I am relocating an existing solar system and also adding four more panels at the same time. I am changing to a single 11.4KW Solaredge inverter I got cheap since my two Solaredge inverters were maxed out. I want to keep one of the old inverters to add more panels at a later date. Garage is being torn down and replaced with much larger garage so panels have to come off roof and ground mount has to move.
Current config is combo of ground mount and panels on detached garage roof with two Solaredge inverters. AC runs 80 feet to house with about a ten foot run of DC to each string.
New config will be two ground mounts with a single inverter to start. Original plan was to run AC 200 feet to inverter with DC going about ten feet to panels. It sounds like I should mount the inverters close to meter so AC run is a lot shorter and DC run is much longer.
Most Popular Topics
Collapse
AC Disconnect Sizing and Type for Line Tap (no backfeed)
Collapse
X
-
This is going to completely screw with my plans then. I don't really have any place to mount two inverters near my meter. The east wall of my house will already be covered in electrical and gas stuff. I will have a gas meter, meter base, 200 amp disconnect switch, and utility required disconnect for my solar on that wall already. It is also the wall all guests walk by, but I could count on both hands how many guests I have had in six years use the front door.
Solaredge uses a constant DC voltage of approximately 350 volts. I'm not sure if I will have issues running three DC strings through a single conduit. I will absolutely have to go with conduit and not direct burial if I have to run multiple strings of DC.Leave a comment:
-
The breaker is next to the inverter and the inverter is next to the panels. My understanding has always been that AC has less voltage drop than DC. Remember the whole Tesla vs Edison thing when electricity was still a new thing? Tesla won out with AC because AC go go long distances with less voltage drop.
wire loop to the PoCo meter. But efficiency is not the reason, Tesla managed efficient
long distance transmission by sending power at very high voltages and low current, then
using a transformer to bring the voltage down near the consumer. A transformer does
not work on DC. Bruce RoeLeave a comment:
-
Solaredge uses a constant DC voltage of approximately 350 volts. I'm not sure if I will have issues running three DC strings through a single conduit. I will absolutely have to go with conduit and not direct burial if I have to run multiple strings of DC.Leave a comment:
-
The breaker is next to the inverter and the inverter is next to the panels. My understanding has always been that AC has less voltage drop than DC. Remember the whole Tesla vs Edison thing when electricity was still a new thing? Tesla won out with AC because AC go go long distances with less voltage drop.
I believe 240v DC is actually even better than 240v AC since DC is able to transfer more power per volt since it doesn't alternate. Most PV system operate at >350v DC. ~350vdc is WAY better than 240vac.
With grid-tied solar you want your DC voltage as close to 480v as you can get it without going over 600v open circuit. Then keep your DC lines long and your AC lines short
Leave a comment:
-
The breaker is next to the inverter and the inverter is next to the panels. My understanding has always been that AC has less voltage drop than DC. Remember the whole Tesla vs Edison thing when electricity was still a new thing? Tesla won out with AC because AC go go long distances with less voltage drop.Leave a comment:
-
Leave a comment:
-
[QUOTE=nwdiver;n420427
That's common with line side taps as the rules posted up thread outline. I've done a couple installs like that. It's treated in a similar way to your main panel. No way to de-energize the wire feeding your main breaker without pulling the meter either.[/QUOTE]
The connection from my meter to my main load center is less than 10 feet. My solar tap runs 70 feet before the first breaker. My new solar tap is going to be almost 200 feet before the first breaker.
I am not going to worry about it so long as what I am doing meets code.Leave a comment:
-
That's common with line side taps as the rules posted up thread outline. I've done a couple installs like that. It's treated in a similar way to your main panel. No way to de-energize the wire feeding your main breaker without pulling the meter either.Leave a comment:
-
There is a breaker next to the inverters. The wire from the meter to the breaker next to the inverters has no way to de-energize without pulling the meter.Leave a comment:
-
10-Foot Feeder Tap Rule [240.21(B)(1)]
Feeder tap conductors can be run not over 10 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 1
(1) The ampacity of the tap conductor is:
1 Not less than the computed load in accordance with Article 220, and
2 Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the equipment they supply.
(3) The tap conductors are installed in a raceway if they leave the enclosure.
(4) The tap conductors have an ampacity of no less than 10 percent of the ampacity of the overcurrent protection device from which the conductors are tapped.
25-Foot Feeder Tap Rule [240.21(B)(2)
Feeder tap conductors can be run not over 25 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 2
(1) The ampacity of the tap conductors is not less than 1/3 the ampacity of the overcurrent protection device protecting the feeder.
(2) The tap conductors terminate in a single circuit breaker, or set of fuses having a rating no greater than the conductor ampacity as listed in Table 310.16.
(3) The tap conductors are suitably protected from physical damage or are enclosed in a raceway.
Leave a comment:
-
A line side tap will require the wires to be rated as much as the bus bars are or they can be 1/3 less if the length is 10 feet or less. There is another 25 foot rule that I can't quite remember what the requirements are.
The whole idea is to make sure the wires are protected by some type of over current device.
Feeder tap conductors can be run not over 10 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 1
(1) The ampacity of the tap conductor is:
1 Not less than the computed load in accordance with Article 220, and
2 Not less than the rating of the device supplied by the tap conductors or the overcurrent protective device at the termination of the tap conductors.
(2) The tap conductors do not extend beyond the equipment they supply.
(3) The tap conductors are installed in a raceway if they leave the enclosure.
(4) The tap conductors have an ampacity of no less than 10 percent of the ampacity of the overcurrent protection device from which the conductors are tapped.
25-Foot Feeder Tap Rule [240.21(B)(2)
Feeder tap conductors can be run not over 25 ft without overcurrent protection at the point they receive their supply, but they must be installed in accordance with the following requirements: Figure 2
(1) The ampacity of the tap conductors is not less than 1/3 the ampacity of the overcurrent protection device protecting the feeder.
(2) The tap conductors terminate in a single circuit breaker, or set of fuses having a rating no greater than the conductor ampacity as listed in Table 310.16.
(3) The tap conductors are suitably protected from physical damage or are enclosed in a raceway.
Leave a comment:
-
I had a solar electrician wire my solar stuff in 2017. I was a little bit surprised there is no breaker, fuse, or disconnect for the load side tap he installed. The only way to de-energize the underground wire from the meter to the inverters is to pull the meter. It was all permitted and passed inspection, but I don't know that the inspector checked that side very closely.
The whole idea is to make sure the wires are protected by some type of over current device.Leave a comment:
-
I had a solar electrician wire my solar stuff in 2017. I was a little bit surprised there is no breaker, fuse, or disconnect for the load side tap he installed. The only way to de-energize the underground wire from the meter to the inverters is to pull the meter. It was all permitted and passed inspection, but I don't know that the inspector checked that side very closely.Leave a comment:
-
I had a solar electrician wire my solar stuff in 2017. I was a little bit surprised there is no breaker, fuse, or disconnect for the load side tap he installed. The only way to de-energize the underground wire from the meter to the inverters is to pull the meter. It was all permitted and passed inspection, but I don't know that the inspector checked that side very closely.Leave a comment: