That is what I hate about the solar industry. Most of them expect their customer to know nothing and care for nothing.
When you actually monitor things and point out the problems, they act offended and annoyed....Last edited by scrambler; 06-02-2023, 04:11 PM.Leave a comment:
-
Just wanted to wrap this up. SolaX issued me new firmware and remote installed it. This immediately increased production to the full 5kW on both invertors. They said bi-wiring was still required but this could just be from the DC isolator to the invertor and did not need to be all the way to the solar cells. My installer turned up and bi-wired the units (no apology or even any comment on the fact they had screwed up) but hey, they did turn up and it was free. I regularly got the full 10kW in summer (actually 9.96 kW) so maybe I should sue for my missing 40 watts
A good outcome but I am absolutely sure if I wasn't a data nerd and an engineer monitoring this closely it would have been capped at 3.4kW per unit for the entire life of the units.Leave a comment:
-
+1. The bigger they are, the less they'll respond.
But a pitch for and another advantage and logic of using established, local, quality vendors: They are usually much better at service after a sale.Leave a comment:
-
Leave a comment:
-
If you are not proactive and persistent, don't hold your breath waiting for a response.Leave a comment:
-
Neither my installer nor SolaX are responding to any emails. I pointed out that this 3.5kW limit is not documented. Expect there will be a lot of finger pointing and shouting. Just as long as I get my system fixed.Last edited by smbunn; 11-02-2021, 05:46 PM.Leave a comment:
-
I bet the installer has quite a few installations with maxed out MPPT inputs since they originally thought it was normal.SOLVED: I finally got the SolaX company to respond directly. These units have dual string MPPTs. Each string has a maximum capacity of 3.5 kW. My installer has wired 5 kW to one string only in each unit.
The only solution is to split the panels so there is 5 panels per string (2.5 kW) and run 2 more twin core DC cables. Down the side of my 3 story house with no access now that the scaffolding my neighbour let me put on his driveway has long since gone. The ducting is 1 inch (25mm) so no room to get 4 sets of 4mm DC pairs plus a 6mm earth.
The installer is going to have a big cost to fix this. Not my problem and ready to sue if they don't step up.
I have reviewed the Solax X1 boost "manual" in detail and cannot find anything about having MPPT input power limitations of 3.5kW. Solax manuals and technical support documents are very below par. Compare Solax documents to SMA, Fronius or Solar Edge.
Some possible solutions you can discuss with Other installers.
1) My SMA 7.7 -40 inverter supports parallel inputs on strings A and B. My original design had two strings of 9 panels panels each paralleled on the roof in a junction box (4 wires to 2 wires) , then split back out in my garage (2 wires to 4 wires) to inputs A and B. In my case this was 420Vdc max and 20amps max in two wires coming down from the roof, split back out to inputs A & B each 10mps max. Upon booting up, the inverter figures out that inputs A and B are paralleled and configures inputs A and B as one MPPT. The SMA 5.0 has three MPPT inputs and can parallel MPPT inputs A and B.
2) or you could look at a Fronius Primo and bring the + wire from the array input Fronius DC + input 1 and put a jumper between DC + input 1 and DC + input 2. Array - wire goes to Fronius DC - input 1; no jumper required. Then set MPP tracker 2 to off during start up.
Both of these potential solutions would not require you to pull additional wires from your roof. SMA and Fronius documentation is extensive. It would be up to your new installers knowledge base to ensure the solution selected would work with all of the equipment. I also believe you would have to change the export meter too, but I would do that anyway since Solax would have to remove all their less than perfect equipment.
This also assumed your original installer used the correct wire and wire sizes.
Like I said, I have an SMA -40 and it is built like a tank. I like it so much, I went ahead and bought a replacement to sit on the shelf. Lead times are out of this world right now. If you want first hand knowledge on Fronius, bruce can give you feedback.Leave a comment:
-
Leave a comment:
-
That is a major oversight in the part of the installer indeed
And the fact that they tried to BS you on top of it is more like a black eye...
Glad you got it sorted out.Last edited by scrambler; 09-13-2021, 11:59 PM.Leave a comment:
-
SOLVED: I finally got the SolaX company to respond directly. These units have dual string MPPTs. Each string has a maximum capacity of 3.5 kW. My installer has wired 5 kW to one string only in each unit.
The only solution is to split the panels so there is 5 panels per string (2.5 kW) and run 2 more twin core DC cables. Down the side of my 3 story house with no access now that the scaffolding my neighbour let me put on his driveway has long since gone. The ducting is 1 inch (25mm) so no room to get 4 sets of 4mm DC pairs plus a 6mm earth.
The installer is going to have a big cost to fix this. Not my problem and ready to sue if they don't step up.Last edited by smbunn; 09-13-2021, 11:57 PM.Leave a comment:
-
IMG_20210912_134115.jpg
IMG_20210912_134126.jpg
Checked both units faceplates. Both are SolaX Boost X1-5.0T rated at 4999 watts AC (5200 watts DC). It was something I considered as well.Leave a comment:
-
Good catch, although for Tigo even at 500W it should still not be an issue.
I assume you also verified the Model Number on your inverters faceplate, to make sure they actually installed 5kW models ....Leave a comment:
-
Tigo still sells TS4-A-O, 500 watt, part number: 451-00252-32. 700 watt model is part number: 461-00252-32.
Is the part number on your bill of sale? Your installer should have installed the 700 watt model but you never know. The optimizer description is exactly the same.
Also, just to check, there is a power limits parameter in your Solax menu tree. It is proportional and I assume it should be set to 1. This is not the export limits parameter.
Just two WAGs.Leave a comment:
-
Thank you.
In my case it was part of an Ambient WS2000 weather station that has a small solar panel on top of it. Rough but still matches the Solar production pretty well.
Since then because I have two of my 20 panels on Enphase micro inverters, I setup monitoring of these two Enphase panel with an Emporia Vue 2 Energy monitor, and it gives me the perfect baseline for what the other panel should be producing
I am definitely not suggesting to invest any significant amount of money on that. Just mentioned it in case he hits a wall with the installer.
The argument in itself should be sufficient. And at worst he can wait for summer to show his installer that his explanation does not hold...
Yes, it will be a rough correspondence and not much use unless correction is made to convert the GHI (Global Horizontal Irradiance) the weather station measures to POA (Plane of Array) irradiance the array sees. That's one of several reasons why Smbunn's irradiance graph of clear day GHI included with his first post was mostly useless.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 11:09 AM.
Leave a comment: