Try our solar cost and savings calculator
Net Metering to Distributed Generation Program.
Collapse
X
-
Definitely depends on usage during periods of generation but the max hit for jschner (which is what this thread is about) is calculated in post 1 at about $600 / year (not as I misstated $60 / month) based on his actual load and actual generation. It won't be $150 / month. Also, "modern" dishwashers, washers, dryers have timers. Usage on weekends is generally different than weekdays. One can put a timer on their water heater and delay morning water heating load until high generating hours. You don't have to be retired to shift load.Actually, whether or not the classic net metering and the IN vs. OUT at separate prices come anywhere close to each other depends very strongly on whether or not the user has large local loads during the peak production hours.
Consider two hypothetical users:
1. Nobody home during the day, and all of the housekeeping (dishwasher, showers, cooking, A/C, etc.) take place in early morning or late evening. If this user sizes the system to offset 100% of total load power, he will end up paying a little less than 1/2 of his original (no-PV) bill.
2. Retired person who occupies the home during the day and runs the A/C, etc, and is careful to schedule cooking, washing, etc. during solar production hours. With the same size system as above, that person will have a close to zero bill.
With classic net metering, both of them would have a zero bill.
I can easily see a difference of more than $60 per month for user A under the new plan as long as their no-PV bill was more than $150/month!
There is really is no basis for the "a little less than 1/2 of his original bill". The worst case is 1 kWh of usage paid at $0.1437 and 1 kWh of generation sold at $0.0865. So, the No-PV bill is $0.1437. The with PV net bill worse case is $0.0572. 572/1437 = 40% worse case which is a lot less than 50% and the 40% assumes no offset of instantaneous load with instantaneous generation which there will be some.Leave a comment:
-
2 meters system: you are not sure if the power generated send to the grid is growth or net after consumption. That is why I told him to check. If he has to sell ALL to POCO then never mind, $0 saving. If the power send to the grid is net after consumption, try to do all the house keeping during solar production.Leave a comment:
-
Actually, whether or not the classic net metering and the IN vs. OUT at separate prices come anywhere close to each other depends very strongly on whether or not the user has large local loads during the peak production hours.
Consider two hypothetical users:
1. Nobody home during the day, and all of the housekeeping (dishwasher, showers, cooking, A/C, etc.) take place in early morning or late evening. If this user sizes the system to offset 100% of total load power, he will end up paying a little less than 1/2 of his original (no-PV) bill.
2. Retired person who occupies the home during the day and runs the A/C, etc, and is careful to schedule cooking, washing, etc. during solar production hours. With the same size system as above, that person will have a close to zero bill.
With classic net metering, both of them would have a zero bill.
I can easily see a difference of more than $60 per month for user A under the new plan as long as their no-PV bill was more than $150/month!Leave a comment:
-
jschner, are you saying that the City is going to sum energy coming into the meter and energy going out of the meter for the billing period? So, apparently the city is replacing the net meter with one that accumulates IN +Flow (delivery to customer) and OUT -Flow (excess generation purchased by City). You pay for energy coming in at $0.1437 / kWh and you get credit for energy going out to the utility at $0.0865 / kWh. Actually that's not as bad as I thought in that your generation on an instantaneous bases does offset usage at the $0.1437 rate. It's your excess instantaneous generation that gets paid at the $0.0865 rate. Problem is how does one estimate what that might be and how it affects the Solar 13? If this is the case, you want to shift load into your high production hours (especially on clear days).
However, this is not what is in the resolution presented to the Council. It clearly shows that the old Net Metering = Co-metered (Delivery minus Generation). What is in the Council resolution is IMO significantly more costly to the Solar 13 than the instantaneous in and out metering because one can offset load with generation. Actually, this is fair. The only question is what is the power delivered to the City worth. It appears they give credit for purchased power cost and RECs in the rate - seems fair. I believe the resolution needs a lot more clarity on this. If the resolution is based on instantaneous accumulated in and out meter readings then your original estimate / interpretation of $600 / year hit is likely significantly overstated.Leave a comment:
-
I think Tom misunderstands Example 2. He claims "Assumes solar production is greater than household consumption by 200kWh" when shouldn't it be "assumes solar production is less than household consumption by 200kWh?" In any event, I think you are right about needing a meter that tracks instantly - and separately - the kWh's going into and out of the home. That's the type of meter we have here in Phoenix (APS); in fact it also tracks instantly and separately the peak kWh's going in and out. APS then does an on-bill subtraction to give the off-peak kWh's going in and out. APS doesn't bother at all with the production meter at least for billing purposes.I'm working on the formal proposal to the city for first, grandfathering existing customers and second, making changes to the DG program. In the mean time I asked for clarification of the meters needed and formulas.
Here is my email:
I get what is happening here. My examples were not exactly right but it did clarify things. They need to change my meter and want to track ALL incoming and outgoing power by the minute to my home instead of by the month and buy my exported power at the lowest rate and sell my power back to me at full retail rate. Negating all the reasons why they promoted solar in the first place and the fact that in a year I only use 426kWh net. Anything else you guys can see in these examples?
While I'm producing power in excess, are my neighbors not using that power at the full rate while the city is sourcing that much less? It appears the city will be double charging for power here. I'm still trying to wrap my head around that.Leave a comment:
-
I'm working on the formal proposal to the city for first, grandfathering existing customers and second, making changes to the DG program. In the mean time I asked for clarification of the meters needed and formulas.
Here is my email:
I get what is happening here. My examples were not exactly right but it did clarify things. They need to change my meter and want to track ALL incoming and outgoing power by the minute to my home instead of by the month and buy my exported power at the lowest rate and sell my power back to me at full retail rate. Negating all the reasons why they promoted solar in the first place and the fact that in a year I only use 426kWh net. Anything else you guys can see in these examples?Jim –Tom,
Thanks for taking the time last night to answer questions.
Real quick two things were not explained enough to help us understand fully.
First, the two meters. I understand there are single meter customers out there but I need to understand my situation better which is probably most of the solar customers. I currently have two meters. A production meter that shows how much my solar produces and a use meter whatever you call it that spins forward and backwards that shows my overall house net use after solar.
Other than not being wireless, are those meters sufficient to operate under the new DG program? If not please explain why and what the difference is in the way the meter reads. If they are sufficient, then I really need is to be able to understand the example given in the spread sheet.
Second, the example bill. It is still not fully clear. I would like to give you three scenarios and hopefully you can create three tabs on an excel sheet or send me three separate bill examples.
For ease of understanding I assume starting at 0000 on both my meters for all three examples. That would represent the new monthly "true up" in the DG program correct?
Example #1 starting at 0000 and 0000, after 30 days the meters read: Production meter = 1000kWh - 2-way meter = 0kWh
Example #2 again starting at 0000 and 0000, after 30days the meters read:Production meter = 1000kWh - 2-way meter = 200kWh
Example#3 Starting a 0000 and 0000, after 30days the meters read: Production meter = 1000kWh 2-way meter = 9800kWh <---spun backwards.
I'm sure you can understand why the three examples. What I need to understand in your spreadsheet is how these numbers are plugged in because the example is not clear. The example given in the Nov 15th Agenda shows "300" and "530" and you mentioned last night that represents the customers monthly 830kWh personal usage.
These calculations are at the heart of the matter really. And maybe I'm wrong in my understanding of them? So you don't have to explain everything in words, if you don't mind, please plug my examples into three separate spreadsheets and send all three via email if you can.
I'm pretty sure with these three examples I can figure it out and understand the numbers a lot better.
Thank you very much,
Jim
The net meter does not tell us how much, in total, was taken from the utility and how much, in total, excess solar is put back into the grid; it only tells us by the meter reading at a point in time compared to the next meter reading the results of traffic for the time period.
For example:
On a two lane road with a north and south bound lanes there are 100 cars passing a given point going north. At the same point there are 12 cars travelling south. So the total traffic is 112 passing the point with 88 more cars heading north. The City’s net meter only tells us there are 88 cars going north.
The existing meter is insufficient in providing a true picture of activity.
From the DG perspective
Example #1
· Assumes 0 kWh energy provide by the utility; Charge to solar producer is $14.50
· Assumes total solar production = total household consumption perfectly during all 720 hours in a month
· Solar production 1,000 * $0.0865 = $86.50 paid to household
· Household has $72.00 credit on bill
Example #2
· Assumes solar production is greater than household consumption by 200kWh
· How many kWh went to the household from the utility? Charge to the household; $14.50 plus toll from any kWh heading to the household; total charge unknown
· Solar production 1,000 * $0.0865 = $86.50 paid to household
· Unknown charge less $86.50 is presented on the bill
Example #3
· Same answer as example #2
From the Net Meter perspective
· Example #1
· Household billed $14.50 for the current month
Example #2
· Household billed $14.50 for the current month
· Household billed 200 kWh times $0.1437 = $28.74
· Total monthly charge is $43.24
Example #3
· Household billed $14.50 for the current month
· 200 kWh held off book for 12 months; if the carryover is still there after 12 months than 200 kWh * $0.0341 = $6.82 paid to household
· Total monthly charge is $7.68 the month of 12-month settlement
I hope this helps. If not, keep asking away.
Thanks for being an active participant. I truly appreciate the discussion.
Tom M.
While I'm producing power in excess, are my neighbors not using that power at the full rate while the city is sourcing that much less? It appears the city will be double charging for power here. I'm still trying to wrap my head around that.Leave a comment:
-
Leave a comment:
-
That's probably true - city council would likely rather look good to the vast majority for political reasons and may not even be the same that promoted Solar.I am sure the city council cares - not. This is a downside for those who have taken advantage of subsidies and incentives. The vast majority that haven't used those financial aids are not too sympathetic. On the site solar is the big thing but in the real world - different story.
IMO, the 13 solar owners in the City have one card to play - "begging for mercy" - grandfather the "Solar 13" at little extra cost to the rest of the City's electric customers. Spread say $7,800 ($600 *13) a year over all customers say $3.00 / year additional for the mistake of the previous council. Can the current council in good conscience ask 13 residential customers to pay around $600 per year more so that other customers might save $3.00 a year?Leave a comment:
-
I am sure the city council cares - not. This is a downside for those who have taken advantage of subsidies and incentives. The vast majority that haven't used those financial aids are not too sympathetic. On the site solar is the big thing but in the real world - different story.Exactly. The city made a decision that they now regret and they're screwing those who made a long term financial commitment based on trusting the city's original decision. Grandfathering is a fair and cheap solution (so few solar customers anyway) and if they won't go for that, then if I were living there, I'd make sure the council did not get re-elected and I'd bad-mouth the city every chance I got.Leave a comment:
-
Exactly. The city made a decision that they now regret and they're screwing those who made a long term financial commitment based on trusting the city's original decision. Grandfathering is a fair and cheap solution (so few solar customers anyway) and if they won't go for that, then if I were living there, I'd make sure the council did not get re-elected and I'd bad-mouth the city every chance I got.You really need to get the other solar owners to perhaps sign a petition to such indicating how they were "duped" by the City when they put in solar. The City needs to recognize that perhaps they made a mistake earlier in support of solar but should honor their original support of solar as they are now causing financial harm to 13 CIty residential customers with their decision.Leave a comment:
-
The City says they can buy power at $0.0865 per kWh. The presumption is that is the delivered price to the City. Get a copy of their power purchase contracts. So, if it is the delivered price, the City is in essence paying for transmission of the power to the City under FERC approved tariffs. The relief on the City side is virtually non-existent and won't be a factor until there is a high saturation of solar. So, why should a non-solar City customer pay extra now to help increase solar in the City so that perhaps there is a distribution or other benefits years in the future.
The problem you are facing is that Solar cannot stand alone now without subsidies / tax credits / net metering in the hopes that the benefits will be reaped by all in the future. IMO, your best bet is to seek grandfathering since the City promoted solar in prior years. You really need to get the other solar owners to perhaps sign a petition to such indicating how they were "duped" by the City when they put in solar. The City needs to recognize that perhaps they made a mistake earlier in support of solar but should honor their original support of solar as they are now causing financial harm to 13 CIty residential customers with their decision.Leave a comment:
-
Re-read what I wrote. I switched from 20 amps on my side to saying 4kW to 5kW of relief on the transmission side because I did not know what their voltage was.The flaw in your thinking is that 15 to 25 amps on your side of the service transformer equates to 15 to 20 amps on the transmission side if completely false. Distribution is at 13.2 Kv and Transmission as high as 750 Kv, not the 240 volts at your transformer. 5 Kw on a 13.2 Kv Distribution line is 0.38 amps, and on 750 Kv Transmission is .006 amps. Neither is enough to make a bit of difference on lines that carry up to 2000 amps. It is like saying carrying an extra quarter in your pocket is going to effect your cars gas mileage. So if you bring that up to informed people are going to know that and completely dismiss anything you have to say.
Anyway, thanks for the info.Leave a comment:
-
Yes but the flaw is that it is a two meter system. He is being forced to sell ALL his power low and purchase back his own power at higher prices.
If it were a single meter he would be able to use his own power and avoid purchasing the higher cost power from the grid. Yes his excess power would be sold less than the net price but at lease he could time his usage to take best advantage of his own production.Leave a comment:
-
Net Metering by legal definition is you buy and sell at the same price. If you are a biz and do that you go bankrupt.I know it is a "2 meters" system now. you sell all your generated power back to the grid at 0.0865 per kWh. Is it the net (after your usage like net metering) or you have to sell ALL of your power generatied? Find out on this part, it is very important. At least you can use less energy from the grid during solar production and make your money worth.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.