    Originally posted by inetdog
    Sounds good to me. Just use the right type of wire (PV wire is the most likely for sun and water exposure and even without conduit, but USE-2 will also work without conduit and may be more available locally. If you use conduit, then THWN-2 is a good type. XHWW-2 may allow a higher ampacity on the roof if you are under the 2014 NEC.) and run it where it is protected from physical damage.
    Problem hopefully handled. I am paying the original installer to come back and add the last panel. He knows what wire to use to jumper cable this 9th panel into the 8-string.

    He offered to do it in combination with installing a new 50amp breaker in my service panel and a NEMA 14-50 outlet in my garage.....so I can plug in my new guess-what!

    Leave a comment:


  • bcroe
    replied
    Originally posted by Naptown
    Wire type depends on the type of inverter used.
    If transformerless then PV wire must be used.
    USE2 is fine for an inverter with a transformer ( galvanic isolation.)
    What you use in conduit is up to the AHJ
    OH and while we are on the subject of transformerless inverters if you have more than 2 steings feeding an input you need a combiner with fuses on both positive and negative legs of the source circuit.
    The Fronius has the negative PV leg grounded (through a ground fault fuse). It has provisions for up
    to 6 string inputs with individual positive leg fuses, if running all string wires to the inverter. It also
    has a DC disconnect switch for both legs. Bruce Roe

    Leave a comment:


  • Naptown
    replied
    Originally posted by inetdog
    Sounds good to me. Just use the right type of wire (PV wire is the most likely for sun and water exposure and even without conduit, but USE-2 will also work without conduit and may be more available locally. If you use conduit, then THWN-2 is a good type. XHWW-2 may allow a higher ampacity on the roof if you are under the 2014 NEC.) and run it where it is protected from physical damage.
    Wire type depends on the type of inverter used.
    If transformerless then PV wire must be used.
    USE2 is fine for an inverter with a transformer ( galvanic isolation.)
    What you use in conduit is up to the AHJ
    OH and while we are on the subject of transformerless inverters if you have more than 2 steings feeding an input you need a combiner with fuses on both positive and negative legs of the source circuit.

    Leave a comment:


  • inetdog
    replied
    Originally posted by MARKSDCA
    Shouldn't this be as easy (yes I know nothing is as easy as it sounds) as disconnecting a pair of connected panels anywhere in the series of 8 from each other and running jumper cables to add in the 9th panel in between them? This 9th panel would be on the same roof plane/angle/direction, 25 feet away from the array of 8, and there is no shading whatsoever on this roof.
    Sounds good to me. Just use the right type of wire (PV wire is the most likely for sun and water exposure and even without conduit, but USE-2 will also work without conduit and may be more available locally. If you use conduit, then THWN-2 is a good type. XHWW-2 may allow a higher ampacity on the roof if you are under the 2014 NEC.) and run it where it is protected from physical damage.
    Last edited by inetdog; 09-28-2015, 08:47 PM.

    Leave a comment:


  • MARKSDCA
    replied
    Originally posted by solarix
    OP needs to figure out how exactly the array was wired and add the additional panel onto the string of 8.
    Shouldn't this be as easy (yes I know nothing is as easy as it sounds) as disconnecting a pair of connected panels anywhere in the series of 8 from each other and running jumper cables to add in the 9th panel in between them? This 9th panel would be on the same roof plane/angle/direction, 25 feet away from the array of 8, and there is no shading whatsoever on this roof.

    Leave a comment:


  • solarix
    replied
    OP needs to figure out how exactly the array was wired and add the additional panel onto the string of 8.

    Leave a comment:


  • MARKSDCA
    replied
    Originally posted by inetdog
    Right now the 9-9-8 configuration will cause the MPPT tracker algorithm in the inverter to either:
    1. operate all three strings at the voltage appropriate for an 8 panel string, giving you in effect only 24 panels (8-8-8).
    2. operate all three strings at the voltage appropriate to an 9 panel string, with the 8 panel string not contributing at all. Effectively only 18 panels (9-9-0)
    3. somewhere in between in voltage so that neither the 8 nor the 9 panel string are putting out their optimum output.

    In any case, the result will not be noticeably better than 8-8-8.

    If you went to 10-9-8, the results would be even worse, and you might get only the power appropriate to a total of 10 panels or 18 panels.
    According to Fronius Tech Support your first theory is correct. My system is not recognizing the 9th panel in those 2 strings.

    So now the question is: Do I add my last spare panel for 9-9-9 or do I remove 2 panels and sell all 3 to somebody that can use 3 matched Solarworld 270 panels for some kind of project? Or do I just leave it as is. It kills me that if I add just one more panel I will get the benefit of adding 3 more...it will drive me nuts if I don't do it.

    Fronius said having 7290 watts of panels on a 6000 watt inverter is no problem....so no issue adding the last panel for the 9-9-9 config.

    Leave a comment:


  • inetdog
    replied
    Originally posted by MARKSDCA
    Hmmm...so maybe I should be adding that spare panel NOW to the string of 8 so I have 9-9-9? How much am I "hurting" myself having 9-9-8 presently? It sounds like I could be making even more and increase the yield of the whole system.

    I'm currently making MORE than twice as much energy as I am consuming so no urgency here. I want to buy an EV but I should still be making more that I need after that.
    Right now the 9-9-8 configuration will cause the MPPT tracker algorithm in the inverter to either:
    1. operate all three strings at the voltage appropriate for an 8 panel string, giving you in effect only 24 panels (8-8-8).
    2. operate all three strings at the voltage appropriate to an 9 panel string, with the 8 panel string not contributing at all. Effectively only 18 panels (9-9-0)
    3. somewhere in between in voltage so that neither the 8 nor the 9 panel string are putting out their optimum output.

    In any case, the result will not be noticeably better than 8-8-8.

    If you went to 10-9-8, the results would be even worse, and you might get only the power appropriate to a total of 10 panels or 18 panels.

    Leave a comment:


  • bcroe
    replied
    Originally posted by MARKSDCA
    Hmmm...so maybe I should be adding that spare panel NOW to the string of 8 so I have 9-9-9? How much am I "hurting" myself having 9-9-8 presently? It sounds like I could be making even more and increase the yield of the whole system.

    I'm currently making MORE than twice as much energy as I am consuming so no urgency here. I want to buy an EV but I should still be making more that I need after that.
    I am guessing shading isn't generally a problem with these panels. If you put a clamp on ammeter on
    each of the 3 strings in good sun, you would probably find the 9s are putting out WAY MORE current than
    the 8 panel string. 3 strings of 9 would work well if the addition didn't see different shade than the rest
    of that string.

    I would not be surprised that 3 strings of 8 would put out more than 9-9-8, because 24 panels would be
    working hard instead of 18. Or, the mppt may be dragging the voltage down to that of 3 strings of 8.

    With temperatures hitting 25 deg F below zero here, I would not wire 13
    panels of 60 cels in series, but your situation may be different. Bruce Roe

    Leave a comment:


  • MARKSDCA
    replied
    Originally posted by ButchDeal
    parallel strings need to be equal. You are hurting yourself with the 9-9-8 now, a 10-9-8 would be little more effective than an 8-8-8
    Note: we are talking about the electrical wiring not the physical layout of the modules.
    Hmmm...so maybe I should be adding that spare panel NOW to the string of 8 so I have 9-9-9? How much am I "hurting" myself having 9-9-8 presently? It sounds like I could be making even more and increase the yield of the whole system.

    I'm currently making MORE than twice as much energy as I am consuming so no urgency here. I want to buy an EV but I should still be making more that I need after that.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by solarix
    Yes, but they are not independent. Those terminals are where the strings get paralleled (or combined) and should have fuses for each string.
    If it makes you feel any better, there are no current inverters (not counting the kind with micro inverters or optimizers) that have three independent inputs (each with its own MPP tracking). ABB and SMA brands have dual MPPT inputs though.
    The new Fronius Symo systems do have dual MPPT as well.



    Though, it doesn't sound like the OP has one here.

    Leave a comment:


  • ButchDeal
    replied
    Originally posted by MARKSDCA
    So would 10-9-8 be counter productive? Is 9-9-9 the only way to go? Is this as simple as running a wire from the new panel to the first panel in the string of 8?? All of the panels on my roof are on the same plane and completely shadeless so except for before 8am or after 5pm (trees near the horizon) they are in uniform full sun.
    parallel strings need to be equal. You are hurting yourself with the 9-9-8 now, a 10-9-8 would be little more effective than an 8-8-8
    Note: we are talking about the electrical wiring not the physical layout of the modules.

    Leave a comment:


  • MARKSDCA
    replied
    So would 10-9-8 be counter productive? Is 9-9-9 the only way to go? Is this as simple as running a wire from the new panel to the first panel in the string of 8?? All of the panels on my roof are on the same plane and completely shadeless so except for before 8am or after 5pm (trees near the horizon) they are in uniform full sun.

    Leave a comment:


  • solarix
    replied
    Yes, but they are not independent. Those terminals are where the strings get paralleled (or combined) and should have fuses for each string.
    If it makes you feel any better, there are no current inverters (not counting the kind with micro inverters or optimizers) that have three independent inputs (each with its own MPP tracking). ABB and SMA brands have dual MPPT inputs though.

    Leave a comment:


  • MARKSDCA
    replied
    Originally posted by solarix
    Fronius inverters just have a single input so all the strings are wired in parallel and ought to be the same length. Interesting that the installed design is one panel short on one of the strings. The added panel should really be added to the string of 8 so that they will all be the same. I also wonder why they did not originally wire it as 2 strings of 13? You could go find the "Fronius online string sizer" and play with different combinations.