The other concern is that with these load shedding appearances, the power surges quite a bit when its diverted back. And during the last 3 years we have heard lots of stories of fridges, TVs, etc blowing up due to the power spikes..
So your backup battery, needs to only last you for 3 hours or so, and then it can be recharged from the grid. (I expect your grid power is still less expensive than solar)Leave a comment:
-
Yes i have looked at what it would work out on, and it would work out more expensive for the next 3 years or so.
Here in South Africa our electricity supplier Eskom, barely has enough capacity to supply the whole country, and during peak times we tend to have rolling blackouts, or as its called here, load shedding. Peak hours is when everyone gets home after work, starts cooking, watching TV, bathing, etc. Now to have no power for an hour or 2 during that time is not so nice. I think if i at least have some lights running off battery it would soothe the annoyence.
Now to compensate for the low capacity, they are building 2 new power plants, but those will be up and running in 1 to 2 years time. And as all African systems seem te be operated, there isnt enough money around to finance completion. So now we will be getting rates increases ranging from 21 to 28 % every few months from Eskom, to try and get funds available. As it stands, it appears South Africa already has the most expensive electricity in the world, and that will just keep getting worse the way these increases happen. In the last year our electricity bill went up by about R160 or $21 per month. And ours is just a small household. Some larger homes are almost paying R1000 or more each month.
So i understand what you're saying, but i think we will get to a point where the grid supplied power will costthe same, if not more than the solar option.
The other concern is that with these load shedding appearances, the power surges quite a bit when its diverted back. And during the last 3 years we have heard lots of stories of fridges, TVs, etc blowing up due to the power spikes. This is the 2nd concern to get the essential appliances on to a independant of the grid system.
So that being said, i need to confirm that the factor of 5 you said is then to allow for a larger capacity bank. Which means that i only need a battery bank of 210Ah, not the 1050 i calculated.
Thanks for your feedback guys, it is really helpful.Leave a comment:
-
So my daily Whours are = 4W * 14 units/lights * 6 hours = 336Wh.
Now i found the formula for battery Ahours calculations on the forum, which im hoping is correct: Ah Capacity = (daily wh * 7.5)/V
Using that my Ah = (336 * 7.5) / 12 = 210 Ah. Now i dont know why they have the 7.5 in there, so can anyone advise what its for?
Now with that said I really have to ask what are you thinking? You have commercial power right? Why on earth would you want to take anything off grid and on to batteries?
Going off grid, especially on such a small scale is going to cost you at least 20 times more for electricity. National average is 10.8-cents per Kwh, down from 12.1 cents 3 years ago. The system you are thinking about will generate about 2 cents of electricity per day. That works out to 60-cents/month, $7.20/year, $36/5 years.
That 12 volt 200 amp hour battery alone is going to cost you about $300 and will need replaced in a few short years. Assuming just the battery cost and it can acutally last 5 years, it will not, you will be paying about $0.50/Kwh. 5 years from now the price of that battery will be $400. That is just the battery cost and nothing else.
Have you stopped and thought about that?Leave a comment:
-
Ok i have done some calculations for the LED lighting system alone. The fridge running for the whole day (6 hours guestimating it actually running at full power) with the LEDs running for 6 hours will require a panel wattage of about 730W, wich is already too large in physical size to accomodate.
The LED lights run on 12V, so im stuck with that on battery voltage. I have 14 light fittings, so i can use 14 LED lights running at 4W each. Now i wont be using all of them at once of course, but at least 8 of them at once, but im designing for maximum usage, so using 14. And even then i wont be using them for more than 6 hours a day.
So my daily Whours are = 4W * 14 units/lights * 6 hours = 336Wh.
Now i found the formula for battery Ahours calculations on the forum, which im hoping is correct: Ah Capacity = (daily wh * 7.5)/V
Using that my Ah = (336 * 7.5) / 12 = 210 Ah. Now i dont know why they have the 7.5 in there, so can anyone advise what its for?
Now, assuming i dont want to discharge my battery bank below 80% of total capacity, i would assume that if 20% equates to 210Ah, my battery bank needs to be at least 1050Ah? Would i be correct in my assumption?
Ok, since i need to be able to replace the energy used each day, my panel size i calculate as follow, assuming 5 sun hours, and a 50% efficiency using a PWM charge controller: P Watts = Total Wh / Charge loss / Sun hours
P Watts = 336 Wh / 0.5 / 5 = 84W. So a 85W panel should do the trick. Doing a quick search on locally available panels, i find one 85W panel that might fit. It has a maximum voltage of 18.2V, a maximum current of 4.7A, an open circuit voltage of 22.2V and a short circuit current of 5.3A.
BUT, if i want to have a C/8 maximum charge rate or 13%, i would need to be limit the charge at max 27.3A. And a minimum rate of 5% or C/20 giving me 10.5A. So i would need to be in the range of 10.5 to 27.3 A to charge the batteries. So would i need to then have 3 of the 85W panels above in parralel just to get above the minimum limit, giving me 3 x 4.7 = 14.1A?
If im correct with my above statement, using the Charge controller = Solar panel W / Battery Voltage formula, my charge controller should be = (3 x 85) / 12 = 21.25 Amps, so a 30 A controller should be sufficient.
Ok, this is my calculations and assumptions. Please check if im going about it the the correct way, or if im cocking up big time.
Thanks in advance.Leave a comment:
-
Will not affect charge time at all.
with your 10 12 volt batteries in parallel you have a capacity of 12 volts x 1000 AH = 12,000 watt hours. To charge them at the C/10 rate, 100 amps would require 1200 watt panel. If you were to reconfigure the batteries all in series to 120 volts at 100 AH, Would still require a 1200 watt panel to generate a C/10 charge rate of 10 amps.
But to answer your question you should be using a higher battery voltage so you only require 1 charge controller. Problem is 10 batteries do not fit for 24 or 48 volts. With 10 batteris your only option is 24 volts or 5 parallel strings. That would allow you to use a 80 amp charge controller and allow a panel wattage up to 2000 watts. At 12 volts the most panel wattage you can have is 1000 watts with an 80 amp charge controller.
So in effect i would need to have a battery bank to sustain the fridge, and a seperate 12V battery to run the lights off. I think 1 should be sufficient, but will calculate the exact requirements to make sure.
I am limited to the amount of panels i can use, as i have a middle floor apartment, and we are not allowed to install anything on the roof. I will probably be able to install them on my balcony. This will however limit my exposure i know, so ill have to ensure my charging/battery capacity is enough.
Thanks again.Leave a comment:
-
mppt
does it mean an mppt technique
[ mod note - we won't accept attachments (especially PDF) from new users, till we have some idea of what the story is, a terse one liner is not enough to allow PDF's with all the nasty tricks that can come with them on un-patched computers. ] Expound more, in text, of what you are trying to say.Last edited by Mike90250; 10-09-2011, 10:03 AM.Leave a comment:
-
with your 10 12 volt batteries in parallel you have a capacity of 12 volts x 1000 AH = 12,000 watt hours. To charge them at the C/10 rate, 100 amps would require 1200 watt panel. If you were to reconfigure the batteries all in series to 120 volts at 100 AH, Would still require a 1200 watt panel to generate a C/10 charge rate of 10 amps.
But to answer your question you should be using a higher battery voltage so you only require 1 charge controller. Problem is 10 batteries do not fit for 24 or 48 volts. With 10 batteris your only option is 24 volts or 5 parallel strings. That would allow you to use a 80 amp charge controller and allow a panel wattage up to 2000 watts. At 12 volts the most panel wattage you can have is 1000 watts with an 80 amp charge controller.Leave a comment:
-
Ok, so would you recommend having a higher voltage battery then?
If you up the voltage, and lower the Ah capacity, will it decrease your charge time? My mind is realing now on all the questions i have, but will reasearch a bit more before i post something silly.Leave a comment:
-
Thanks Sunking.
One more question. If i have a battery bank consisting of 10 x 100 Ah 12V batteries, wired in parralel, i would still just apply a charge of 13A to the bank? Or will i have to boost it to 130A which is 13% of the 1000 Ah capacity? I guess what im getting at is do i work on 13% of the bank capacity or the capacity of each battery in the bank?
To be honest you are going to have a lot of problems with batteries in parallel keeping them all equalized. You will likely be replacing the batteries every year or two. The other problem you are going to have using 12 volts at that battery capacity you wil have to use at least 2, maybe 3, or more charge controllers.Leave a comment:
-
Thanks Sunking.
One more question. If i have a battery bank consisting of 10 x 100 Ah 12V batteries, wired in parralel, i would still just apply a charge of 13A to the bank? Or will i have to boost it to 130A which is 13% of the 1000 Ah capacity? I guess what im getting at is do i work on 13% of the bank capacity or the capacity of each battery in the bank?
Thanks in advance.Leave a comment:
-
On the low side you do not want to go below C/20 or 5%.
To determine panel size to do that job depends on the charge controller type used. If you use a PWM charge then input current = output current. So using a standard 12 volt panel @ 13% you need the panel current to = 13 amps and that would require about a 210 watt panel.
For MPPT to find the panel wattage is easy. Watt = Volts x Amps. So with a 12 volt battery and 13 amps = 156 watts or round up to 160 watts.Leave a comment:
-
that you don't want to exceed, when charging. Otherwise, you overheat the battery and damage it. Even if it's only 0.5% each damage cycle, in a year (360 cycles) , that can add up. And that varys, when the battery is discharged , it's a little safer to charge it faster, but as it approaches 80%,
Mod note - Links are not allowed - you can post your email in your profile if you wish
Leave a comment:
-
Thanks Mike. Now i know.
All the more important to get the correct charge controller to ensure the batteries dont boil.
Thanks guys for your input.Leave a comment:
-
2) 90% is your own invention. I said 80% (of full), after that the charge rate has to slow down or the battery can/will boil. That's always bad.Last edited by Mike90250; 09-29-2011, 11:56 AM.Leave a comment: