Zero feed into grid with Enphase?

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • #46
    The M250 installation manual http://enphase.com/sites/default/fil..._Manual_NA.pdf says:

    "NOTE: When inter-connecting to grids managed by Hawaii Electric Industries (HEI), including HECO, you must select an appropriate grid profile for your installation. You can set the grid profile through Enlighten, during system registration, or through Installer Toolkit at any time. You must have an Enphase Envoy communications gateway to set or change the grid profile. For more information on setting or changing the grid profile, refer to the Envoy or Envoy-S Installation and Operation Manual at enphase.com/support."

    I found https://www.hawaiianelectric.com/cle...upply-programs with a list of "qualified equipment": https://www.hawaiianelectric.com/Doc..._equipment.pdf. The S-series is listed as CSS (customer self service = zero feedback) capable, the M250 is not.
    Last edited by rickj; 07-09-2017, 02:27 PM.