A few years ago I took the full Investment Tax Credit (ITC) on a system with a DC to AC ratio of 1.5 to one. I do not recall even having to state the DC to AC ratio on that or any of my previous ITC deductions. It was simply the total cost that was used. Is that stated somewhere in the IRS Regulations?
I am not familiar with the term STCs as it pertains to the ITC. In the solar world STC usually refers to Standard Test Conditions.
Try our solar cost and savings calculator
Adding solar panels
Collapse
X
-
Last edited by Ampster; 09-23-2021, 02:13 PM. -
My DC:AC ratio is over 2.3:1. That works because the panels are split between E and W,
giving the same peak power for more hours. And and a 2 sided array can mount twice as
many panels for about the same cost. Bruce Roe 3Direction.JPG
Leave a comment:
-
If you have a 1.5kW inverter, you can have up to 2kW of panels attached.
If you have a 3kW inverter you can have up to 4kW of panels attached.
If you have a 5kW inverter you can have up to 6.65kW of panels attached.
And if you don’t go over the 133%, you can claim the solar rebate (STCs) on those extra panels which will cover a big chunk of their of their cost (excluding installation costs and installer margin).
Moderator edit: Please, no more advertising links, thanks.Leave a comment:
-
I am glad your batteries are ok with your CC arrangement. Keep us informed on how it performs.
Bingo!
That did it. On the whole I'm wasting some wattage from the older array but as far as resolving issues, that fixed it. Max output with Classic 150 and Epever 3210 = 64~ amps. Max amperage with Classic 150 handling both arrays was 74.4 today. SG end of day is 1.26.
Batteries handled it well with no more bubbling than usual. Only issue presented was how much hotter the Classic got, with FET and PCB both around 69C. But Midnite Solar told me that is way under unit tolerance. It won't perform as well but it won't melt either.
Even the 2 arrays weren't all that mismatched on vdc, probably because of age and possible dust buildup on 1st array. When I put my voltmeter to every series all voltages (on load to Classic) were between 65.7 and 68.1. So the new panels are just like the old panels except they contribute 3x the amps to system.
Thanks for all input, folks.Leave a comment:
-
Bingo!
"My first concern is having a second pv charging system connected to the same batteries"
So... on that idea. My understanding is that if you install mismatched panels the system voltage will degrade to lower VMP but IMP will still be added to array. If the Classic sizing tool indicates my 150 can handle the additional 4 panels I installed, and the VMP difference between the older (36.5 vdc) and newer panels (31.3 vdc) is acceptable wattage loss, can I try doing that to see if it improves things? VOC of old is 43.8. VOC of new is 38.5.
That did it. On the whole I'm wasting some wattage from the older array but as far as resolving issues, that fixed it. Max output with Classic 150 and Epever 3210 = 64~ amps. Max amperage with Classic 150 handling both arrays was 74.4 today. SG end of day is 1.26.
Batteries handled it well with no more bubbling than usual. Only issue presented was how much hotter the Classic got, with FET and PCB both around 69C. But Midnite Solar told me that is way under unit tolerance. It won't perform as well but it won't melt either.
Even the 2 arrays weren't all that mismatched on vdc, probably because of age and possible dust buildup on 1st array. When I put my voltmeter to every series all voltages (on load to Classic) were between 65.7 and 68.1. So the new panels are just like the old panels except they contribute 3x the amps to system.
Thanks for all input, folks.Last edited by -robw-; 08-14-2020, 09:57 PM.Leave a comment:
-
"My first concern is having a second pv charging system connected to the same batteries"
What is strange is that 1800watts should deliver over 60amps into a 24V battery system. Those 8 CR305 wired 2Px4S create a 610Ah 24V system which should match up to that Classic 150 just fine.
My first concern is having a second pv charging system connected to the same batteries.
My second concern is having 1080w connected to the Epever 3210 which exceeds it's max watt input by close to 300watts. Unless you point the panels in different directions you could overload the Epever.
So... on that idea. My understanding is that if you install mismatched panels the system voltage will degrade to lower VMP but IMP will still be added to array. If the Classic sizing tool indicates my 150 can handle the additional 4 panels I installed, and the VMP difference between the older (36.5 vdc) and newer panels (31.3 vdc) is acceptable wattage loss, can I try doing that to see if it improves things? VOC of old is 43.8. VOC of new is 38.5.
ThanksLeave a comment:
-
For sure, but when I have 2580 PV watts available, and the Classic's 5 hr absorb stage completes with ending amps at around 8 but SG is only 1.22 something ain't right.Leave a comment:
-
That's the way a 3 stage charger works, max amps till Absorb voltage is reached, then the amps taper off thru the whole absorb. Usually Absorb is 3 or so hours , fancy controllers you can preset so that at 10% of max amps. it terminates Absorb and drops to FLoat, which can still continue to top off the batteries.
MS_charge_stages.pngLeave a comment:
-
I want to add that 60a isn't actually the issue. With clouds being outlawed here 300 amps is easy to accomplish with 60 amp current. The actual problem is how once absorb voltage is hit and current starts dropping, I'll find the SOC at around 75% and current dropped all the way below 20 amps. That's why I can't top SG.Leave a comment:
-
Done. Not yet in peak sun which hits 2 hours from now, but reached a high of 650~ watt output from Epever 3210. That's acceptable given sun, 780w max, and that the thing cost $80. Then turned on strings connected to Classic 150, one by one. All 5 between 4-4.2 amps, also acceptable given 5.3a IMP, sun, and age. Total current hitting batteries is 64 amps, 48.5a from Classic and 16.8a from Epever.So, you must have several strings of PV wired to the charge controller. At your combiner box, shut all strings but one, down. let controller stabilize, and record the power, and then add another string, remove the first, let stabilize, and record the power until you have tested and recorded all strings. All should be within a couple % of the rest. You may have some bad panels, and comparing strings is the quick way to test for them.
I've got 800ah of batteries @ 48V, and 5kw of PV, and just able to get by in winter with 7kwh daily usage, 2 cloudy days, and I need generator. If you are over paneled, you can switch some strings off in the summer and bring them back on for cloudy conditions. Having a decent combiner box with breakers is critical.
All that is consistent with my thoughts that this issue has nothing to do with input, and everything to do with batteries internal resistance. Even now, as the Classic 150 was ramping up to its present 48a the Epever was dropping down to 17a. The batteries just won't accept more than 60~ amps.
I tested end of strings with my ammeter and results are 30.08a on 1st string, and 31.4a on 2nd string. So connectivity isn't issue. Only thing left, imo, is 3 month old batteries.
As I post this total current has increased to 64.8a
.Leave a comment:
-
So, you must have several strings of PV wired to the charge controller. At your combiner box, shut all strings but one, down. let controller stabilize, and record the power, and then add another string, remove the first, let stabilize, and record the power until you have tested and recorded all strings. All should be within a couple % of the rest. You may have some bad panels, and comparing strings is the quick way to test for them.
I've got 800ah of batteries @ 48V, and 5kw of PV, and just able to get by in winter with 7kwh daily usage, 2 cloudy days, and I need generator. If you are over paneled, you can switch some strings off in the summer and bring them back on for cloudy conditions. Having a decent combiner box with breakers is critical.Leave a comment:
-
Well something is not working up to par with your system. You should be getting that 75amps of charging with 1800watts.
It's all good. If you're curious as to what I did: 1) sent reply 2) edited to add quoting of Suneagle's response 3) tried re-editing to embolden a statement by Suneagle.
Classic does take over as lead charger, and Epever isn't terrible in backup role. For example, my larger system has 2 FM-80's and where I would rather each supply current 50-50, instead one always drops off later in the absorb cycle as "charged". So, right now one of them is supplying 40+ amps while the other is "charged" - not supplying anything. At least the Epever is supplying 1 amps right now while Classic is supplying 11.5a.
Thanks for the 76a rate. I was looking for that all morning because Crown had no idea.
As far as panel tilt, they're perfect for this time of year at 13 degrees. As far as Classic config, not only have I spent the past month talking with techs at Crown, Midnite Solar, Epever, and the people I bought equipment from, trying to solve SG issue, but I can't imagine what setting besides "max output amperage" (set at 80a) would control this. I have played with absorb voltage (currently at default: 29.1v), time (3-6 hrs, set at 5hr), I have done more frequent equalizations. Ending amps is and has been at 0.
If you recall, this all started with me wanting a consistent 1.26+ SG every night. But as it is, if I dedicate my day I can achieve that (restarting, equalizing, etc.), but no config will achieve that by itself. My primary system hits 1.27 every. single. night.
Since you have gone over all the possibilities for the Classic maybe one or more of the panels is not putting out what it is listed for and your system is rated below that 1800watt total.Leave a comment:
-
It's all good. If you're curious as to what I did: 1) sent reply 2) edited to add quoting of Suneagle's response 3) tried re-editing to embolden a statement by Suneagle.Sorry about the post problems, the site tries to figure out who is a spammer based on their behavior and I guess something you did, maybe editing a couple of times, gave it a false positive. It puts it into a moderation status, but we'll try to fix it quickly when we see that it has happened. --Steve
Classic does take over as lead charger, and Epever isn't terrible in backup role. For example, my larger system has 2 FM-80's and where I would rather each supply current 50-50, instead one always drops off later in the absorb cycle as "charged". So, right now one of them is supplying 40+ amps while the other is "charged" - not supplying anything. At least the Epever is supplying 1 amps right now while Classic is supplying 11.5a.The reason I am concerned with a second CC connected to the same battery system is that in the past unless the two CC can communicate with each other they can fight each other.
Maybe the Classic will take over as the lead charger with the Epever doing the rest but if the battery system is up to a specific voltage a second CC will think all it done and not provide any additional charging amps.
The Classic should be able to provide up to 96amps but I do not have hands on experience to know how much wattage that requires for a 24V systems without exceeding its 150VDC input rating.
The batteries should be able to handle a C/8 charge rate which would be about 76amps. Maybe the Classic is not set up correctly to continue to charge even with enough panel wattage.
Also even though you may have 1800 watts connected to the Classic the panels may not be optimumly pointed to generate full output.
Thanks for the 76a rate. I was looking for that all morning because Crown had no idea.
As far as panel tilt, they're perfect for this time of year at 13 degrees. As far as Classic config, not only have I spent the past month talking with techs at Crown, Midnite Solar, Epever, and the people I bought equipment from, trying to solve SG issue, but I can't imagine what setting besides "max output amperage" (set at 80a) would control this. I have played with absorb voltage (currently at default: 29.1v), time (3-6 hrs, set at 5hr), I have done more frequent equalizations. Ending amps is and has been at 0.
If you recall, this all started with me wanting a consistent 1.26+ SG every night. But as it is, if I dedicate my day I can achieve that (restarting, equalizing, etc.), but no config will achieve that by itself. My primary system hits 1.27 every. single. night.
Leave a comment:
-
Sorry you are having issues posting. Steve should be able to get it under controlSite is not allowing me to edit my post so a couple of post-edits:
1) I was responding to "What is strange is that 1800watts should deliver over 60amps into a 24V battery system"
2) Max PV for 3210 is 1170w, although max charge current is 780. We both acknowledged I would be wasting some wattage but doing so was a compromise.
Why is the 2nd controller a concern? afaik, it was the only way I could wattage to system, short of purchasing another Classic 150.
The reason I am concerned with a second CC connected to the same battery system is that in the past unless the two CC can communicate with each other they can fight each other.
Maybe the Classic will take over as the lead charger with the Epever doing the rest but if the battery system is up to a specific voltage a second CC will think all it done and not provide any additional charging amps.
The Classic should be able to provide up to 96amps but I do not have hands on experience to know how much wattage that requires for a 24V systems without exceeding its 150VDC input rating.
The batteries should be able to handle a C/8 charge rate which would be about 76amps. Maybe the Classic is not set up correctly to continue to charge even with enough panel wattage.
Also even though you may have 1800 watts connected to the Classic the panels may not be optimumly pointed to generate full output.Leave a comment:
-
Sorry about the post problems, the site tries to figure out who is a spammer based on their behavior and I guess something you did, maybe editing a couple of times, gave it a false positive. It puts it into a moderation status, but we'll try to fix it quickly when we see that it has happened. --SteveLeave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 07:32 AM.
Leave a comment: