New 11kW Ground Mount in N San Diego
Collapse
X
-
It also looks like the -2 series (NEMA 4 rated) of optimizers is being discontinued in favor of the -5 series with better NEMA 6 rating, which is consistent with what my installer told me about the availability of different optimizer sku's.Leave a comment:
-
You also have to figure in the circuit breaker size for the pv system will be larger for the 7.6kw inverter and may be too big for the Main Panel buss capacity. Going with that 6kw inverter may clip some of the panel generation but can be used on most house panels without needing to de-rate the main CB.Leave a comment:
-
I'm new here
Hi
I'm new here & want to learn about installing my own solar system
thanks for allLeave a comment:
-
Especially with a couple years of panel fouling / degradation, a 7.6 kW inverter on a 7.2 kW system is a probably not worth the extra cost. Lots more lessons to learn!Leave a comment:
-
Sensij
Our array is on 38* angle and azimuth 211* and we are in NH. I understand it's about perfect for production this time of year.
As I mentioned in my edited post, we are planning to build another house with a 6KW system in 2 years and I will swap inverters at that time..
Lesson learned.
Thanks
CarlLeave a comment:
-
Extrapolating performance in March to the rest of the year is faulty. For panels mounted close to latitude tilt, this is the best performing time of year, since the temps are cool and the angle of incidence is best. Summertime will probably produce more on a raw kWh basis since the days are longer, but if you are looking for peak kW, this is the time of year to see it.Leave a comment:
-
I too am working up the design for a 7.2 KW ground-mount array, and am comparing the advantages of a 24 panel LG300 array plus optimizers and a string inverter, with 24 LGA1C-B3 AC panels. My design site is about 140' from my service panel, so I tend to favor the AC panel approach with #6 AWG cables to the panel, to avoid long heavy DC cables. How far from your house is your ground site? Also, what mounting frame is being proposed by your installers? Since I am figuring on doing 80% DIY, I am basing my design on the Ironridge ground-mount system.
I have read this thread with interest as we just installed 24LG 300 panels, 24 SE 300 Optimizers, and the SE6000 Inverter system - vendor said it would handle the load but didn't say it would not convert it!
My understanding about DC overrating was incorrect, as the SE6000 inverter will accept up to 7500WDC, but MAX AC output for this unit is 6000W AC.
So we are loosing 4-5 KW a day or roughly 100KW month due to clipping. Now the interesting thing is every other SE Inverter than the SE6000 has a 10-15% over the rated AC output capability.
For instance the SE7600 max AC output is 8450 W AC and the SE11400 is max AC output is 12000 W AC - its like Solar Edge and the SE6000 was at the top of the design limit. So with your 7200 W output you will be fine with the SE7600 if you go that route.
By the way, I learned that the SE6000 when over current, it "shuts down" or limits the current input to the inverter keeping it at the max 6000 W AC output so as not to convert the excess to heat at the inverter, it lets the heat out at the panel level. In any case, as I have learned buyer beware!
I intend to build another house with 6KW system in the coming years, so will swap inverters at that time.
CarlLeave a comment:
-
Originally posted by PowayOne last thing to consider though is if you bring back DC then you will have to use metal conduit approx $1/ft and mark it every 10 feet i think. And this approach is not compatible with Micro inverters ... but does work with optimizers. Good luck
from each string may allow using the inverter internal combiner function, instead of a
separate combiner box. Bruce RoeLeave a comment:
-
I too am working up the design for a 7.2 KW ground-mount array, and am comparing the advantages of a 24 panel LG300 array plus optimizers and a string inverter, with 24 LGA1C-B3 AC panels. My design site is about 140' from my service panel, so I tend to favor the AC panel approach with #6 AWG cables to the panel, to avoid long heavy DC cables. How far from your house is your ground site? Also, what mounting frame is being proposed by your installers? Since I am figuring on doing 80% DIY, I am basing my design on the Ironridge ground-mount system.
The calculator I like the best
This free voltage drop calculator estimates the voltage drop of an electrical circuit based on the wire size, distance, and anticipated load current.
computes a 1.4% loss for #6 wire at 140ft
this drops to 0.9% loss for #4 wire (which is cheaper by the foot than #6 at both home depot and lowes now [$0.79/ft * 140 ft * 4 wires = $442 for AC from panel to main]
But what DanS26 said is correct. If you do this with DC (and have the inverter at the house) the voltage would be approx twice as high and with 4 wires could bring back two strings so (so 1/4th the curr in each of the 4 wires) bottom line is small #10 wire could be used
One last thing to consider though is if you bring back DC then you will have to use metal conduit approx $1/ft and mark it every 10 feet i think. And this approach is not compatible with Micro inverters ... but does work with optimizers
Good luckLeave a comment:
-
I too am working up the design for a 7.2 KW ground-mount array, and am comparing the advantages of a 24 panel LG300 array plus optimizers and a string inverter, with 24 LGA1C-B3 AC panels. My design site is about 140' from my service panel, so I tend to favor the AC panel approach with #6 AWG cables to the panel, to avoid long heavy DC cables. How far from your house is your ground site? Also, what mounting frame is being proposed by your installers? Since I am figuring on doing 80% DIY, I am basing my design on the Ironridge ground-mount system.
Do a little more homework on the design.Leave a comment:
-
How far is your array from your house?
Looking comments on the following configurations... And PM of recommended installers (thejq any recommendations?)
Ground Mount. Perfect conditions (point south or slightly west... any elevation... no obstructions)
11.95 kW DC
28x SunPower 427W Panels
Solar Edge P400 Optimizers
SE11400 inverter (is this to small for the 11.95 DC if so could drop to 26 panels 11.1KW?)
10.8 KW DC
36x LG 300W Panels
Solar Edge P300 Optimizers (or should I still use P400 optimizers?)
SE11400 inverter
10.8 KW DC
36x LG 300W Panels
Enphase M250 (will these clip ... do I need to use lower wattage panels given ideal pointing of array?)
ThanksLeave a comment:
-
This is a good read on oversizing.......may help your decision process:
Leave a comment:
-
Most accurate because it is the highest? Um, ok. This is among the reasons why PVOutput.org data isn't totally reliable. Shutting off the SolarEdge public site is classy, too.
Edit:
You might want to check this thread to see that the SolarEdge end of day energy number could be inflated by several percent relative to more trustworthy data sources.
But I think we are digressing a little bit, I think we're in agreement that purely basing ones' choice on clipping alone without weighting cost is not smart. When costs are comparable, the effect of clipping (or running at full capacity) is very much dependent on individual situation and personal preference.
Edit: just checked, my SolarEdge public site is still working, did they shut down yours?Leave a comment:
-
Edit:
You might want to check this thread to see that the SolarEdge end of day energy number could be inflated by several percent relative to more trustworthy data sources.Last edited by sensij; 03-04-2015, 04:51 PM. Reason: Sorry for the snark. SolarEdge's portal site was down.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.0
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 02:04 PM.
Leave a comment: