X
 
  • Time
  • Show
Clear All
new posts

  • GreenTeeCrazy
    replied
    Originally posted by tehan
    Code is always subject to interpretation and the only thing that matters at this point is what will get you past inspection. Enphase's position is you don't need that #6 grounding conductor at all because all the grounding required for an ungrounded PV system is provided by the grounding conductor in the Engage cable (assuming you use a suitable washer to bond the M250 to the rail). Some inspectors don't agree.
    Correct about the M250
    #6 is for the rails and the Solar modules ground.
    is it ok to have the ground wire be installed as a "n" shape? start from 1st rail go up to the 6th rail then connect back at the 1st rail again?

    Leave a comment:


  • tehan
    replied
    Originally posted by GreenTeeCrazy
    Enphase M250 are grounded using engage cable.
    So i guess it ok to run the cable from point A, run it around the circuit and return back to point A?
    Code is always subject to interpretation and the only thing that matters at this point is what will get you past inspection. Enphase's position is you don't need that #6 grounding conductor at all because all the grounding required for an ungrounded PV system is provided by the grounding conductor in the Engage cable (assuming you use a suitable washer to bond the M250 to the rail). Some inspectors don't agree.

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by JFinch57
    I like these Enphase brackets, but for some reason you have to elongate the holes to fit a standard square box. Also, the M250s have integral ground that carries through to the racking if properly bonded by the racking manufacturer's instructions. There should be no additional ground wires required. See http://www.ecodirect.com/ProductDeta...FYQ_aQodaE0IbA
    THAT'S IT!!!!

    Exactly what i am looking for.

    Leave a comment:


  • JFinch57
    replied
    Originally posted by GreenTeeCrazy
    Connecting the Aluminum J-BOX to the Al rail:

    Any adapter or plate should i use or can i use a zinc plated self-tapping screws from inside J-Box to the rail?

    Running the #6 ground wire:

    As you can see in my diagram, I run the ground wire from top to bottom in circuit 2, then run it to Circuit 1 going up to the top rail then back to the J-Box by the lower left end. in the shape of "nj"

    Is it ok by code to backloop the ground wire?
    I like these Enphase brackets, but for some reason you have to elongate the holes to fit a standard square box. Also, the M250s have integral ground that carries through to the racking if properly bonded by the racking manufacturer's instructions. There should be no additional ground wires required. See http://www.ecodirect.com/ProductDeta...FYQ_aQodaE0IbA

    Leave a comment:


  • GreenTeeCrazy
    replied
    All i could find at HD was the Aluminum 1 and 2 gang box
    NEC 2011.
    Enphase M250 are grounded using engage cable.
    So i guess it ok to run the cable from point A, run it around the circuit and return back to point A?

    My installation setup:

    Connect Engage cable to J-Box 2 in Circuit 2 using liquid tight adapter.
    From J-Box 2, run #10 inside Ultratite conduit connect to J-Box 2 using 1" liquidtight adapter.
    using large stapler to hook the conduit to the 3ft siding (valley), If the bend is too great then i'll have to use 1 of those 90 degree adapter.
    Tie the conduit to the rail using Stainless steel or nylon zipties to keep the conduit from touching the roof every 3 feet. no more than a ft away from J-Boxes

    and do the same again on Circuit 1 to the AC Combiner.

    The whole wiring is done outside the house.

    Attached Files

    Leave a comment:


  • foo1bar
    replied
    Originally posted by GreenTeeCrazy
    I
    running the cable from Ciruit 2 to Circuit 1 to MNPV6 using 1" Utlratite NM conduit. After inspection is passed ( permit 1st lol) I am going to spray paint it to match the siding of the house. I'll discuss that with the inspector 1st.
    How are you supporting it as it goes across the roof, then up the wall. (You won't want it on on the roof - you probably want it 4" off the roof because of temp de-rating)
    How are you getting it around the edge of the roof at the top of the wall?

    Are you completely exterior to the structure with all your wiring? (If you were doing a regular string inverter, you'd need the wires inside the structure inside metallic conduit I think... With enphase microinverters, I'm not sure how those rules apply to them) But I think you're completely outside - so that shouldn't be a problem.

    With flexible conduit you will need to make sure that you're not making too many bends because of it sagging between support points.

    Leave a comment:


  • Naptown
    replied
    All hardware should be stainless steel
    What NEC code cycle are you on?
    You may be able to just ground each rail and bond the inverters to the rail with web clips. Same with modules.
    Most racking now a days allows this.

    Leave a comment:


  • GreenTeeCrazy
    replied
    Connecting the Aluminum J-BOX to the Al rail:

    Any adapter or plate should i use or can i use a zinc plated self-tapping screws from inside J-Box to the rail?

    Running the #6 ground wire:

    As you can see in my diagram, I run the ground wire from top to bottom in circuit 2, then run it to Circuit 1 going up to the top rail then back to the J-Box by the lower left end. in the shape of "nj"

    Is it ok by code to backloop the ground wire?

    Leave a comment:


  • sdold
    replied
    Originally posted by GreenTeeCrazy
    Irreversible is/was removed
    I just meant that you need to check your spelling, you had two wrong letters in there. Clean this stuff up or they'll think you are working for Substandard Construction. heh heh

    Leave a comment:


  • sensij
    replied
    2011 NEC Table 310.15 (b)(16)

    Leave a comment:


  • JFinch57
    replied
    Originally posted by sensij
    The way in which the ampacity adjustments and corrections was done is sort of logically backwards... the conductor rating should be adjusted down and checked against the rated ampacity of the circuit, not the circuit ampacity adjusted up. 12 AWG is OK for the 9 panel strings.

    90 deg 12 AWG base ampacity = 30 A
    adjustment for conduit fill = 30 * 0.8 = 24 A
    correction for temperature = 24 * 0.71 = 17 A

    17 A > circuit rating of 11.25 A - OK
    17 A > 15 A breaker - OK
    25 A terminal rating for 12 AWG > circuit rating of 11.25 A - OK
    15 A breaker <= 20 A for 12 AWG - OK
    What chart are you using for 12 AWG? This says 20A. http://www.cerrowire.com/ampacity-charts

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by GreenTeeCrazy
    Here are the .doc files for the proposal work:
    Roof pemmit
    Attached Files

    Leave a comment:


  • GreenTeeCrazy
    replied
    Originally posted by sensij
    The way in which the ampacity adjustments and corrections was done is sort of logically backwards... the conductor rating should be adjusted down and checked against the rated ampacity of the circuit, not the circuit ampacity adjusted up. 12 AWG is OK for the 9 panel strings.

    90 deg 12 AWG base ampacity = 30 A
    adjustment for conduit fill = 30 * 0.8 = 24 A
    correction for temperature = 24 * 0.71 = 17 A

    17 A > circuit rating of 11.25 A - OK
    17 A > 15 A breaker - OK
    25 A terminal rating for 12 AWG > circuit rating of 11.25 A - OK
    15 A breaker <= 20 A for 12 AWG - OK
    I agree with you, I am trying to get the lowest drop/rise %

    Leave a comment:


  • GreenTeeCrazy
    replied
    I would like to thank everyone who for taking their time to answer and guide me in my quest.

    Irreversible is/was removed

    If you mean the Enphase engage cable, I am running it as "5" shape. from top right panel to the the lower bottom left next JBOX on both circuits.

    running the cable from Ciruit 2 to Circuit 1 to MNPV6 using 1" Utlratite NM conduit. After inspection is passed ( permit 1st lol) I am going to spray paint it to match the siding of the house. I'll discuss that with the inspector 1st.

    Also i do have to access to the attic, so i installed over the weekend a blocking system to support more weight on my aging roof, In the worst case scenario that if i missed a rafter, i can always install 2x6 joint under the roof membrane .

    @JFinch57, About the PE, I am going to wait and see if the inspector request the report, But thank you for the info. Did you do your own installation?

    Leave a comment:


  • sensij
    replied
    The way in which the ampacity adjustments and corrections was done is sort of logically backwards... the conductor rating should be adjusted down and checked against the rated ampacity of the circuit, not the circuit ampacity adjusted up. 12 AWG is OK for the 9 panel strings.

    90 deg 12 AWG base ampacity = 30 A
    adjustment for conduit fill = 30 * 0.8 = 24 A
    correction for temperature = 24 * 0.71 = 17 A

    17 A > circuit rating of 11.25 A - OK
    17 A > 15 A breaker - OK
    25 A terminal rating for 12 AWG > circuit rating of 11.25 A - OK
    15 A breaker <= 20 A for 12 AWG - OK

    Leave a comment:

Working...