It's not 'overclocking'. That would be tinkering with the inverter to force it to output more than its nameplate. A 7.6kW inverter is designed to put out 7.6kW. I'd love to see the design criteria of the inverters but it doubt they assume a typical load profile. I worked with 150kW inverters at a plant that ran 24/7 for years with no issues. Heat is the enemy of electronics and while 7.6kW for 5 hours would produce more heat than a bell shaped load profile that increased heat is small compared to environmental factors. So an 'oversized' inverter in Denver would be 'stressed' much less than a 'right-size' inverter installed in Phoenix.
Plus if there was a significant impact on longevity I doubt inverter manufacturers would be not only covering oversized inverters up to 150% but actively encouraging it.
https://www.sma-sunny.com/en/7-reaso...ur-pv-array-2/
Try our solar cost and savings calculator
Clipping more than expected
Collapse
X
-
Last edited by nwdiver; 03-25-2019, 01:22 PM. -
Inverter stressing is definitely a thing. Read the literature from the SolarEdge inverter lineup. You are quoting information from a professional grade solar farm inverter which are designed to do this. The normal household inverter would suffer greatly from this type of overclocking. You CAN NOT compare a solar farm installation to a home installation.
My argument is that as Solar policies shift due to increased adoption, as NEM goes away the 'cost' of clipping will be significantly reduced. In SPS territory in TX there is no NEM. A kWh exported is worth ~80% less than a kWh self-consumed. Even with storage increasing generation when it's needed is cheaper than storing mid-day surplus. So energy added in the morning and evening will likely be worth ~5x more than energy that would be lost mid-day. Sure, if it's just a $150 step change to the next size inverter it may pencil out but this is often not the case. The system profile I attached would have required a $5k service upgrade to increase the inverter capacity.
And 'inverter stressing' isn't a thing. SMA actually published a white paper explaining that failure rates don't increase even with arrays oversized by 200%.
https://www.sma.de/fileadmin/content..._180530_01.pdf
Current home inverters also don't suffer from kicking on earlier to give you extra energy in the morning. The efficiency of current inverters don't have the same type of curves of solar farm inverters or the older inverters.Leave a comment:
-
My argument is that as Solar policies shift due to increased adoption, as NEM goes away the 'cost' of clipping will be significantly reduced. In SPS territory in TX there is no NEM. A kWh exported is worth ~80% less than a kWh self-consumed. Even with storage increasing generation when it's needed is cheaper than storing mid-day surplus. So energy added in the morning and evening will likely be worth ~5x more than energy that would be lost mid-day. Sure, if it's just a $150 step change to the next size inverter it may pencil out but this is often not the case. The system profile I attached would have required a $5k service upgrade to increase the inverter capacity.
I have no idea what type of argument is being made here. Clipping should be minimal, especially with the small price increases in inverter size. If you think it is acceptable that your installer thinks clipping from 10 am until 4 am is acceptable, then you embraced a lie... This type of clipping is going to stress inverters, I hope you have an extended warranty on them!
And 'inverter stressing' isn't a thing. SMA actually published a white paper explaining that failure rates don't increase even with arrays oversized by 200%.
Leave a comment:
-
I have no idea what type of argument is being made here. Clipping should be minimal, especially with the small price increases in inverter size. If you think it is acceptable that your installer thinks clipping from 10 am until 4 am is acceptable, then you embraced a lie... This type of clipping is going to stress inverters, I hope you have an extended warranty on them!I think a lot of this has to do with better educating customers. Clipping is going to get A LOT more common going forward. Installers and owners need to start embracing it. As solar PV becomes more common energy generated around noon on a sunny day will be worth less and less while energy on cloudy days and in the evenings will be worth more and more. So it's going to make sense to oversize arrays and face them west to increase the production of valuable energy even if it means losing some at noon that would be worth much less. My most recent system was similarly oversized though the panels are in a E/W arrangement which slightly mitigates clipped production.
NEM also can't last forever... clipped energy is much more likely to be exported => less valuable than energy added in the morning and especially in the evenings.
Screen Shot 2019-03-24 at 7.50.05 PM.pngLeave a comment:
-
I think a lot of this has to do with better educating customers. Clipping is going to get A LOT more common going forward. Installers and owners need to start embracing it. As solar PV becomes more common energy generated around noon on a sunny day will be worth less and less while energy on cloudy days and in the evenings will be worth more and more. So it's going to make sense to oversize arrays and face them west to increase the production of valuable energy even if it means losing some at noon that would be worth much less. My most recent system was similarly oversized though the panels are in a E/W arrangement which slightly mitigates clipped production.
NEM also can't last forever... clipped energy is much more likely to be exported => less valuable than energy added in the morning and especially in the evenings.
Screen Shot 2019-03-24 at 7.50.05 PM.pngLast edited by nwdiver; 03-25-2019, 01:18 AM.Leave a comment:
-
Well about year later and I finally got my system "fixed". Because of the clipping almost everyday for 4 hours from my 11.25 kW system from March until August, the owner agreed last summer to add a SE3800H, free EV charger since they installed an older SE7600, do a line-side tap, and have me $360 for clipping. They then forgot about me and I had to call back. They then came to add the inverter in January this year and were just going to put half of the 11.25 kW panels on a 3800 inverter and make my clipping worse. I had to stop the workers from doing this. They then said I was correct and they would call me that night. One month without contact and i was the one who contacted back. The owner personally apologized again and they came out two days later and now my system is finally finished and I can charge my car with a SE7600.
So my 11.25 kW three array system was on a single SE7600 before. Now my system has two SE7600 inverters with 5.625 kW on each inverter, they did a line-side tap, gave me a free EV charger, will be installing two more LG375W panels on my system for free in a few weeks, gave me a $200 check(now up to $560), and $100 gift card to a nice steakhouse in town. Plus the lead guy in charge of the maintenance part of the company told me that if I ever want to add more panels that they would give me a good deal.
The company dropped the ball many times with me and I think they are hoping I don't leave a bad review. Here is a picture of my production today. It is still February and I would have clipped today with the system that was "designed" by someone that had no idea what they were doing.Attached FilesLeave a comment:
-
I already have a Chevy Bolt and I charge about 40 kWh everyday. The EV rates for the electric company are amazing if you can avoid using energy during peak times. Plus the EV rates don't have any tiers.
No it is NOT commonplace. SolarEdge allows that for situations of high shade, or straight East/West installs etc. Most installers would NOT have put in such an over paneled system as yours. However I would definitely try to get a better handle on an estimate of the loss. Since you were looking at an EV, one solution would be to add a SE3800H which can also have an EV charger allowing you to have two EV chargers, and no clipping. it might be cheaper to do a lineside tap instead of electric panel upgrade as well.
I will ask the contractor about the possibility of adding a smaller inverter. I think that this would be the way to go. It also would allow me to maybe get battery storage in the future when prices fall and still have an EV charger at the same time. I really don't want to lose the ability to charge my EV directly from my solar panels, even though I have a hard-wired 40 amp EV charger. Net metering does have a 2 cent charge for each kWh pulled from the grid. I think I will definitely look at that option of adding another inverter.Leave a comment:
-
No it is NOT commonplace. SolarEdge allows that for situations of high shade, or straight East/West installs etc. Most installers would NOT have put in such an over paneled system as yours. However I would definitely try to get a better handle on an estimate of the loss. Since you were looking at an EV, one solution would be to add a SE3800H which can also have an EV charger allowing you to have two EV chargers, and no clipping. it might be cheaper to do a lineside tap instead of electric panel upgrade as well.I agree the system design could have been better. The clipping is probably a few thousand per year looking at the graphs from the last few days. With the 7600 accepting up to 11.78 kW of panels I think this may be commonplace now. I have three separate arrays, so it probably isn't as bad as other systems. I could see a contractor putting the same system I have on one azimuth. It is not enough for me to complain to the contractor since their price was $2.80 a watt compared to the other 5 quotes I received that were all over $3.10. The contractor also said they would include the EV charger for the inverter once it becomes available. Seeing a flat line graph for 9 hours in three days shows that my system is overpowered for the inverter.Leave a comment:
-
I agree the system design could have been better. The clipping is probably a few thousand per year looking at the graphs from the last few days. With the 7600 accepting up to 11.78 kW of panels I think this may be commonplace now. I have three separate arrays, so it probably isn't as bad as other systems. I could see a contractor putting the same system I have on one azimuth. It is not enough for me to complain to the contractor since their price was $2.80 a watt compared to the other 5 quotes I received that were all over $3.10. The contractor also said they would include the EV charger for the inverter once it becomes available. Seeing a flat line graph for 9 hours in three days shows that my system is overpowered for the inverter.Leave a comment:
-
Get a better handle on how much clipping you may be experiencing. It probably isn't 15,000 kWh/yr. or as much as a few hundred kWh/yr. More than that and I'd suggest the system design might have been better.Leave a comment:
-
I was thinking about upgrading my electric panel to accommodate a larger inverter. It would cost me about $3000 to do this and with the large clipping I thought it may be worth it. $3000 is a lot of kWh and it would take about 15,000 kWh to earn back that money.
Leave a comment:
-
See my post and then read the PVWatts help screens and the TMY manual for a better understanding of why PVWatts is not "predicting" clipping.
I put in the three separate arrays with the pitch of roof, geographic location, azimuth, etc... I took the data from the spreadsheets and added the three arrays together for production for each hour. The results showed clipping, but not until April. Even then, the clipping was minimal. Maybe an hour or two a day max. Does PVWatts seem to underestimate production?
PVWatts will produce a model of annual output based on input. No more. Saying an hour's output or a series of hourly outputs is a reliable predictor of future behavior is unrealistic.Leave a comment:
-
I put in the three separate arrays with the pitch of roof, geographic location, azimuth, etc... I took the data from the spreadsheets and added the three arrays together for production for each hour. The results showed clipping, but not until April. Even then, the clipping was minimal. Maybe an hour or two a day max. Does PVWatts seem to underestimate production?Leave a comment:
-
PVWatts showed you nothing of the sort. Read the PVWatts help screens.
The question is how much clipping am I really experiencing? I was expecting a little clipping, but even pvwatts showed me I wouldn't be getting any in March. Getting five hours of clipping in a partially cloudy, windy, and below 60 degree day in March is excessive. I know I shouldn't worry about this and I should be glad I produced almost 67 kWh in a single day in March.
The output from PVWatts is based on "representative" weather - not "actual" or "average" weather. Most all of the weather, particularly the irradiance data from what PVWatts and many other output models use is synthetic, or modeled. Little of it, particularly the irradiance data is from actual weather records. See something called the TMY manual for details.
Any or a lot of clipping may or may not occur. Provided a system is well designed and fit for purpose, how much or how little clipping occurs and in what sequence or season is mostly a function of the weather. As such, clipping predictions are about as reliable as a weather forecast and for about as far into the future. No model can predict the weather beyond a few days, much less over a year's worth of modeling.
PVWatts is a model used for system design. It is not a predictor.
If you know you shouldn't be worried about it, why are you ?
Leave a comment:
-
I didn't realize that panels have positive temperature coefficient when they are colder than 77 degrees. I thought the 77 F was optimal temperature for production, it is just the temperature they are tested at. How can wind help? Is it just by clearing dust and debris off of the solar panels?
I know the clipping may be difficult to model, especially with multiple arrays. I know you can't apply a simple bell type curve with multiple azimuths. The cold weather makes perfect sense with getting peak production, I was actually thinking about upgrading my inverter and electric panel because of the results recently.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.