    Originally posted by organic farmer

    If your gear takes a 'direct' lightning strike, it is likely going to be trashed. Period.

    If there is a nearby lightning strike which induces eddy currents on your conductors, there may be preventative measures you could take that will lessen the damage.

    I have two lightning rod towers up over my photovoltaic array. In the hope that if direct strikes happen in this area those strikes will go to one or both of my towers. As a previous poster said, a tower provides you an inverted 'cone' of protection.

    I served as an Electronic Tech on submarines for 20-years. Before I could bring any of my gear up out of a sub onto the pier, we had to ensure that the pier had lightning rods above the pier every 40 feet. So walking on the pier underneath those rods was 'protected' from any direct strikes.

    Protection from induced lightning could be in the form of voltage surge protectors.
    Thank you for such a clear explanation.

    Leave a comment:


  • organic farmer
    replied
    Originally posted by Kot Basil
    I hope my question is correct in the this thread, because it is regarding lightning protection. I've read there is a difference between a direct and induced lightning impact https://www.streamer-electric.com/pr...rying-solution, could someone explain it here to me, please? Is induced lightning protection the same as surge protection?
    If your gear takes a 'direct' lightning strike, it is likely going to be trashed. Period.

    If there is a nearby lightning strike which induces eddy currents on your conductors, there may be preventative measures you could take that will lessen the damage.

    I have two lightning rod towers up over my photovoltaic array. In the hope that if direct strikes happen in this area those strikes will go to one or both of my towers. As a previous poster said, a tower provides you an inverted 'cone' of protection.

    I served as an Electronic Tech on submarines for 20-years. Before I could bring any of my gear up out of a sub onto the pier, we had to ensure that the pier had lightning rods above the pier every 40 feet. So walking on the pier underneath those rods was 'protected' from any direct strikes.

    Protection from induced lightning could be in the form of voltage surge protectors.

    Leave a comment:


  • Kot Basil
    replied
    I hope my question is correct in the this thread, because it is regarding lightning protection. I've read there is a difference between a direct and induced lightning impact https://www.streamer-electric.com/pr...rying-solution, could someone explain it here to me, please? Is induced lightning protection the same as surge protection?

    Leave a comment:


  • ILFE
    replied
    And to think, people (not speaking of anyone on this forum) were calling me nuts for not using a lightning arrester.

    Leave a comment:


  • Sunking
    replied
    Originally posted by DanS26
    Our local POCO has tried to help. They now install an SPD right on the transformer can on the pole. IMO that helps a lot in keeping excess high voltage on their lines on the outside where it belongs. Don't know the clamping rating of those devices but it got to help.
    Let you in on a little secret. At the Transformer is as good as it can get as th eprimary device and the Utility gets a lot better quality than most could home owners can afford. Couple that with a Collar type meter and it cannot get any better. Only thing you can do to improve it is Point of Use strip to help add a layer of protection like your TV and Putter.

    Utility grade SPD Clamping voltage and Let Through is the same as what you can buy due to UL 1741 listed equipment. If anything little better than what UL specifies. Devil is in the details. TVSS can really only protect you from utility faults and nearby minor lightning strikes. No TVSS can protect you from a direct strike unless you have the budget of NASA and they may not be enough using EMP protectors the military uses for TVSS.

    Leave a comment:


  • DanS26
    replied
    I agree it is not good practice. Almost every house and farm in my neck of the woods is wired this way when using overhead service.

    Our local POCO has tried to help. They now install an SPD right on the transformer can on the pole. IMO that helps a lot in keeping excess high voltage on their lines on the outside where it belongs. Don't know the clamping rating of those devices but it got to help.

    Leave a comment:


  • Sunking
    replied
    Originally posted by DanS26
    No, you do not have to draw it up........I understand......pulling the meter is the Service Disconnect.
    OK Dan just trying to be helpful You can ggo in the basement 3-wire, you use the UL approved metal raceway approved as the the EGC conductor. It is not a Ground Electrode Conductor or even connected to dirt once inside.

    You see a lot of what you describe in homes with basements, especially older homes. Technically it complies with code, just not a good practice inviting outside inside your home. Good luck to you.

    Leave a comment:


  • DanS26
    replied
    No, you do not have to draw it up........I understand......pulling the meter is the Service Disconnect.

    Leave a comment:


  • Sunking
    replied
    Originally posted by DanS26
    Well, I'm in the backwoods of Indiana. We do not have a disconnect at the meter. Three wire from transformer to meter...then three wire from meter to main distribution panel (ie first disconnect) inside the house.
    Dan the disconnect has to be accessible to the FD. That is why the Meter itself is the Service Disconnect in most installations. All the FD has to pull the meter out. Code also requires that the utility Grounded Circuit Conductor to remain Solidly Bonded even when the meter or disconnect switch is operated. I will draw something up later for for you to look at if that will help. From the meter you can go in either 3 or 4 wire, makes no difference.

    Leave a comment:


  • DanS26
    replied
    Well, I'm in the backwoods of Indiana. We do not have a disconnect at the meter. Three wire from transformer to meter...then three wire from meter to main distribution panel (ie first disconnect) inside the house.

    Yes, if I move the first disconnect to the meter location then I would not have to direct over voltages into the house using the under meter SPD since I could then use a four wire connection between the meter and main distribution panel and the GEC would be completely outside the house.

    For a variety of reasons I do not want to move the first disconnect. So far I have just lived with the risk rather than violate the NEC rules.

    Leave a comment:


  • Sunking
    replied
    Originally posted by DanS26
    I have a code compliant three wire connection between the meter and main disconnect inside my house. The path would be from meter through the neutral wire into the main disconnect, then would have to reverse direction to leave via the GEC to the grounding electrodes.
    Dan you either have a misunderstanding or something wrong I am missing.

    You Meter collar as you say is 3-wire from the POCO Transformer. At your meter is most likely also your Service Disconnect Device and that is where the Earth Ground to Grounded Circuit Conductor (Neutral) is made. You are also there is no other conection made between ground and Neutral beyond that point electrically. With me so far?

    The SPD only has 3-modes meaning A SPD device connected between L1-N, L2-N, and L1-L2. There is no need for a 4th SPD L-G because it does not do anything if N & G are solidly bonded together or dead bolted Short Circuit. Lighting is seeking all paths to Dirt. If your N-G bond were inside your home basement means it has to come inside first before it can go back outside where it came for and looking for in the first place.

    Leave a comment:


  • DanS26
    replied
    SK, I had my POCO install the SPD collar on my meter just like in your pic. It cost me $90. As the lineman was installing the SPD it appeared to me that if that device worked as advertised it would direct high voltage current directly into my main distribution panel located in my basement. I have a code compliant three wire connection between the meter and main disconnect inside my house. The path would be from meter through the neutral wire into the main disconnect, then would have to reverse direction to leave via the GEC to the grounding electrodes.

    If I install a GEC from the meter directly to the grounding electrodes on the outside of the house, I then create a duplicate neutral path which is frowned upon by the NEC. I am tempted to add this additional GEC from meter to grounding electrodes since I have this device installed on my meter.

    Leave a comment:


  • Sunking
    replied
    Steve that is certainly a step in the right direction and most certainly one-step of a good Power Protection design. I am very familiar MR65 and other such documents. Having said that the POCO Collars TVSS are a bit light duty. If you know how to get in touch with me, do so with your email address and I can send you some documentation via email. I would say PM me here, but I digress.

    One way to find me since you are a Pro, consider join Mike Holt Code Forum and reply back here when done. I will then Log in to Moderator Panel and look at your email address, approve your membership if another MOd does not beat me to it. We screen applicants. Just be sure to use the same username and a real email address. Once you are a member there, you can get all your technical questions answered on any electrical subject including Solar from pros who do it every day for a living.

    DIY need not apply, for professionals and students with credentials or references

    Let me know and hope that helps.

    EDIT NOTE TO STEVE:

    Crap Steve it just occured to me who you are and you know how to reach me. I know you kind of and you are already a member at MH. My bad. Let me know if you want the documents or call me and we can discuss. You know how to find me. . That is what happens when you get old. My daughter Amy and Jr. are doing great, hope your kids, you, and all your family doing great too along with you and all your family.
    Last edited by Sunking; 12-30-2016, 02:47 PM.

    Leave a comment:


  • sdold
    replied
    Dereck, would that SPD collar on the meter be something we should look into using at repeater sites? We do also (try to) comply with the rest of the codes and Motorola R56 that you might be familiar with.

    Leave a comment:


  • Mike90250
    replied
    Yep. A direct strike and you are toast. But the protection can help with induced voltages from near strikes.