  • SunEagle
    replied
    Originally posted by bcroe
    I assume none of that applies to ground mount PV? Bruce Roe
    I'm pretty sure the code applies to buildings that may require first responders to open up a hole to vent and need access to the peak of the roof.

    I have to read the NEC again if there is any specifics for ground mount pv systems. Certainly there should be some type of disconnect somewhere in the circuit.

    For a ground mount system they may just let it burn or bulldoze it under to keep the fire from spreading.

    Leave a comment:


  • bcroe
    replied
    Originally posted by SunEagle
    I just read an article where Louisiana has recently adopted the 2014 NEC article 690 concerning fire set backs.

    It also has a requirement concerning a manual disconnect within 5 feet of the array to protect First responders from getting shocked. So interesting changes for solar not only in CA.
    I assume none of that applies to ground mount PV? Bruce Roe

    Leave a comment:


  • Willaby
    replied
    Originally posted by daev
    I just wanted to post an update. My installer was able to get a variance to the 3' peak setback rule based on alternate venting availability. Because there are fire venting possibilities on the roof that are equally viable to the roof face with solar panels, the exemption was issued. So the setback rule is definitely not written in stone.
    Same here. Variance was not a problem, right up to the ridge line. City Fire Chief's make the policy. Factors are: 1. panels can only be installed on one side of the ridge and 2. what's under the roof (living area or attic). For this I don't quite understand, but my panels are installed over the vaulted living area and the access is on the other side, over an attic area.

    Getting the variance opened up a whole row of panel availability, 7 panels of prime production area.

    Leave a comment:


  • SunEagle
    replied
    Originally posted by J.P.M.
    Thank you for the information and update. Seems good to have confirmation of what is possible.
    I just read an article where Louisiana has recently adopted the 2014 NEC article 690 concerning fire set backs.

    It also has a requirement concerning a manual disconnect within 5 feet of the array to protect First responders from getting shocked.

    So interesting changes for solar not only in CA.

    Leave a comment:


  • J.P.M.
    replied
    Originally posted by daev
    I just wanted to post an update. My installer was able to get a variance to the 3' peak setback rule based on alternate venting availability. Because there are fire venting possibilities on the roof that are equally viable to the roof face with solar panels, the exemption was issued. So the setback rule is definitely not written in stone.
    Thank you for the information and update. Seems good to have confirmation of what is possible.

    Leave a comment:


  • daev
    replied
    I just wanted to post an update. My installer was able to get a variance to the 3' peak setback rule based on alternate venting availability. Because there are fire venting possibilities on the roof that are equally viable to the roof face with solar panels, the exemption was issued. So the setback rule is definitely not written in stone.

    Leave a comment:


  • J.P.M.
    replied
    I believe it's local fire authorities rather than Calfire. I was perhaps a bit parochial as they are the folks in my neighborhood.

    On the setbacks: point is, there is the possibility of an exception being granted as referenced in the statute. It may not apply in all or even a few cases, but the case for exemptions does exist in statute. the ridge setback at least, is therefore, not an absolute requirement.

    Leave a comment:


  • Samsolar
    replied
    Google "Pitched Roof Array Layout for Fire Code Compliance " for a good article that explains setback options.

    Leave a comment:


  • inetdog
    replied
    Originally posted by daev
    Thanks. I did read the thorough analyses by Overthesun in that thread and others.

    The installer made it seem like exceptions get granted all the time, so I wanted to see if it was really common. It doesn't seem so, but it's still possible as long as there's alternate ventilation.
    There is probably a lot more variation of policy among local FDs than with Cal Fire. Although the local management within Cal Fire could still enforce more or less strictly.
    Or are you just using Cal Fire to refer to all FDs in California?

    Leave a comment:


  • daev
    replied
    Originally posted by J.P.M.
    See Title 24, Part 9, chap. 6 , Sec. 605.11. Set back requirements start at Sec. 605.11.3. See exceptions listed there. Then go to bldg. dept. with your hat in your hand. There seems to be an exception provided the fire marshal signs off on it.

    Complements of Overthesun,02/28/2014.
    Thanks. I did read the thorough analyses by Overthesun in that thread and others.

    The installer made it seem like exceptions get granted all the time, so I wanted to see if it was really common. It doesn't seem so, but it's still possible as long as there's alternate ventilation.

    Leave a comment:


  • foo1bar
    replied
    Originally posted by daev
    That's good to know. From your previous posts it seems like you may have done your own installation?

    I wonder how the process would be different if working with an installer. I assume it's something they'd take care of just like pulling permits.
    I did my own install.

    I would expect it to be similar with an installer - just that they would do it.
    IMO an installer is less likely to want to bother with it though.

    Leave a comment:


  • J.P.M.
    replied
    Originally posted by daev
    That's good to know. From your previous posts it seems like you may have done your own installation?

    I wonder how the process would be different if working with an installer. I assume it's something they'd take care of just like pulling permits.
    See Title 24, Part 9, chap. 6 , Sec. 605.11. Set back requirements start at Sec. 605.11.3. See exceptions listed there. Then go to bldg. dept. with your hat in your hand. There seems to be an exception provided the fire marshal signs off on it.

    Complements of Overthesun,02/28/2014.

    Leave a comment:


  • daev
    replied
    Originally posted by foo1bar
    I asked the building dept if it was possible.
    They told me I would need to get it signed off by the fire dept.
    I went over there, setup an appointment with their guy for a few days later.
    I showed them my planned roof layout, and they asked me a few questions (like where the kitchen is)
    The two firemen discussed some things as they were looking - I think one comment from one to the other was "Yeah, we could hand carry a ladder around to here [north side of house] and get up that way."
    That's good to know. From your previous posts it seems like you may have done your own installation?

    I wonder how the process would be different if working with an installer. I assume it's something they'd take care of just like pulling permits.

    Leave a comment:


  • foo1bar
    replied
    Originally posted by solarix
    This is good to know. The 3' rule just went into effect in some AHJ's around here. Can you tell me how exactly you go about getting a variance? Is it from the fire dept or the building dept?
    I asked the building dept if it was possible.
    They told me I would need to get it signed off by the fire dept.
    I went over there, setup an appointment with their guy for a few days later.
    I showed them my planned roof layout, and they asked me a few questions (like where the kitchen is)
    The two firemen discussed some things as they were looking - I think one comment from one to the other was "Yeah, we could hand carry a ladder around to here [north side of house] and get up that way."

    Leave a comment:


  • solarix
    replied
    This is good to know. The 3' rule just went into effect in some AHJ's around here. Can you tell me how exactly you go about getting a variance? Is it from the fire dept or the building dept?

    Leave a comment: