Tear your drawing up, it is worthless. Quit talking to sales people and factory reps telling you what you need or do not need. Cheese and Rice dude they are trying to sell you a Lightning Arrestor, Combiner with fuse for a stinking RV. That is a few hundred dollars of stuff you have no use for like a shunt. Ask them if they can sell you four flat tires for the RV while you are talking to them. I am sure you could use those too. Give me a couple of hours and I wil draw up what you need.
Answer these questions.
Panel Wattage
Battery Voltage and Capacity
Inverter Size
Try our solar cost and savings calculator
I have (x3) 150W panels, and need 1600Wh a day. Suggestions for battery banks?
Collapse
X
-
Two separate issue. Fo rcurrent counting you will need 2 shunts which basically don't tell you a dang thing. Just more money for the seller.She tried pretty hard to sell me on that Whizbang Jr. thing, so I threw that in there. (Although it's an axiom of mine to remain skeptical about any claim of safety or usefulness, least not from the person whose trying to sell you the thing in question.)
$60 for an accurate reading on battery charge was the jist of it, from what I understand (hence requiring a shunt instead of one of those Blueseas Busbars?)
Depends if you operate the system Grounded or Floating. If Grounded then only on the Ungrounded Circuit Conductor. If Floating then both polarities must be protected.Leave a comment:
-
What you need to insure is that the only path for that part of the current that you want to measure is through the shunt.
If you want the shunt to measure total current into and out of the battery there must be no parallel connection to the battery terminal from any equipment that would bypass the shunt.
If you want to measure inverter load current, you would put the shunt in series with the inverter's negative input.
If you want to measure charging current, you would put the shunt in series with the negative connection between the charger and the battery.Leave a comment:
-
I called Midnite Solar today to ask a couple questions about the Midnite Classic 150, and the woman I talked to referred me to this http://www.midnitesolar.com/pdfs/MNE...150-120VAC.pdf
After having studied it, and read Sunking's last post, I put together this wiring diagram. Wiring Diagram 2.0.JPG
She tried pretty hard to sell me on that Whizbang Jr. thing, so I threw that in there. (Although it's an axiom of mine to remain skeptical about any claim of safety or usefulness, least not from the person whose trying to sell you the thing in question.)
$60 for an accurate reading on battery charge was the jist of it, from what I understand (hence requiring a shunt instead of one of those Blueseas Busbars?)
I am confused though, because I read that
"If your system has a shunt, one side must be connected DIRECTLY to the battery terminal and there must be NO other cables attached to that battery terminal. To attach cables to the battery terminal that the shunt is connected to is to by-pass the shunt." Although Midnite Solar's diagram has the Whizbang attached to a DC Shunt which is attached to battery, inverter, DC surge protector, and Charge controller.
Sunking- I've also read that fuses should be placed on positive terminals, so would the second set on negative terminal be necessary? or added protection?
And would having those MRBF fuses placed on the battery terminal posts make the 120A breaker switch that I drew (on the charge controller side) redundant, or will it function just as an added level of protection?Leave a comment:
-
It is a mobile Inverter and like any mobile Inverter does not need any AC protection. It does not generate enough power to operate a breaker. 600 watts dead bolt fault only generates a whopping 5 amps of current. A 14 AWG plug cord can handle 15 amps of current all day long and never break a sweat.
5 amps will kill you dead in a second, but breakers are not there to protect you, they are there to protect the wiring only from catching fire. What does protect you and the Inverter uses is a GFCI NEMA 5-15 socket to plug in your cords. Before you ask your next question NO GROUND REQUIRED so don't ask.
What you do need is a DC fuses, 4 of them installed directly onto the battery term post. Two fuses facing the CC, and the other two facing the Inverter. You need two Blue Seas 2151 Battery Fuse Blocks, and four MRB Fuses.
BLU_Terminal_Fuse_Blocks.gif
Click on pictures to enlarge for connection detail.
DualBatteryFuse_zps19afcf46.jpgLeave a comment:
-
Leave a comment:
-
I am thinking about buying the Midnite Classic 150 for Charge Controller and was looking at the Samlex PST 600W 24v Pure Sine Wave for Inverter. It's UL Listed, apparently, and only $221. It does not, as far as I see, have a built in AC breaker. Does anyone know of any UL Listed 24v, 600w inverters that do? Or should those components be kept separate?
Features of Samlex PST 600W: built-in electronic GFCI, overload protection, low battery alarm / shut down, low idle power draw of less than 0.5 Amps.Leave a comment:
-
Vehicle engine at idle, the alternator puts out minimal power, you have to increase engine RPM's to get the alternator up to full speed to get charging power. 3,000 watts takes about 6 hp to spin, so you are still not burning much fuel. Time to recharge depends on the size of both the alternator and battery size. An average 100A alternator can continually produce about 70A without overheating, so that's about 1,190watts at 17v charging voltage.Who said anything about driving and wasting fuel? Certainly not me. That is a diesel engine right? Diesel engines at idle sip fuel. Granted it is over kill.Leave a comment:
-
Leave a comment:
-
Thanks for answering all my questions man, I really appreciate it. Just so you know, I copied and pasted the entirety of that thread you posted regarding 2kw 12v inverters to the Amazon review page for that Microsolar Inverter I bought/returned along with a 1-star rating. They reviewed the post, let it pass, but added "You had better know what you are doing or have professional training-" as the byline to cover everyone's asses. Haha.Leave a comment:
-
That is a 12 volt box because you used 12 volt batteries to build your box. Don't get me wrong, 12 volt batteries can work providing they have the required Amp Hour capacity but there is a limit. Largest 12 volt battery capacity you can buy is around 200 AH. At 200 watt hours would be difficult to work with weighing 175 or pounds. A 12 volt 500 AH battery would weigh in at 300+m pounds. That is where you got caught stuck inside a 12 volt box, and used parallel strings. You never considered using 4 or 6 volt batteries of 450 to 500 AH because all you knew is 12 volts batteries.
For every 12 volt of battery requires roughly 18 volts. So at 48 volt battery minimum panel voltage is around 70 volts. Good charge controllers have a Voc input of 150 and 600 volts. You want to run panel voltage as high as possible. Yes you can run a panel voltage of 500 volts on a 12 volt batteryWhat about having x4 12v in series, producing a 48v bank? Would that be chargeable by a 48v-series module? I know the "vmp being too close to the batteries voltage will make fully charge an issue". But the vmp is still 22, even though the string of panels will be operating at 48v, presumably. (x4) 6v in series would seem to be preferable, but could it be done without too terrible of consequences if options were limited?
Who said anything about driving and wasting fuel? Certainly not me. That is a diesel engine right? Diesel engines at idle sip fuel. Granted it is over kill.The charging of the batteries via engine running hadn't been a consideration until now, but I am eager to research it (via the alternator, I presume?). I'd like to have both options though, rather than either/or. It's a 2004 Ford E-450 with a Triton V10, so it's gas mileage is pretty terrible, but I got a good deal on it and it's pretty reliable from having been well maintained during its run as a shuttle bus. I'd like to be able to just hunker down in it for a couple days at a time without having to move it.
But here is the reality, any full time off-grid battery system requires a generator. That gives you two options. Use the Engine alternator, or buy a portable generator and battery charge. Take your pick. If it were me I would do both, but that is just me.Leave a comment:
-
Well, I was proposing x3 12v batteries in series, producing a 36v battery in effect, and then adding a parallel string. So I'm unsure why that counts as being stuck in a 12v box. What about having x4 12v in series, producing a 48v bank? Would that be chargeable by a 48v-series module? I know the "vmp being too close to the batteries voltage will make fully charge an issue". But the vmp is still 22, even though the string of panels will be operating at 48v, presumably. (x4) 6v in series would seem to be preferable, but could it be done without too terrible of consequences if options were limited?You are talking two different animals which have nothing to do with each other.
You are correct higher voltage (24 )means half the current and wire losses of lower voltage (12), but that has nothing to do with what voltage batteries you use. If you use 6 volt batteries, you use two in series to make 12 volts, four in series to make 24 volts, or eight in series to make 48 volts.
The charging of the batteries via engine running hadn't been a consideration until now, but I am eager to research it (via the alternator, I presume?). I'd like to have both options though, rather than either/or. It's a 2004 Ford E-450 with a Triton V10, so it's gas mileage is pretty terrible, but I got a good deal on it and it's pretty reliable from having been well maintained during its run as a shuttle bus. I'd like to be able to just hunker down in it for a couple days at a time without having to move it.
Quick math: Bus gets 8mpg. If I drove it on the highway for one hour a day at 60mph, it would take 7.5 gallons of gas, @ 2.50 a gallon = $18.75 in gas. How long would it take for a full charge? 30 Minutes is still $9.37. 10 Minutes is still $3.123. Again: the option would be great, but as a standalone source it seems less than ideal. But if it's going to be running anyways, (or I have a string of cloudy days) it sounds great.Leave a comment:
-
Neither. It is about balancing equally between the parallel strings. You cannot balance them because each string has different internal resistance. That forces the strongest string to do most of the work which quickly weakens it, and shortens th ecycle life of every string. That of it as the Fast Lane to Death. LFP can be done, but they use a Ladder Method.
You are talking two different animals which have nothing to do with each other.And wouldn't the disadvantages of 12v vs. 24v, (i.e., 12v systems requiring larger cords due to increased amperage, and the increased danger associated with higher amperage when the freezer kicks on and draws power from the a lower voltage inverter) make 2,4,and 6v batteries even worse choices?
You are correct higher voltage (24 )means half the current and wire losses of lower voltage (12), but that has nothing to do with what voltage batteries you use. If you use 6 volt batteries, you use two in series to make 12 volts, four in series to make 24 volts, or eight in series to make 48 volts.Leave a comment:
-
Thanks, that's all enourmously helpful. I will note the precaution, but what are the reasons for avoiding parallel batteries? Are they based in safety or efficiency, or both?
And wouldn't the disadvantages of 12v vs. 24v, (i.e., 12v systems requiring larger cords due to increased amperage, and the increased danger associated with higher amperage when the freezer kicks on and draws power from the a lower voltage inverter) make 2,4,and 6v batteries even worse choices?Leave a comment:
-
The chart is generic to low and mid end FLA batteries. Some of the better ones are 5 times that amount. However all charts are grossly over exaggerated. Batteries have both Calendar and Cycle Life, whichever comes first. You can determine Calendar life looking at the warranty.
I found a chart for D.O.D/ cycle lifetime earlier in my research, which looked like this:
* 50% = 200 cycles
* 40% = 500 cycles
* 30% = 1000 cycles
* 20% = 2000 cycles
* 10% = 4000 cycles
And I guess I took it for granted that this chart was applicable to AGM, (which I would be willing to pay for to avoid having to deal with the potential safety hazards of FLA, however manageable they may be with proper knowledge), but I think the article mentioned using a hydrometer, which I am unsure applies to AGM. How would this D.O.D chart look for AGM?
Manufactures spin the numbers and test under lab conditions. Yes they can get 2000 cycles at 20% DOD, but that is done in less than a year, in a lab with computer controlled equipment, on a 2 year battery. In your real 2 years is maybe 600 cycles before Calendar Life hits the end. There are a very few batteries out there that have 10 year warranties like Rolls 5000 Series, but you are going to pay $250 to $300 per Kwh for them vs $75/Kwh for a 1 year battery. However long term the high-end is less expensive.
Now there are 10 year AGM batteries out there. They come under the Marketing names as Fork Lift, Traction, and Industrial batteries but come with a stiff price tag of $400 to $500 per Kwh.
If I were in your shoes I would be looking at LiFeP04 aka LFP batteries in a mobile application. They do not have any meaningful Peukert Effect, can be charged discharged at rates of in excess of 1C. It takes 100 AH of LFP to equal 200 AH of FLA to DOD 0f 80%. In practice if you assume only 33% DOD per Day with FLA it only takes 40 AH of LFP top equal 100 AH of FLA.
Today Chi-Com LFP batteries sell for 420/Kwh. A set of 4 Calb 100 AH cells (12 volts) will cost 4 cells x $133 each = roughly $540. That roughly equals a 12 volt 250 AH FLA battery which will cost you as little as $225 for a 1 year model up to $750 for a good 6 to 8 year FLA. A LFP battery should give you 1800 to 2500 real cycles, and they do not need to be charged every day like FLA. In fact you never fully charge them up.
However IMO you are not a candidate for LFP batteries. You just simple do not know enough yet about them. Just one silly mistake, over discharge, will turn them into boat anchors. Perhaps you rnext set you migh tbe ready for them and hopefully more charge controllers on the market to support them.
Yes but it requires you to use a MPPT controller. Be aware there are a lot of controllers out there that claim to be MPPT, but they are not. You want somewthing that can input 150 Voc
Try finding and pricing out a 36 volt Inverter and you will understand. If you should find one in the power you require will be very expensive compared to its 12/24/48 cousin.
OK don't do this and get out of that 12 Volt Box you are stuck in. If you need 465 AH battery, then buy 465 AH batteries. DO NOT PARALLEL BATTERIES unless you have no choice. Unless you need more than 4000 AH, there is no reason to have parallel batteries. 465 AH batteries are are going to be either 6, 4, or 2 volt batteries.Based on that chart, I was thinking 6 AGM 12v 155ah batteries, with two strings of (x3) in parallel. Gives me 11,160 Watt/hours total. 10,000 is a 20% depth of discharge after I adjusted my daily usage to be 2,000 W/h to compensate for 40% loss from module to freezer, so I could have a little buffer for multiple cloudy days.
Since the batteries themselves are 12v, what size would the wires have to be? Those rated for 12v? or can they be suited for the 36v, since that what each string of batteries will, in effect, combine to form? Once again, is there any links or books anyone can refer me which might provide any pertinent information about any of this?
However how do you intend to charge such a monster 24 volt 465 AH battery? It will take at least 1100 watts of panels with a 45 amp controller to feed that monster. Not to mention weigh in around 700 pounds.
Last comment invest in a Electronic Battery Isolator for $50 to $75. If you run the engine everyday for an hour would completely eliminate the need for any solar. In addition could cut your battery size by 50%. You would only need three day reserve capacity and not 5. Did that occur to you?Leave a comment: