Okay...
let me get this straight in my head.
I'll do 4 panels in series, that's about to be around 150 V dc.
So... 4 panels in series. the negative lead of the last panel won't be connected to anything, just a dangling in the air.
From the + lead I'll measure with my low impedance analog meter to the frame (ground) or use a light bulb like you did
If I see voltage, then removed one panel at a time from the string until the voltage goes away. That panel is the one that's faulty.
Repeat on the other two strings 'cause I have 12 modules, four modules in a string, and thus three strings.
The new Hyundai panels are on the left, the used Trinas on the right. They are all back including the frames
IMG_1131-a.jpg
Mike
Try our solar cost and savings calculator
Solaredge ground fault isolation fault
Collapse
X
-
Actually my test was for bare panels, not sure if it will work with optimizers. Just
leaving the optimizers out and connecting the panels for the ground test might
work better, it will give the high voltages that cause more leakage. Bruce RoeLeave a comment:
-
You almost got it, use the IMAGE button, and the dialog box that pops up
UploadImage.png
Chose the UPLOAD tab, then BROWSE
and finally, SEND it to the SERVER, when the upload is complete, you can
then the Blue OK button.
Leave a comment:
-
This was the test I was conducting using my ohm meter. Reading ohms to ground.Attached FilesLeave a comment:
-
Mike, Sounds like you are on the right trail. Maybe those used panels were removed
because of ground leakage issues. I might disconnect the suspect panel string and
with some sun, use an old time mechanical meter to measure voltage from either end
of the string, to ground. The meter must draw small current (the Fluke does not) to
drain off any electro static charge. Or connect a 220K ohm resistor in parallel with
the Fluke.
Leaking bypass diodes will not cause a ground fault.
With a ground fault, I would expect a certain voltage at either end (opposite polarities),
which add up to the Voc of the panels. Regarding the string as a voltage divider, you
may be able to estimate the point of the fault. Multiple faults will be more difficult.
With the meter still reading one end of the string, you could disconnect the most far
away panel. Keep doing the next panel till the meter drops to zero, you have just
unplugged a ground fault panel. Removing it and reconnecting the rest, you may
find more faults. good luck, Bruce Roe
I was working on the array yesterday, it was about 60 here, and thought the very same thing. My Fluke as an input impedance of about 200MΩ which is clearly not enough load. Between my finger and the metal array frame, I can see some voltage displayed on the fluke caused by the dissimilar metals. I have an old Simpson 260 which I'll dig out. If I remember, I think it has an input impedance of about 20K or so.
Okay on the bypass diodes. I was reaching for an answer...
Each panel has one of the Solaredge optimizers hooked to it. Each optimizer makes 1 V when connected to a solar panel. As you may well be aware, when the inverter is happy, it turns on the optimizers and they squirt out 400ish V dc. Are you suggesting I disconnect the panels from the optimizers and then check panels?
One quickie... how do I post a photo? I clicked on the menu and it asks for url.
Mike
Leave a comment:
-
I would not use an ohmmeter to try and locate a panel ground fault, they
do not handle the voltages and junctions in a panel. On my 400 V strings
I have used this tool instead of a meter, a good part of an amp must flow.
Bruce Roe
PVtestLt.JPGLeave a comment:
-
Mike, Sounds like you are on the right trail. Maybe those used panels were removed
because of ground leakage issues. I might disconnect the suspect panel string and
with some sun, use an old time mechanical meter to measure voltage from either end
of the string, to ground. The meter must draw small current (the Fluke does not) to
drain off any electro static charge. Or connect a 220K ohm resistor in parallel with
the Fluke.
Leaking bypass diodes will not cause a ground fault.
With a ground fault, I would expect a certain voltage at either end (opposite polarities),
which add up to the Voc of the panels. Regarding the string as a voltage divider, you
may be able to estimate the point of the fault. Multiple faults will be more difficult.
With the meter still reading one end of the string, you could disconnect the most far
away panel. Keep doing the next panel till the meter drops to zero, you have just
unplugged a ground fault panel. Removing it and reconnecting the rest, you may
find more faults. good luck, Bruce RoeLeave a comment:
-
Solaredge ground fault isolation fault
Hello everyone. This is my first post.
My name is mike, and I'm in Ohio. I've been using and designing photovoltaic systems since 1978. This isn't my first rodeo, however that being said, up until this summer all my systems have been off the gird battery based and generally used for communications.
This summer I completely re-did my 48 V dc battery system complete with new batteries and new panels. The 20+ year old Solarex (remember those?) panels were removed and 20 used (Came from a decommissioned solar farm out west) 250 W Trina panels were installed. A new Midnite Solar Classic 150 went in with all new wiring and controls. Life is good! On a bright cool days, I see 80+ A going into my 16 US batteries (L16 clones) A Trace 5548 sine wave inverter handles 80% of the home's loads.
That system works like gang busters.
Until I purchased a electric car.
The old trace can't do 240 V, so I decided to install a grid tie system that would supply the missing 20% the inverter can't do like the 240 V deep well pump and the AC. The gird tie would also allow me to charge the EV when the sun is shinning.
Long story short as they say...
Found out from the local electrical inspector that the panels I had purchased, the used Trinas, won't pass inspection because the "UL" labels had been removed. So I purchased 12 new panels and installed them on the ground mount. Because of several issues with my panel box, and the meter base, I had to have an licensed electrical do the actual hookup to the gird.
Inspector came out, passed the system on the first go.
I was making 3kW back into the grid with 12 Hyundai 250 W panels.
Later, I added another 12 panels. These were the used Trina panels. So I bumped my output from 3kW to 6kW.
Between the new grid tie and the battery based inverter, the following electric bill was $5.01 which was the cost of the meter and billing. I actually had an excess of kWs generated.
Fast forward....
The Solaredge inverter would shut down when it would rain or have a few cloudy/wet days. Error was a ground fault. They also call it a isolation fault.
Disconnected the trina array, and the error went away.
I don't have a Megger, but do have some Fluke 87 meters.
With the + and - leads of a solar panel shorted together, I see 590Ω to the array framework.
Some modules show more leakage, some are perfectly fine. According to the Solaredge trouble shooting guide, I should see 80MΩ on the panel. My Fluke can't read that high of resistance, but 590Ω certainly isn't correct!
If I test from the + lead of the single pv module, to frame (ground) with the neg lead of the PV module just a hanging in the wind, I read from 5 V to as high as 27 V.
Obviously, there is leakage from the + lead to the frame, and the inverter senses this leakage and throws the error.
Has anyone ever seen this happen with the panels? I could see water in a junction box, moisture in the MC4 connectors, a wire break, and so on.
While I haven't checked, I'm thinking maybe the bypass diodes in the Jbox of the panel might be leaky. I popped the cover and the diodes look like they are welded in,
So, I'm up for any suggestions, because right now, It looks like I'm going to have to scrap the Trina panels and install new ones. (BTW the new panels don't give the same results as the used Trinas)
Sorry for the long post, but wanted to cover all the bases
I'm Mike
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 09:13 PM.
Leave a comment: