    Originally posted by soamz
    Its 750 in between. Normally it wont use even 350W.
    yes, servers will run 24x7.
    And it will be connected to grid as well in case solar gets short.
    You would be a fool to go solar. I build Data centers and telephone switching offices for a living for the last 35 years. No company would ever think of going solar. By doing so you just opened yourself to unnecessary outages, and paying 5 to 10 more for electricity. No manager would ever think of doing something so stupid.

    All critical communications faculties use commercial power to run the equipment via UPS and battery power. When commercial power fails the batteries take over, the generators start up and take over the load and run until commercial power is restored. If designed properly, and not installed in earth quake zones or flood plains gives you 99.99% availability. No solar system can even come close to that reliability, and the solar option is a lot more expensive.

    A properly designed communication system will have a battery capacity of 2 to 12 hours for short duration outages and in the event both generators fail to start. A solar battery system needs a minimum 72 hour capacity for a non critical system like a house where being out of power for a week is no problem, otherwise 240 hours or 10 days for critical systems where power outages are unacceptable.

    Leave a comment:


  • SunEagle
    replied
    Originally posted by soamz
    Its 750 in between. Normally it wont use even 350W.
    yes, servers will run 24x7.
    And it will be connected to grid as well in case solar gets short.
    If the servers are connected to the grid then you just need to size a UPS system big enough to allow a generator to start up and then supply the power to the servers.

    Forget about going with a solar / battery system if you are worried about the cost or reliability.

    When it comes to large continuous loads running off batteries, you are going to need lots of money.
    Last edited by SunEagle; 11-06-2015, 04:08 PM. Reason: spelling

    Leave a comment:


  • lkruper
    replied
    Originally posted by JFinch57
    So it will be grid tied and the power requirement is probably 1/4 of what was calculated above. Your switches and routers should be minimal, so the continuous rating would be about 2KW, right? That changes everything!
    Yes, instead of 1/2 million with labor it will only be $125,000 to implement. Then the OP can spend 10X the utility price for electricity forever. Why is this good?

    Leave a comment:


  • JFinch57
    replied
    Originally posted by soamz
    Its 750 in between. Normally it wont use even 350W.
    yes, servers will run 24x7.
    And it will be connected to grid as well in case solar gets short.
    So it will be grid tied and the power requirement is probably 1/4 of what was calculated above. Your switches and routers should be minimal, so the continuous rating would be about 2KW, right? That changes everything!

    Leave a comment:


  • soamz
    replied
    Originally posted by JFinch57
    You didn't really give clear inputs to the equation. Is it 750W X 2 inputs (1500W) or 750W between the 2? What is the power of the other equipment? Also, didn't state that the servers are required to run 24/7 with high availability, thus the need for a generator when the batteries run out, or can you afford down time since you have an alternate site that can assume the data flow. The bottom line is that off grid with batteries is very expensive to build and maintain.
    Its 750 in between. Normally it wont use even 350W.
    yes, servers will run 24x7.
    And it will be connected to grid as well in case solar gets short.

    Leave a comment:


  • JFinch57
    replied
    Originally posted by soamz
    Now Im more confused with the confusing replies
    You didn't really give clear inputs to the equation. Is it 750W X 2 inputs (1500W) or 750W between the 2? What is the power of the other equipment? Also, didn't state that the servers are required to run 24/7 with high availability, thus the need for a generator when the batteries run out, or can you afford down time since you have an alternate site that can assume the data flow. The bottom line is that off grid with batteries is very expensive to build and maintain.

    Leave a comment:


  • soamz
    replied
    Now Im more confused with the confusing replies

    Leave a comment:


  • Sunking
    replied
    You are not going to like the answers. but who cares right? It will never happen

    OK just based on what little information you have provided:
    • Panel Wattage = 34,000 watts. Roughly $50,000 USD, higher outside USA
    • 8 x 80 amp MPPT Controllers. Unit Cost $700 each x 8 units = $5600 USD higher outside USA
    • Batteries = 675 Kwh capacity. 48 volts @ 14,000 AH. That is a battery that weighs 40,000 pounds/ 18150 Kg and cost you $140,000 every few years. You will need a dedicated large room with enforced floor to hold the weight with air conditioning year round. The room and mechanical systems wil cost more than the batteries. Who cares right?
    • 50 Kw Diesel Generator, 500 gallon Diesel tank, 48 volt 800 amp Rectifier, concrete pad another $40,000 out of your pocket.
    • Misc hardware Inverters, wiring, shipping, and all the other crap to make it work another $40,000 USD


    When said and done just under $300,000 in equipment cost alone. Does not include permits, engineering, and labor. So I can do this Turn-Key for you for $500,000 if you are in the USA. Otherwise you are on your own. Just give me you Fax Number and I will send you a Contract. Sigh and return it with $50,000 check and I can get started. Be sure to have your lawyers look over the contract. I can also build your battery room for an additional $200,000 but there is a catch as it will require commercial AC power for the air conditioning.

    So are you ready to get into dirt cheap free power? Just sign the contract. When said and done by going solar you have elected to pay 5 to 10 times more for electricity for the rest of you rlife vs buying it from the POCO. Really a great strategy for any business looking to throw money away and go bankrupt. You will be out of biz before you know it.

    Leave a comment:


  • Yaryman
    replied
    Not the expert many here are, but one BIG problem with running the servers with solar only is that it's not sunny every day and solar is pretty
    useless at night. So to implement your plan you would need a very reliable, VERY expensive battery system.

    Better to be grid tied with solar and let the fine folks at your regulated power monopoly provide energy when you can't.

    Leave a comment:


  • How much Solar Power we would need for 5 Dell Servers to run 24x7 ?

    Hi, my server room has around 5 Dell Rack servers and 5 switches, routers.

    How much solar power do I need to run them for 24 hours a day ?
    Means, completely off grid and all the power being used from the solar power generated energy only ?

    Dell Servers Power Rating are 750w, 2 power plugs for redundancy.