neutral overload can only happen if you start making changes to the loads after connecting PV and only when it actually producing electricity. Come cloud / night and the main breaker would trip (if the system makes that far after changes). If we stick to the original case of up-to-code MSP and then adding PV to it the only consequence is cooler busbar..
Don't get me wrong- I respect the Code for it providing consistent set of rules and accumulating measures which would prevent mistakes. OTOH I don't worship the Code for multiple reasons. It is written by people, not some tech gods. People are susceptible to politics, mistakes, etc. Just one such example you sited yourself: it took them 3 years between 2011 and 2014 cycles to realize the headroom in breaker current rating is not going to heat up the MSP busbar. When things like this get missed my desire to understand their reasoning behind other rules increases even more.
Try our solar cost and savings calculator
Most Popular Topics
Collapse
Noob needs more help (pics inside)
Collapse
X
-
Surprisingly all discussions related to the rule revolve around busbars without anyone ever bringing up problem of asymmetric load overloading neutral with people commonly upgrading their MSPs even though the service wires are often sized to support higher current such that only MSP gets replaced. Based on this discussion that is not really needed.
Anyway, even if you increase the size of the service conductor, the neutral bus+lug are still potentially getting overloaded. Even if you add in some 120 V loads on L2 to balance the service neutral conductor, the neutral bus could still have areas that are overloaded, depending on where each of the connections are made in the bus.
Clearly I'm out of my expertise here and just throwing stuff to the wall to see what sticks, and I'm fine with conceding the point on L1/L2 bus temperature for the scenarios you and foo1bar have walked through. I just think that is is generally a bad idea to try to get into the mind of the code panel and pick it apart on the basis of one particular aspect of the system (which might be the most obvious place to look), without considering the impact to the entire system. It is a slippery slope to attempt to qualify code with "too conservative" or "not conservative enough" without more training and experience than I think most of us here possess.Last edited by sensij; 09-28-2017, 01:14 PM.Leave a comment:
-
Its good to thrash this subject some. I have a few conclusions.
The idea of resistance at the breaker connection to the busbar causing a lot of heat
is new to me. However these are likely to fail "safe" as an open circuit, in fact likely
all breakers are designed to fail that way.
I conclude its best not to put very large "continuous" load breakers on buses; move them to their own
boxes. Lots of small breakers in the middle will not contribute to contact heat, with far less current
through just as robust a contact, even with more, the heat of each contact diminishes as the SQUARE
of current. Or consider it as many contacts in parallel having much less resistance than just one.
Certainly badly unbalanced L1 and L2 is not good. Bruce RoeLeave a comment:
-
No, you are missing the point. You want to assert that the worst case without PV is a single 200 A load on the end of the busbar. Ok, now add PV to that specific case, and allow the load to increase to 250 A (which is possible now in a fault scenario, and no limit on the PV input). Don't you think that would be hotter? You'd have 200 A still flowing the length of the busbar to one slot above the PV, plus 50 A from the PV going to that load now. The finger from the bus that the breaker attaches to would be carrying all 250 A.
It would be 200A flowing 90% of the length (instead of 100%)
And 50A flowing on the remaining 10% (instead of 200A on that portion)
If there were a 250A breaker (there isn't) it'd be across multiple fingers.
I believe all the 100A or 200A breakers are across multiple fingers. So if there were larger ones, they would be too.
Leave a comment:
-
to L1 and L2, the power goes out to the pole transformer which as an autotransformer feeds back 200A 120V. With PV
supplying the load, I see on L1 100A from PV and 100A from main breaker (to PoCo trans) feeding load point,
200A from load return to PoCo trans, and in L2 100A from PV to main breaker (to PoCo trans). Bruce RoeLeave a comment:
-
Nope. Let's say L1 has 200 A of 120 V load circuits (10 x 20 A circuits, for example, not very different than what is the service panel of my old house), and a 100 A main breaker (we agree that it is typical for the sum of load breakers to exceed the main breaker). With a single source, we know that even in an overload condition, the 100 A main will trip.
Now let's add 100 A of PV to the opposite end of that bus because we think 120% is conservative and 200% sounds better. It would be *possible* for 200 A of load on L1 to be supplied (100 A from main, 100 A from PV) and no breakers tripped. All 200 A of that current would potentially travel to the transfomer through the neutral (which had been sized, like the service panel, only for 100 A service), where 100 A could then return to the inverter on L2. Yes, L2 loads would reduce the neutral current, but there is nothing that requires L1 and L2 loads to be balanced, or for L2 loads to even be present if the load center was poorly arranged.
Surprisingly all discussions related to the rule revolve around busbars without anyone ever bringing up problem of asymmetric load overloading neutral with people commonly upgrading their MSPs even though the service wires are often sized to support higher current such that only MSP gets replaced. Based on this discussion that is not really needed.Leave a comment:
-
Nope. Let's say L1 has 200 A of 120 V load circuits (10 x 20 A circuits, for example, not very different than what is the service panel of my old house), and a 100 A main breaker (we agree that it is typical for the sum of load breakers to exceed the main breaker). With a single source, we know that even in an overload condition, the 100 A main will trip.
Now let's add 100 A of PV to the opposite end of that bus because we think 120% is conservative and 200% sounds better. It would be *possible* for 200 A of load on L1 to be supplied (100 A from main, 100 A from PV) and no breakers tripped. All 200 A of that current would potentially travel to the transfomer through the neutral bus (which also has 100 A rating), neutral lug, neutral service feed and service drop (which have been sized, like the service panel, only for 100 A service), where 100 A could then return to the inverter on L2. Yes, L2 loads would reduce the neutral current, but there is nothing that requires L1 and L2 loads to be balanced, or for L2 loads to even be present if the load center was poorly arranged.Last edited by sensij; 09-28-2017, 02:30 AM.Leave a comment:
-
not really possible to sum up: say we put load 200A on L1 only and PV is capable of supplying that current - the grid neutral would provide 'return' path but then grid L2 would carry 200A back to PV inverter to close the circuit. If we put some load on L2 as well it would reduce current through neutral and L2 coming from the grid as inverter current can now travel back over shorter circuit. When L2 load reaches 200A as well neutral or L2 from the grid won't have any current flowing through them. Now if we continue to increase L2 load asymmetrically L2 current from the grid can reach 200A on its own (to the total of 400A through the L2 load) creating 200A neutral current from the grid. Then we can increase load on L1 from 200 to 400A at which point point PV and grid would be symmetrically supplying 200A each with neutral conducting 0 current. If in any of those cases asymmetrical load exceeds 200A the main breaker would trip. Have I covered this scenario as well?Leave a comment:
-
I haven't seen yet even 1 scenario where 120% rule would improve safety. My analysis is 'good enough' - it covers what is going on so no other complications would change the fact that current has to travel less distance along the bar with PV producing extra power. I guess, it just seems too counter intuitive to accept: extra source + extra power but less losses.Leave a comment:
-
It is applicable to the neutral discussion. It is possible for the utility current and the PV current to be summed on the neutral conductor, no fault required, just unbalanced loading.Leave a comment:
-
What we started with was code complaint MSP where all breakers are feeding correctly sized wires and the only change made was additional PV source on the busbar end opposite to the main breaker. It is still my opinion such addition would reduce heat load on the busbar during times PV produces power.Leave a comment:
-
What we started with was code complaint MSP where all breakers are feeding correctly sized wires and the only change made was additional PV source on the busbar end opposite to the main breaker. It is still my opinion such addition would reduce heat load on the busbar during times PV produces power.
Leave a comment:
-
please elaborate, I was under impression 120% rule is only intended to limit heat from the current flowing through the bus. It would be fairly far fetched to claim it is relevant to neutral conductor ampacity- why they didn't simply state that in neutral conductor requirements directly?
BTW, your example with singe 250A load is not very realistic unless someone deliberately installed 250A breaker/load on the 200A rated bus. If you meant possible short fault then it wouldn't limit itself to 250A and would trip one of the breakers.
In a fault scenario, you don't know what the fault current will be. That is why you don't protect 14 AWG with a 40 A breaker... logic that says "a short will trip it in any case" is terrible.Last edited by sensij; 09-27-2017, 11:39 PM.Leave a comment:
-
BTW, your example with singe 250A load is not very realistic unless someone deliberately installed 250A breaker/load on the 200A rated bus. If you meant possible short fault then it wouldn't limit itself to 250A and would trip one of the breakers. Multiple loads totaling to more than 200A don't present a problem as was shown above.
I think bcroe's comment is the closest to the reasoning- someone said 50% heat overload is acceptable, they took square root, got 1.22, rounded it down to 1.2 and 120% rule was born.
Last edited by max2k; 09-27-2017, 11:42 PM.Leave a comment:
-