Last edited by cdtruckn; 05-29-2019, 04:03 PM.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by cdtruckn

    Solaredge must have called my installer because thy called me about what pg&e did. Thy are going to install a 40amp disconnect. I don't see what that will fix
    bring it up to code. You also mentioned it was on a 20amp breaker which is not right either. It should be on a 40a breaker and disconnect and the wires should be rated for 40a as well.

    Leave a comment:


  • cdtruckn
    replied
    Pg&e says 252v is max on there side. Normal here is 247v +- 2
    my inverter brought it up from 247 to as high as 257v when I shut it down it goes back to 247v

    Turn the inverter back on and it stay at 247v for a while 40 to 60 minutes then start to climb.

    Solaredge must have called my installer because thy called me about what pg&e did. Thy are going to install a 40amp disconnect. I don't see what that will fix

    Leave a comment:


  • bcroe
    replied
    Originally posted by cdtruckn
    He said that the connection on my power lines at the house was not pg&e connection (someone else installed the 200amp service) so he ran a new lines from the pole to the house at that time we pulled the meter and check all the connections. All the connections are good. I asked about pg&e line voltage, he pulled out a book that showed max voltage on there lines 252v max.

    I checked the meter and the voltage is 247v before the solar system wakes up. around 930am the solar system is producing around 5,500 watts I look at the meter and it has a voltage of 253v already, so I go to my other neighbor's house
    and check their voltage an it's the same I go two more houses down and is the same I come home and shut down my inverter and everyones including mine dropped to 247v .
    I turned on the inverter and the voltage stayed at 247 v now at 11am the voltage is climbing is at 250v I believe that is why it drops out several times a day.
    Did you get better balance between halves? I thought the legal limit was 120V/240V, not 247V?
    One fix to excess voltage tripout is to reprogram the inverter V monitors higher. Bruce Roe

    Leave a comment:


  • cdtruckn
    replied
    Talked to solaredge yesterday, thy tell me that the inverter is dropping out because of high voltage and line harmonics,
    so I called pg&e to check my power. The guy showed up and I explain what needs to be checked. He said that the connection on my power lines at the house was not pg&e connection (someone else installed the 200amp service) so he ran a new lines from the pole to the house at that time we pulled the meter and check all the connections. All the connections are good. I asked about pg&e line voltage, he pulled out a book that showed max voltage on there lines 252v max. He also checked the meter volt reading to make sure it was calibrated
    it was, I have seen my meter as high as 257v. So this morning
    I checked the meter and the voltage is 247v before the solar system wakes up. around 930am the solar system is producing around 5,500 watts I look at the meter and it has a voltage of 253v already, so I go to my other neighbor's house
    and check their voltage an it's the same I go two more houses down and is the same I come home and shut down my inverter and everyones including mine dropped to 247v .
    I turned on the inverter and the voltage stayed at 247 v now at 11am the voltage is climbing is at 250v I believe that is why it drops out several times a day. Trying to get ahold of my installer no one ever gets back to me. Called solaredge with this information thy are fast tracking. I believe my system is over volting my neighborhood.
    Last edited by cdtruckn; 05-29-2019, 02:31 PM.

    Leave a comment:


  • JSchnee21
    replied
    Well, before drawing any conclusions from a third party product. I would still get your inverter hooked up to the internet (sounds like you may have already done this) and your system registered in the SolarEdge web monitoring portal. With ethernet connectivity (or Ethernet to Wifi bridge (3rd party), you'll get 15min updates with 5min resolution and any warnings errors from the inverter will be logged to the portal. If you have the newer "screenless" HD inverter design you can check your firmware versions with the App or in the Web Portal. But unfortunately, there is no change log (in the web portal, at least) to record when things were updated.

    The other possibility could be a loose, cracked, or improperly torqued DC or AC connection. If it is flexing, expanding/contracting, or heating (due to increase resistance), you may get momentary breaks in the connection or enough line disruption for the inverter to briefly go into shutdown due to its "line reactive" circuity.

    Leave a comment:


  • cdtruckn
    replied
    Each line that hits the bottom is a drop out. This has happened every day except today at least not yet.

    Leave a comment:


  • cdtruckn
    replied
    Screenshot_20190528-123029_Sense.jpg

    Leave a comment:


  • cdtruckn
    replied
    Yes production drops to 0 full sun only for a minute then full production with no warmup. The line voltage difference was measured on the earth ground side green. When measuring from the neutral thy are the same.that is why I moved the inverter neutral to the neutral buss from the earth ground. Even though both are attached to the breaker panel there must be some resistance. I'm at full production now with 254 meter volts. Thy may have pushed a update because it has not dropped out so far fingers crossed.
    Last edited by cdtruckn; 05-28-2019, 03:27 PM.

    Leave a comment:


  • JSchnee21
    replied
    Are you saying the production amps from your inverter drops to near zero for ~1.5min and then resumes? Cloud passing in front of the sun?

    IMHO, the HD's series of inverters seems to still have a lot of software bugs. I'd contact SE directly and have them check and verify that your unit has the latest firmware.

    Also not an electrician, but if you only have a single load center, neutral bus and ground bus should be linked in the panel and tied into your grounding rod.

    Keeping the solar out of the equation for now, I'm more concerned about your 8V differential between L1 and L2. Do you have 200amp service from your PoCo. What is the differential with your main breaker off? How does it change under load?

    Unless the loads on your legs are VERY unbalanced, you shouldn't see an 8V differential between L1 and L2 from your PoCo. Generator maybe, under heavy unbalanced load. But there should be no sag (maybe 1 or 2 volts) coming from your PoCo. That might suggest a crack in your service cable. Or a heavy overloaded step down transformer on the pole.

    Use the SE monitoring portal to inspect your DC volts/current, and AC volts/current during these "drop outs." It could be the Inverter is set "too fusy" and limiting production if the PoCo values are out of spec.

    Leave a comment:


  • cdtruckn
    replied
    Well it through a code today 03X6E meter comm. Error, it doesn't have a meter.

    Leave a comment:


  • cdtruckn
    replied
    It is also on a 20amp 240v circuit breaker

    Leave a comment:


  • cdtruckn
    replied
    Its rated for 100,000 amps, lsp 100k

    Leave a comment:


  • Mike90250
    replied
    I noticed the neutral wire for the inverter was connected to the earth ground buss bar so I checked voltage L1 had 118v, L2 had 126v. so then I checked voltage with the neutral buss bar L1 was123v L2 123v 246v total, so moved the neutral to the neutral bus. I know earth ground and neutral can be tied together but in my panel that are not bonded other than attach to the panel that is painted, Still the inverter drops out. Then I found some have had luck with capacitor, surge protector. Well that didn't help.
    unless you are an electrician, stop messing with stuff. If that capacitor and surge protector are not rated for 600V, you are setting yourself up for a fire.

    Leave a comment:


  • J.P.M.
    replied
    Originally posted by cdtruckn
    The installer said not to touch it.
    Anything further to that, or are you S.O.L. ?

    Leave a comment: