Try our solar cost and savings calculator
MorningStar Tristar or Midnight Charge Controller For Small Off Grid System?
Collapse
X
-
Whoa. here's my data.
Morningstar Only the MS 60A mppt has the ethernet port. The MS 45A I think, has a serial port (my 60a does) and I connect it to my laptop with a SERIAL-USB adapter. The morningstar MSView program downloads the log files, and also can re-program the settings. MSView is a very powerful program, but the .CSV file it outputs, needs to be massaged in a spreadsheet.
The ethernet is just a Viewing HTML page, not interactive.
Midnight Classic. I've never tried to get the logs out of it, I just need the daily stats that I can read off it's monitor panel (over ethernet) The Classic has a nice ethernet remote control app, I use the float/absorb controls, and the ability to tweak the voltages remotely, enables me to get the two controllers to sync nicely.
With my 2 Evergreen arrays, the Morningstar seems to have a better efficiency and robustness than the Classic. it's also much cooler and quieter (no fans) -
Leave a comment:
-
I'd rather not make the sale than sell what I don't believe in. I also try to prevent the Burning Man reenactments at people's homes.Leave a comment:
-
Mistake everyone makes. We trust educators to give us the correct information without question. Unfortunately there is a reason why some teachers teach. Takes a while and some age to question everything. I am not saying what you were taught was wrong. Over sizing is not wrong, but it is not required and is a design issue and not a requirement.
In any event do not take the manufactures word for any code issue. They might be Covering their butts with over kill and it is important you understand when you see that. It could cost you a job. If they cite a code, go read it. If you do not understand go to Mike Holt Forum and either I or one of the other mods or members will get you the right info.Leave a comment:
-
No problem with that Amy from a code POV, but it does allow your competitor to underbid you, and makes the manufacture mo money. So you need to understand the difference between minimum code requirements and biz requirements. One effects the other.
Technically both but NEC is the one that gets you in trouble with the AHJ and courts. Good example is compression connectors. NEC basically says follow all manufactures directions for making a certified listed connector (UL). The manufacture will tell you what specific tool is required. You cannot use the truck to run over and squeeze on a compression connector. Redneck Tools and Southern Engineering is not allowed.
Here is me in my Red Neck Swimming Pool

Here is what happens to Red Necks doing Electrical Wiring.
Leave a comment:
-
Leave a comment:
-
That's why I like this forum, it's making me rethink the status quo and question things I learned 7 years ago, and have been teaching forward. I do stand by oversizing the charge controller by 25%, every manufacturers' manual and string sizer tells you to. (Is it UL or NEC or both that tells you to refer to manufacturer's instructions?) I'm just trying to come up with the why. I had been taught that it was for over-irradiance, but again, I can't find the source, and the charge controllers had the 3-hour continuous already included, so just do the one 1.25.
I was about to release a new video today on sizing a charge controller, I put it on hold until I get the answer of why.Leave a comment:
-
You're right. Good catch. I wish they would do a better job of outlining that on their webpage.The data port is not the same as Ethernet. Data is possible locally on all versions via optional adapters, remote Ethernet is only available on the 60A.
Here on page 51 it says Ethernet is only on the TS-MPPT-60. http://www.morningstarcorp.com/wp-co...ors-Manual.pdf
I suggest you read the manuals of both Morningstar and Midnite, and decide which logging features are most important to you. Both are great charge controllers, I think it's a personal choice which meets your needs better.
Thanks!Leave a comment:
-
Amy NEC does not cover equipment as it is out of the NEC jurisdiction. Equipment is UL. I think what you are reading from Manufactures is CYA and ignorance like putting a Ground Stud and telling you to connect it to A GROUND ROD. When you buy a gizmo the manufacture tells you what the input requirement is like not to exceed X volts @ Y amps using a minimum Z gauge conductor.
If you design based on Voltage drop like 2%, then unless you are operating at high voltages or very short distances you will always exceed NEC requirement. Most of the quality Charge Controllers will give you a Table of Wire sizes based on source voltages and distance. The smallest wire will always meet or exceed minimum NEC requirement.
I am not trying to put you down, I am trying to understand where you are coming from. I do not know of anywhere in 690 the code requires the CC to be derated. Nor do I know of any code article that requires the equipment to be derated. What I do know is the code does requires conductors to be up-sized if the equipment is continuous duty, and a solar panel source circuit is considered continuous duty. But NEC jurisdiction ends at the end of the wire going to the equipment. Only exception I can think of is Buss Capacity.Leave a comment:
-
Derek, you've got me obsessed on this today. All of the manuals refer to a NEC safety margin of 1.25 when sizing the charge controller, not just the wiring, but no one is giving a reference number. The one I gave was my guess while getting from the horses mouth. I just sent off a note asking 1 manufacturer, about to send a couple more out to see who can get me the specifics.That is for the wire, not controller. For the wiring between panels in controllers on a battery system unless the run is very short do not really apply in the design because of voltage drop is taken into accout which will almost always be larger then the minimum NEC requirement. Grid Tied systems running several hundred volts are another story.
Example from Morningstar manual:
To comply with the National Electric Code (NEC), the current rating of the controller must be equal to or greater than 125% of the solar array’s short circuit current output (Isc). Therefore, the maximum allowable solar array input to the TriStar MPPT 150V controller for compliance with the NEC is:
TS-MPPT-30: 24 amps Isc*
TS-MPPT-45: 36 amps Isc*
TS-MPPT-60: 48 amps Isc*
*Solar array Isc @ STCLeave a comment:
-
The data port is not the same as Ethernet. Data is possible locally on all versions via optional adapters, remote Ethernet is only available on the 60A.Here you can also find that the 45Amp model does have the same communication features as the 60Amp model: http://www.morningstarcorp.com/compa...81&product_03=
I would prefer to sale my PWM Morningstar Prostar 30, and just stick with the Morningstar brand for now and upgrade to the 45Amp MPPT model. However, if Midnite's charge controller is better for data logging, then maybe it's worth making the switch?
Here on page 51 it says Ethernet is only on the TS-MPPT-60. http://www.morningstarcorp.com/wp-co...ors-Manual.pdf
I suggest you read the manuals of both Morningstar and Midnite, and decide which logging features are most important to you. Both are great charge controllers, I think it's a personal choice which meets your needs better.Leave a comment:
-
That is for the wire, not controller. For the wiring between panels in controllers on a battery system unless the run is very short do not really apply in the design because of voltage drop is taken into accout which will almost always be larger then the minimum NEC requirement. Grid Tied systems running several hundred volts are another story.Leave a comment:
-
Here you can also find that the 45Amp model does have the same communication features as the 60Amp model: http://www.morningstarcorp.com/compa...81&product_03=
I would prefer to sale my PWM Morningstar Prostar 30, and just stick with the Morningstar brand for now and upgrade to the 45Amp MPPT model. However, if Midnite's charge controller is better for data logging, then maybe it's worth making the switch?Leave a comment:
-
The charge controller output is the same for either wiring, so the amp rating required is the same, since charge controllers are rated in their output, not input. The manuals for all of the ones I am familiar with say to multiply the Isc by 1.25 for NEC. None of them actually mention a reference, so I assume it is either for 690.8(A)(1)* or for over-irradiance. I need to double check.Huh? If you are talking about the wiring then OK. But that is not required for the charge controller. He has 400 watts of panels. Does not matter how they are configured with MPPT. The input current can be either 5.75 amps or 23 amps, but at 12 volt battery the output is 33 amps. So what is the 1.25 Correction Factor for the Controller used for? I understand the wiring part, but not the controller as its output is Panel Wattage / Battery Voltage.
Therefore, if wired in parallel, Isc x 4 strings x 1.25, or if wired in series, the charge controller drops the voltage by 4 so it increases the current x4, so same math.
Regardless, if you use any of the manufacturers' string sizers, you will find that the max Isc output is always 80% of their rating.
*690.8(A)(1) Photovoltaic Source Circuit Currents. The maximum current shall be the sum of parallel module rated short-circuit currents multiplied by 125 percent.Leave a comment:
-
Huh? If you are talking about the wiring then OK. But that is not required for the charge controller. He has 400 watts of panels. Does not matter how they are configured with MPPT. The input current can be either 5.75 amps or 23 amps, but at 12 volt battery the output is 33 amps. So what is the 1.25 Correction Factor for the Controller used for? I understand the wiring part, but not the controller as its output is Panel Wattage / Battery Voltage.Leave a comment: