  • JFinch57
    replied
    Where do you get "Where do you get "THWN-2 (90 °C) #12AWG conductor is rated for 30 A"? I'd say 20A. Also, do you need a PE to sign off on your roof load certification? I know at PE that did 2 of mine in NJ, Harry Braich, and he didn't charge an arm and a leg!

    Leave a comment:


  • foo1bar
    replied
    Originally posted by GreenTeeCrazy
    Sorry i cant edit post!!!!!

    more pics
    these 2 are part of a doc file named "Overview Plan"


    I think these help a LOT for someone looking at the plans - makes it much easier to understand them.

    Have you figured out how you're going to get the wires from the western roof section to the eastern roof section?

    Leave a comment:


  • foo1bar
    replied
    Originally posted by GreenTeeCrazy
    Steve, where is irreversable? i cant find it!!!!
    Your one-line. by the Jbox.

    Leave a comment:


  • foo1bar
    replied
    Originally posted by GreenTeeCrazy

    ??? what do you think?
    Have you mapped out the rafter relationship to the array that it'll actually be as you have it laid out in the image?

    I didn't map mine out completely until after I had applied for the permit. (I figured out how many I'd likely need - but I didn't do exact placement until I was on the roof)

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by foo1bar
    How many ways can you spell diagram?

    The filename you made an attachment has it misspelled in the filename.
    AND at the bottom of the jpg it is misspelled.
    I think i am rushing too much to get this permit done, I'll til tomorrow.... to fix all the bugs

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by sdold
    You need to fix the stuff like "IRRIVERSIBLE", too.
    Steve, where is irreversable? i cant find it!!!!

    Leave a comment:


  • foo1bar
    replied
    Originally posted by GreenTeeCrazy
    here is an update to 1 line diagram, i hope this will make more sense, watching Amy Schumer late at night and drawing is not fun
    How many ways can you spell diagram?

    The filename you made an attachment has it misspelled in the filename.
    AND at the bottom of the jpg it is misspelled.

    Leave a comment:


  • GreenTeeCrazy
    replied
    Ok, Rafters @ 16", By providing enough support to all panels without exceeding the maximum spacing limits and observing Zone 2 and 3.

    my best configuration:

    rafter

    1.......2......3......4......5......6......7...... 8
    4-----2-----4-----2-----2----4-----2-----4

    rail 1@ top: 1,3,6,8
    rail2: 1,3,5,7
    rail3: 2,4,6,8
    rail4: 1,3,5,7
    rail5: 2,4,6,8
    rail6: 1,3,6,8

    ??? what do you think?
    Attached Files

    Leave a comment:


  • sdold
    replied
    You need to fix the stuff like "IRRIVERSIBLE", too.

    Leave a comment:


  • sdold
    replied
    Instead of writing "1-17 MODULES", which indicates you'll have some unknown number of modules, I'd write "MODULES #10-18". As an engineer who has to make a lot of drawings, things like that bug me.

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by foo1bar
    4th page is attachment points - but the rafters on there aren't 16" (or the panels aren't typical 1 meter wide)

    I agree that not attaching them all to one set of rafters would be better.
    But you don't want to exceed the maximum cantilever or maximum span from ironridge's documentation either.
    BTW, if you do have access to the bottom of the roof (ie. can see where you drilled through when (not if) you miss the rafter, it'll make your life a lot easier.
    FWIW, I'd probably go with even less cantilever at the corners where I think you're most likely to get more uplift from wind.

    I think with 3 of 1m panels you'll span over 8 of 16" OC rafters. (probably 9 because you'll have extra length of rails that aren't covered by panels.)
    I think in the writeup you have 4 attachment points for each rail, so you'll be doing every-other rafter, and 4' between them for one spot.
    If it's 8 rafters, I'd try have the bottom rail be on rafters 1,3,5,7 the top rail on rafters 2,4,6,8 - distributes the load a little. more across the structure.
    If it's 9 rafters, I might do 1,3,5,8 and 2,4,6,9.
    I think you might even be able to do 3 points per rail - but I didn't do any calculations or run it thorugh ironridge's calculator, so you'd need to do that. (I think 5.5' apart would meet the ironridge recommendation. Or 4' apart with 1' cantilever on each side.) Adding a 4th is going to be more work - slightly more risk of leaks. But definitely will be stronger tie to the bldg.

    I saw on the plans "irreversible splice" for the ground in the Jbox on the roof.
    Is that necessary?
    I don't know enphase installation requirements - so I'm asking the question.
    I'll add another PV page to show the the L-Foot flash connection points, btw you do have very valid point.

    The rafters are 16" spacing,

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by Naptown
    One line is confusing hard to tell what wires are in same conduit
    From junction on roof to combiner panel should be 6 #10 and a # 6
    ( neutral and ground can be combined as neutral is communications only and ground is not a current carrying conductor.
    The attachment plan 2nd page shows not nearly enough attachment points.
    Also when laying them out don't attach all the rails to one set of rafters. Alternate attachments to spread load out as much as possible using all rafters below the array.
    Looks like you are in wind zone 2 on sides and 3 lower corners. These areas will need more attachment points.
    Thank you Naptown,

    here is an update to 1 line diagram, i hope this will make more sense, watching Amy Schumer late at night and drawing is not fun
    Attached Files
    Last edited by inetdog; 08-26-2015, 01:34 PM. Reason: fixed quote tag

    Leave a comment:


  • foo1bar
    replied
    Originally posted by Naptown
    The attachment plan 2nd page shows not nearly enough attachment points.
    Also when laying them out don't attach all the rails to one set of rafters.
    .
    4th page is attachment points - but the rafters on there aren't 16" (or the panels aren't typical 1 meter wide)

    I agree that not attaching them all to one set of rafters would be better.
    But you don't want to exceed the maximum cantilever or maximum span from ironridge's documentation either.
    BTW, if you do have access to the bottom of the roof (ie. can see where you drilled through when (not if) you miss the rafter, it'll make your life a lot easier.
    FWIW, I'd probably go with even less cantilever at the corners where I think you're most likely to get more uplift from wind.

    I think with 3 of 1m panels you'll span over 8 of 16" OC rafters. (probably 9 because you'll have extra length of rails that aren't covered by panels.)
    I think in the writeup you have 4 attachment points for each rail, so you'll be doing every-other rafter, and 4' between them for one spot.
    If it's 8 rafters, I'd try have the bottom rail be on rafters 1,3,5,7 the top rail on rafters 2,4,6,8 - distributes the load a little. more across the structure.
    If it's 9 rafters, I might do 1,3,5,8 and 2,4,6,9.
    I think you might even be able to do 3 points per rail - but I didn't do any calculations or run it thorugh ironridge's calculator, so you'd need to do that. (I think 5.5' apart would meet the ironridge recommendation. Or 4' apart with 1' cantilever on each side.) Adding a 4th is going to be more work - slightly more risk of leaks. But definitely will be stronger tie to the bldg.

    I saw on the plans "irreversible splice" for the ground in the Jbox on the roof.
    Is that necessary?
    I don't know enphase installation requirements - so I'm asking the question.

    Leave a comment:


  • Naptown
    replied
    Originally posted by GreenTeeCrazy
    One more time i need any suggestions or modifications to my drawings.

    here are the updated files, they seem more professional than kindergarten ones.










    One line is confusing hard to tell what wires are in same conduit
    From junction on roof to combiner panel should be 6 #10 and a # 6
    ( neutral and ground can be combined as neutral is communications only and ground is not a current carrying conductor.
    The attachment plan 2nd page shows not nearly enough attachment points.
    Also when laying them out don't attach all the rails to one set of rafters. Alternate attachments to spread load out as much as possible using all rafters below the array.
    Looks like you are in wind zone 2 on sides and 3 lower corners. These areas will need more attachment points.

    Leave a comment:


  • GreenTeeCrazy
    replied
    Sorry i cant edit post!!!!!

    more pics
    these 2 are part of a doc file named "Overview Plan"


    Leave a comment: